NEC Voltage Drop

11/08/2017 9:07 AM

To calculate Voltage drop in the conductors, what is the current value I need to consider, 100% of FLC (or) 125% of FLC?

Register to Reply
Pathfinder Tags: nec voltage drop
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: NEC Voltage drop

11/08/2017 9:22 AM

I would calculate for each and submit both on my homework assignment.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#2

Re: NEC Voltage Drop

11/08/2017 12:11 PM

100%

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#11
In reply to #2

Re: NEC Voltage Drop

11/09/2017 11:05 PM

Friend,

As Tornado has said, the NEC uses 100% of the FLC (full load current). The NEC uses 125% for calculations regarding the ampacity of a circuit and its overcurrent protection device for a continuous load (defined as a load that is on for 3 or more hours). Remember, however, that the NEC specifies a minimum standard of design/installation and encourages workers to exceed this standard. Therefore a calculation using 125% of the FLC will result in a lower energy loss balanced against a higher cost of the installation, along with better operation of the attached load.

--JMM

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: NEC Voltage Drop

11/08/2017 1:12 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Apr 2017
Location: Southern Illinois
Posts: 627
Good Answers: 13
#4
In reply to #3

Re: NEC Voltage Drop

11/09/2017 10:51 AM

One reason would be to ensure that selective-tripping is functional. Especially when nearly identical trip-points are in series and starting currents/voltages exceed the limits of rated values. Also, there are two different ways to look at it. One from the supply side, and one from the load side. Sometimes I get objections when I say that you can use fuses for two different reasons: One to protect the load, and one to protect the supply. They usually think that if a fuse/breaker trips, that the whole circuit is protected because ALL of the current stops. But the problem is that, if there is a partial fault in the load, it could damage the load-side circuits without tripping the supply-side protection. Therefore, the load-side protection should be closer to the normal values of the load, while the supply-side protection should be closer to the capacity of the supply. Sometimes this is not a factor with selective-tripping, and gets forgotten. Also, having a larger safety margin might be desirable (for whatever reason), even if it's not needed. What's required/optimal/safe/over-kill is a judgement call. But whatever call is made, it still has to function properly within the larger system (which may or may not be adjustable).

__________________
Science is the "cookbook" for making things.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#5

Re: NEC Voltage Drop

11/09/2017 1:05 PM

I don't know the current value, what is it presently?

If it is 100% FLC, I would use that. If 130% FLC, I would take off running.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Apr 2017
Location: Southern Illinois
Posts: 627
Good Answers: 13
#6
In reply to #5

Re: NEC Voltage Drop

11/09/2017 1:18 PM

Really? Maybe I misunderstood the whole purpose of the question. I thought it was just to get valid info to.... (???whatever). How could having valid info be "take off running" worthy? Am I missing something?

__________________
Science is the "cookbook" for making things.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#7
In reply to #6

Re: NEC Voltage Drop

11/09/2017 1:24 PM

You missed my joke.

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Apr 2017
Location: Southern Illinois
Posts: 627
Good Answers: 13
#8
In reply to #7

Re: NEC Voltage Drop

11/09/2017 1:53 PM

Oh. I never really had a keen sense of humor. I tried to get it calibrated once, but they thought I was joking.

__________________
Science is the "cookbook" for making things.
Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#9
In reply to #8

Re: NEC Voltage Drop

11/09/2017 2:32 PM

right...

current vs. present...

got it now?

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru

Join Date: Apr 2017
Location: Southern Illinois
Posts: 627
Good Answers: 13
#10
In reply to #9

Re: NEC Voltage Drop

11/09/2017 3:13 PM

Yes, I currently got it at present. Now, I just have to put it in a safe place for tomorrow.

__________________
Science is the "cookbook" for making things.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#12

Re: NEC Voltage Drop

11/10/2017 2:06 AM

100%

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#13

Re: NEC Voltage Drop

11/19/2017 12:05 AM

Usually, you have to check the minimum voltage in 2 situations:

1) at rated current [preferable 100%]

The minimum voltage for continuous function has to be as per NEMA MG1 [or IEC 60034-1].

2) start current

The minimum voltage for start has to assure a minimum torque as required.

If the load inertia it is in limits recommended by NEMA [or IEC] then a minimum 80% of motor rated voltage has to be present at motor terminals [for up to 100 kW induction motor] at start.

__________________
Julius
Register to Reply
Register to Reply 13 comments

"Almost" Good Answers: