Hi, what will happen if a solenoid is rated 110vdc, plugged in to 220Vac supply? Does that burn the coil considering there are no load on the solenoid?
Because a solenoid is a load. For linear devices, when you double the voltage, you quadruple the power dissipated.
A transformer is not designed to be a load. It is an impedance matching device for a range of frequencies. Although some will say that it is used to step-up or step-down voltages with a corresponding inverse relationship of the current, where isolation may be provided between the primary and secondary windings although certain transformers that is not automatically the case.
Oh, anything in the range between a loud buzzing sound and spontaneous and spectacular self-decomposition, which makes it a Silly Thing To Do.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
<...what will happen...?...> The act might attract a range of outcomes between minor re-training and dismissal for incompetence. It might also attract a measure of unpopularity with the facility's fire insurance company.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
It's just a scenario on site. Management has issues with personnel. It can't be perfectly eliminated that some of those technicians who has grief on the management will tend to do scenes like these. Some sort of destructive testing, I presume.
A 110VDC solenoid (or its circuit) is likely to have a suppression diode or voltage dependent resistor wired internally or externally for spark/spike suppression. Connecting 220 VAC will blow diode/VDR and or/ fuse.
To get the maximum pull from the smallest assembly, the DC solenoid will saturate the iron in the magnetic circuit. Thus current much above the rated DC current will certainly get saturation with the with the equivalent AC heating current (root mean square or r.m.s. - rms = 1.11 x DC for resistive circuit) which has a peak current 1.414 x rms, even if the current were sinusoidal.
A pure DC solenoid will not have a laminated iron core so iron losses on AC at rated current would add to the coil DC losses. However, AC solenoids being far more common than DC, DC solenoids are often AC ones with a different winding or a resistance switched-in, once closed, to provide a "holding" current which will not overheat the coil.
To add to trouble, you want to apply 220VAC, potentially 220/120 (note point 2 above, 110 x 1.1 = 120 approx.) times current or 3.4 times watts, neglecting inductance. Excessive current could cause winding failure.
At rated coil current and 220VAC applied, a vector triangle indicates that inductive voltage drop would need to be 185 volts, a power factor of 120/220 = 0.55. Thus it could be quantified, that if current draw at 220VAC was no more than 1.1 x DC rated current and power factor <0.55, then watts loss would be no more than rating.
On AC, a DC coil would have fluctuating pull at 100/120Hz, which could cause "chattering" and cause damage if energised for too long.
It has not been specified if you have DC solenoids of one or a few types - in that case you could test with a variac to see at what AC voltage "true rms" current draw becomes excessive.