Dear sir,
We are having following motor for our Vertical Raw Mill CA Fan in our cement plant and we are using it with a GRR for speed control. The details of the motor and GRR steps with speed are given below. As we have enhanced production, we are running CA fan at 90% or 100% speed. Hence, we don’t need to have this many steps of speed while running the motor. Hence, we are thinking of reducing contactor operations in order to minimize contactors failure in GRR and to reduce maintenance cost. We like to operate the fan in steps 1,2,4,8,9,11,14,18,22 and 26.I have given the speed of the motor at that particular steps. Kindly give your opinion. I want to know what should be the minimum speed to start the motor.The minimum speed at present is 640 RPM.Can we make the minimum speed to 800 or 850 RPM with GRR. Will it have any impact on the motor?Kindly give guidance.
1. Motor details
KW-2000, Amps-223, RPM-993, Rotor Volts-1825, Rotor Amps-650, Make-CGL
|
STEPS |
C1 |
C2 |
C3 |
C4 |
C5 |
C6 |
Speed | Raise in speed |
| 1 | OFF | OFF | OFF | OFF | ON | OFF | 640 | |
| 2 | ON | OFF | OFF | OFF | ON | OFF | 655 | 15 |
| 3 | OFF | ON | OFF | OFF | ON | OFF | 670 | |
| 4 | ON | ON | OFF | OFF | ON | OFF | 685 | 30 |
| 5 | OFF | OFF | ON | OFF | ON | OFF | 700 | |
| 6 | ON | OFF | ON | OFF | ON | OFF | 715 | |
| 7 | OFF | ON | ON | OFF | ON | OFF | 730 | |
| 8 | ON | ON | ON | OFF | ON | OFF | 745 | 60 |
| 9 | OFF | OFF | OFF | ON | ON | OFF | 760 | 15 |
| 10 | ON | OFF | OFF | ON | ON | OFF | 785 | |
| 11 | OFF | OFF | OFF | OFF | OFF | ON | 810 | 50 |
| 12 | ON | OFF | OFF | OFF | OFF | ON | 820 | |
| 13 | OFF | ON | OFF | OFF | OFF | ON | 830 | |
| 14 | ON | ON | OFF | OFF | OFF | ON | 840 | 30 |
| 15 | OFF | OFF | ON | OFF | OFF | ON | 850 | |
| 16 | ON | OFF | ON | OFF | OFF | ON | 860 | |
| 17 | OFF | ON | ON | OFF | OFF | ON | 870 | |
| 18 | ON | ON | ON | OFF | OFF | ON | 880 | 40 |
| 19 | OFF | OFF | OFF | ON | OFF | ON | 890 | |
| 20 | ON | OFF | OFF | ON | OFF | ON | 910 | |
| 21 | OFF | ON | OFF | ON | OFF | ON | 920 | |
| 22 | ON | ON | OFF | ON | OFF | ON | 935 | 55 |
| 23 | OFF | OFF | ON | ON | OFF | ON | 950 | |
| 24 | ON | OFF | ON | ON | OFF | ON | 965 | |
| 25 | OFF | ON | ON | ON | OFF | ON | 980 | |
| 26 | ON | ON | ON | ON | OFF | ON | 1000 | 65 |
We want to understand that the speed raise of 60 , 65 RPM per step is OK for the motor or not.
We want to explore the second option also as given in the drawing.

We want to minimize the no. of contactors in GRR and go for the above mentioned scheme. I want your guidance whether this scheme can be adopted or not. I have given the original scheme for your information and understanding.

Kindly guide me with a proper scheme to minimize maintenance cost.
Thanks,
NVRsrinivas
Good Answers:
"Almost" Good Answers: