First you need a copy of the fan cuve, which should give CFM or L/s against a total resistance and at an RPM.
If you have the fan and not the curve document measure the inlet if it is a centrifugal or the diameter if it is an axial (propeller) then contact a fan manufacturer and ask for a performance curve for a fan of their manufacture with similar dimensions.
If you don't have a fan at all, you need to establish the duty you require and then contach the friendly sales dept of the friendly fan manufacturer to make a corresponding selection for you in CFM.
The nearest I have to look at is a 1000mm fan 12deg pitch at 1400 RPM gives 24,800 CFM in free air. It will draw 13 amps @ 220VAC it will deliver 5300 CFM @ 1.5"wg Hope this can help
gives 24,800 CFM in free air. It will draw 13 amps @ 220VAC it will deliver 5300 CFM @ 1.5"wg
I hope you mean 13 amps for 5300 cfm and not 24,800....gotta be a typo.
Most forward curve fans are not made for free air duty, they require some static on one
side at least ( especially with direct drive motors )
Hopefully our guest lets the professionals select his fan for the application he has or he can just do some studying on fan laws.... a complete science in itself.
__________________
Unless you're the lead dog on the sled, the view is always the same....
When you say you want to "calculate the CFM" of a fan, are you talking theoretical, actual, load, no load etc. For real-world applications, there are many variables that must be considered - The static pressure being exerted on both sides of the fan can play a big role in altering the CFM.
For real time CFM measurements, one would typically perform a pitot tube traverse with a manometer (or hot wire anemometer) and refer to the appropriate conversion tables to determine volumetric air flow, or utilize a velometer, or a balometer (do a search for alnor instruments) to obtain volumetric air flow data directly.