feed water temperature to Non IBR boiler

08/25/2007 10:32 AM

In non IBR boilers, in india, manufacturer recommends feed water temperature should not exceed 40 deg.C. why is it so? Can we use the condensate of temperature 50 deg.C to 80 deg.C to feed boiler. If yes, how?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#1

Re: feed water temperature to Non IBR boiler

08/26/2007 12:14 AM

Prior commenting, I might be asking a stupid question but here it goes - " Whats a "non IBR boiler"? What abbv. is "IBR"?

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Anonymous Poster
#2

Re: feed water temperature to Non IBR boiler

08/26/2007 7:20 AM

Dear ducon

IBR is the abbr for" Indian Boiler Regulation".It may be that Non IBR stands for a Low pressure boiler.Mr Shridhar has clarify the rating of boiler i.e.TPH,Kg/cm2 etc.to get the solution.

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#3
In reply to #2

Re: feed water temperature to Non IBR boiler

08/26/2007 8:59 AM

Thanks. He has yet to state capacity kg/hr or Tph & operating pressure.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#4

Re: feed water temperature to Non IBR boiler

08/26/2007 9:03 AM

Thanks the guest who informed me IBR.

Such Boilers I believe will be steam generators upto 600 kg/hr?

Please state if this is a Steam Generator? Is it for hot water or steam? If steam please state operating pressure Bar & steam generation.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Member

Join Date: Aug 2007
Location: Bangalore - India
Posts: 6
#5
In reply to #4

Re: feed water temperature to Non IBR boiler

08/27/2007 11:27 AM

This is steam generator, packaged boiler or double skinned water tube boiler; having of 600kg/Hr capacity operating at 10kg/cm2 pressure. This has economiser, air blower with burner. Fuel used is HSD and feed water is soft water...

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: feed water temperature to Non IBR boiler

08/28/2007 6:55 AM

Surely a telephone call to the boiler manufacturer for technical assistance would sort this one out?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Aug 2007
Posts: 6
#7

Re: feed water temperature to Non IBR boiler

08/29/2007 1:48 AM

it is because of the limitation of feed pump. normally positive displacement type feed pumps are used in non ibr boilers. if feed water temp is more, then there will be chances of vapour locking and water will not be pumped to boiler leading to watertube coil overheating and accident.

Register to Reply
Member

Join Date: Aug 2007
Location: Bangalore - India
Posts: 6
#8
In reply to #7

Re: feed water temperature to Non IBR boiler

08/29/2007 3:04 AM

I am thankful for your inputs.... i am in touch with the manufacturer M/s.Thermax. As per them, it is not recommended. However i am seeing feasibility / opportunity to use condensate water (without using heat exchanger) to feed the non IBR boilers...

Register to Reply
Guru

Join Date: Dec 2006
Location: Hop around Toronto, New York & Karachi
Posts: 1876
Good Answers: 19
#9
In reply to #8

Re: feed water temperature to Non IBR boiler

08/29/2007 7:25 AM

i agree with Radtherm.

If you change your pump to give feed water at 100C then you will save 1% fuel or increase boiler efficiency 1% with every 6C rise in your feed water temperature.

Your savings can be upto 11%. The difference in the cost of replacing the pump will be paid off within 6 months plus the increase in the boiler/tube life with minimized thermal shocks with feed water at 100C rather than at what temperature you are presently giving it. Consult your Boiler Manufacturer.

__________________
I not only use all the brains that I have, but all that I can borrow. Woodrow Wilson
Register to Reply
Anonymous Poster
#10

IBR VALVES & NON IBR VALVES

03/26/2009 5:45 AM

MAHAVIR METAL INDUSTRIES

S I N C E - 1 9 6 9

Mfrs. of : G.M., Bronze,S.S., C.I., F.S., C.S. Boiler Mounting & Steam Valves

B-172/B, Industrial Area, Jalandhar-4 (Pb.) INDIA

Ph. : O. 0181-2290331, 5008511 R. 6539511

Contact Person: Sumit Jain

9216008511

Subject: Enlistment As Approved Suppliers

Dear Sir,

It is humble privilege to introduce ourselves as one of the leading manufacturers of Bronze, Cast Iron and Cast Steel Valves, Cocks and Boiler Mountings for general purposes and steam lines service in the brand name 'MAHAVIR' since 1969. Our products are known for their excellence in design, finish, workmanship and performance. Our company flourishers in the demanding business of valve manufacturing due to our quality par excellence, our dedicated workforce, our commitment to quality and customer service and proven record of reliable on time deliveries.

MAHAVIR Brand has earned the goodwill of superior performance and reliability for all its products over the last 39 years in the national as well as international market.

The range of our products covers Bronze Gate Valves, Globe Valves, Horizontal Check Valves, Vertical Check Valves, Ball Valves, Union Bonnet Globe Valves, Union Cover Check Valves, Foot Valves, Main Cocks Gland Cocks, 'Y' Type Stainers, Safety Relief Valves and IBR Certified Bronze, Cast Iron, Cast Steel Valves and Boiler Mountings etc.

You are requested to kindly enlist our name in your approved supplier's list for the supply of 'MAHAVIR' Brand Valves, Cocks and Boiler Mountings and send us your valued equerries/orders as and when required.

Your favorable action in the matter shall be highly appreciated.

Thanking you and assuring you our best services always.

Register to Reply