power transformers

09/04/2007 2:28 PM

while conducting pre gommissioning tests on power

transformers what should be the acceptance value

of magnetising current for a 33/11kv,16 mva pr.tr

with Dy11 configuration.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#1

Re: power transformers

09/05/2007 3:54 AM

Demand Manufacturer's test report--on basis of which you accepted the Pr.Tx.

You will have to accept the same as the basis NOW.

Register to Reply
Power-User

Join Date: Aug 2007
Location: Bhopal India
Posts: 234
Good Answers: 5
#2

Re: power transformers

09/08/2007 11:47 PM

The magnetising current can go as high as 12 times the rated primary current of the transformer for few cycles.

__________________
He must be very ignorant as he answers all the questions he is asked. Voltaire
Register to Reply