Previous in Forum: Solenoid Plug In to Higher Voltage   Next in Forum: Fully Controlled Rectifier Firing Mode
22 comments
Detecting Motor Rotation When Motor Is Not Energized
01/16/2018 5:32 AM
A VFD controlled motor is used in a steel transfer car. The power gets transmitted through a 160m 4Cx50sq mm CRD cable. The span of travel for the car is approx 250mtrs. Earlier DC motors (separately excited) were used which have been replaced as a part of up gradation. The problem is when the car stops (no command given), it rolls due to gradient of track or sometimes due to external means of pushing by other car on the same track. This leads to a loop in the CRD cable. Once command is given, the CRD motor is energized, thus retracting the looped cable therby entangling it with roller structures and gets cut.
I need to know how can i detect the rotation of motor (placed in the car) when it is not energized, so that if it rotates a signal can be given to the CRD motor to retract the cable so that loop formation and subsequent cutting of cables be avoided. These travel cars a lifeline for production of steel and further not other devices (like tachos or encoders) can be mounted as they cannot be powered through CRD cable.
Pathfinder Tags: CRD motor not energized rotation
Good Answers: 140
Re: Detecting motor rotation when motor is not energized
01/16/2018 8:40 AM
We had essentially the same problem with trucks that moved along long horizontal cheese drain tables in the food industry. The answer was to have the power cords pay out from spring powered cord reels.
01/16/2018 9:05 AM
IN the dairy industry, when hooking up centrifugal pumps, we had the same issue on making sure the motor runs in the correct direction... one can really destroy the impeller shaft in no time just by testing the rotation...
Good Answers: 140
01/16/2018 9:47 AM
Your 250m requirement is a long way. My cord reel idea would be hard pressed to handle that length.
01/17/2018 10:20 AM
Well for a 3Cx50 sq mm cable the spring powered cord reels for a length of 250mtrs is not feasible.
Thank you
Good Answers: 804
Re: Detecting Motor Rotation When Motor Is Not Energized
01/16/2018 10:44 AM
Your Cable Reeling Drum (CRD for those that didn’t understand that) would typically have some sort of automated tension system in it to avoid this very thing. So I take it that someone decided to go cheap and not include that. This is the consequence of that decision... it will now cost you more (than it already has in damaged cable) to retrofit a solution than had they just done it right the first time. Oh well, not the problem you asked about though...
Assuming this is a motor powered CRD, if your CRD motor has a VFD on it you could place it in “torque mode” to apply a constant tension on the reel, paying out or taking in slack as needed, but keeping it tight at all times to prevent loop formation. If there is no VFD you could add one, but you would need full Flux Vector Control capability without a shaft encoder, something that does not come on cheap drives. The same might hold true if you have a cheap drive incapable of this ability, so you may need to upgrade. Drives that only provide “Sensorless Vector Control” don’t have a true torque regulator loop that would allow that level of tension control, it takes true Flux Vector Control, and less expensive drives will need an encoder feedback to implement this, something you indicate is not possible. But there are a few drives out there that can do “Encoderless Flux Vector Control”, that’s what you will need. A Rockwell PowerFlex 755 drive is the one I use for that, as an example. There are others, I just don’t look for more solutions once I find one.
Another option used used in the past (before VFDs) was a “dancer reel”, a purposeful drop loop in a safe area, keeping tension on the cable by hanging a weight on the pulley. Without seeing your installation I have no way of telling if that’s possible though.
I agree, 250m travel pretty much rules out a mechanical spring tension reel, the other option, unless the car motor is very very small which in a steel mill I seriously doubt.
01/17/2018 12:10 PM
Thank you very much for your patient reply.
Firstly, the CRD motor is a Demag make Torque motor (SRIM with conical rotor and shaft mounted brake, the motor is vertically mounted) which works on DOL and no VFD.
Secondly, the tension gets maintained with a feedback from pendulum limit switches and when command is given, by picking up the rotor contactor of CRD motor.
But as can be seen from the figure, the loop formed after some length of cable is not detected by the CRD motor when travel motor is not energized.
When the travel motor rotates without command towards CRD (due to many reasons) the cable needs to get retracted. The logic takes care if the slackness in cable extends till the pendulum switch and none of them (left or right) are in action and no command is given.
So I need to know the rotation in the travel motor when it is not energized so that it can be used to pick up the rotor contactor of CRD motor to pull the cable taut and thus avoid loop and cable cuts.
01/17/2018 2:13 PM
Stop the transfer car from moving when not commanded, that will fix the CRD reel problem.
When the VSD for the car was changed from DC to AC, and not installing a line voltage mechanical set brake, that appears to be the start of your trouble. Now, add dc injection brake to your transfer car drive, and the motor will not move unless commanded.
Your comment is marked off topic, but it is not, you should change that...
01/16/2018 11:30 AM
01/16/2018 12:57 PM
Why not add other position sensors, like an encoder or camera to this transfer car.
01/16/2018 4:23 PM
If the cord reel is not working, why is that? Seems an obvious solution to me.
NVE makes all manner of rotation sensors using Hall effect, one that measures angles down to about 0.3 degrees. All you may need, though is a number of magnets and a switch sensor (the GMR ones can have some real separation between magnet and sensor), and a counter. If it counts after power is down, then it requires an interlock override from a human operator that has checked the cable reel up, or not.
Good Answers: 225
01/16/2018 7:48 PM
Might not a simple spring loaded lever with the cable running over it via a roller do the job?
The lever would be pulled down thus de-energising the CRD motor via an attached microswitch when the cable was under tension and being played out, but the spring would pull the lever back when the trolley allowed any slack in the cable - thus energising the rewind motor.
It would seem logical that if the trolley reverses, then any slack in the cable would be immediately adjacent to the trolley and thus have sufficient reduction in weight to allow a properly tensioned spring to do the job.
01/17/2018 9:35 AM
An elegant answer and solution my digging friend.
01/16/2018 9:10 PM
Why not battery powered sensors in the cars to detect motor rotation? Batteries could be recharged by power to the VFD motors if necessary.
01/16/2018 10:45 PM
Your VFD may be able to apply a small dc voltage often used for hard starting motors, when stopped, which should lock the car into place. Called dc injection braking, they make add-on modules if not available in your drive. On an older drive, I once had the dc level so high I couldn't get it to turn at all, head scratcher for the newbie.
How did you keep the dc motors from turning, same way, right? Leave the field applied? It sounds like this problem arose when the dc motors were replaced?
DC injection probably cleaner than fitting your motors with mechanical set brakes, a common solution to this sort of unintentional travel, such as on a crane bridge.
01/17/2018 12:10 AM
Option 1 : If new Electromechanical brake is possible to mount on mechanical assembly to prevent the motor shaft rotation when not Energized. Solidstate relay can be use to control the brake On-Off. Option 2 : If Bosch Rexroth servo drive can be use to replace the vfd. Sothat motor shaft will be in servo hold condition when not Energized.This will prevent motor shaft rotation when not Energized. But before this use, you must ensure that you have full technical data sheet of your motor, which is needed at the time of Bosch Rexroth servo drive programming.
01/23/2018 1:27 AM
How do i control the brake? The CRD cable used is 4Cx50 sq mm.
01/17/2018 9:17 AM
Why are your cables vulnerable to being cut by this transfer car or anything else? Put these cables into a flexible cable tray.
Good Answers: 266
01/17/2018 9:26 AM
The fact that it rolls with out power should be the major concern. Accident waiting for a place to happen. Put a brake on it. Which would solve the cable issue.
01/17/2018 9:37 AM
You failed to specify how much rotation is tolerable (if any), and at what rotation you need to activate the CRD motor. Also you failed to point out the general lay-out in your steel mill of the trolley and the cable.
As indicated by redfred, what prevents you from placing the cable on overhead flex tray?
01/17/2018 10:42 AM
I've used a tachometer that is basically a magnet wrapped with a coil that is mounted near a gear on a shaft. If the gear rotates, the teeth interact with the magnetic field from the magnet and generate a pulse in the coil. I was using that signal to determine speed of the shaft and also as a zero speed sensor, similar to what you are trying to do.
01/31/2018 11:59 AM
Absolute encoder
Dave Oliver
02/01/2018 1:48 PM
I assume you want the car to be able to move if pushed by other car or whatever. A hundred years ago (before VFD's, encoders etc.) in blast furnaces they used "tri-rods" to determine level of burden in blast furnaces. A weight rested on burden and a DC electric motor (Driving a "winch") kept cable (a wire rope then) taught. The motor (because of low applied voltage) was unable to lift weight but kept cable taught. When time to add material (replace burden) full voltage was applied to motor and weight came up. After addition went back to reduced voltage and weight rested on burden. If burden raised (It never did.) "winch" would reel in cable and keep it taught. We still use these in plant I work in although there are other burden level indicators as well.
Register to Reply 22 comments
daveoliver (1); hoo8975 (1); James Stewart (3); Jpfalt (1); JRaef (1); North of 60 (2); ozzb (1); phoenix911 (1); redfred (2); Rixter (1); rwilliams (2); satishmalge (1); SolarEagle (1); spades (1); todearprasanth (3)