Consider figure below:

the ACB has no trip unit ,hence cannot trip for any faults .the ACB is just used for isolation.the transformer is protected on LV side by neutral CT only. the CT is connected to over current relay "K1". the contact of over current relay "K1" is hardwired to tripping coil of VCB. will the transformer be protected for faults on LV side by just relay K1? what are the disadvantages of not providing tripping functions of the ACB?

thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42357
Good Answers: 1695
#1

Re: Transformer Protection

01/25/2018 12:57 PM

MY GOD MAN! TAKE A CLASS! DO SOME RESEARCH! QUIT ASKING OTHER PEOPLE TO THINK FOR YOU! DO YOUR OWN HOMEWORK!

Busbar Protection

How do you ever keep a job?

Register to Reply
Power-User

Join Date: Jul 2011
Posts: 286
Good Answers: 1
#2
In reply to #1

Re: Transformer Protection

01/25/2018 1:04 PM

appreciate that

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Transformer Protection

01/25/2018 1:18 PM

Ask you’re supervisor / mentor to explain it to you.

I’m not wasting my time with you on basic and dangerous engineering principals.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Power-User

Join Date: Sep 2016
Location: SPAIN
Posts: 233
Good Answers: 13
#5
In reply to #3

Re: Transformer Protection

01/26/2018 1:08 AM

You're vs your. 50% theoretical chance to get it worng, 90% actual chance.

__________________
Building the future!
Register to Reply Off Topic (Score 5)
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#8
In reply to #5

Re: Transformer Protection

01/26/2018 10:41 AM

Hey, he is in the 100% category, since he only has to be dead wrong one time!

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32212
Good Answers: 839
#4

Re: Transformer Protection

01/25/2018 3:30 PM

Relay K1 is therefore a neutral current trip unit, and cannot protect for phase over-currents downstream, as that's not what it is designed for.

<...what are the disadvantages of not providing tripping functions of the ACB?...> The the above single line diagram does not necessarily show all the protection in the circuits, for that is the job of the "as built" schematic wiring diagrams, which have been withheld from the forum. The documentation cannot be seen from here, therefore no-one in the forum can answer the question.

  • Where is the design documentation and commissioning records that cover the equipment that has been queried over the last few occasions? Where is the name of the Design Engineer on that documentation? Where is the design and the commissioning organisation's telephone number on that documentation? Please explain why this avenue has not yet been explored?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Sep 2017
Posts: 11
Good Answers: 1
#6

Re: Transformer Protection

01/26/2018 3:33 AM

Coolyaar, K1 protects the transformer and HV from faults on the LV side. The LV side receives power from the HV side. It is a passive receipient. Now if power was to flow from the LV side to the HV side then the proposal you have (tripping the ACB to protect the transformer and the LV cct) will be needed. This time the fault will be on the HV side, say, like a ground fault.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7

Re: Transformer Protection

01/26/2018 10:31 AM

Hope there is phase O/C in 6kV switchgear panel. This can take care of phase to phase / three phase faults in 400V system as well as high current earth faults.

The 400V earth fault protection connected to the transformer 400V neutral CT should help in isolating the transformer for those low current faults which may not be good enough to operate the 6kV overcurrent protection.

Generally speaking, the earth faults yield low magnitude of currents due to fault impedance / earth loop impedance.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42357
Good Answers: 1695
#9

Re: Transformer Protection

01/26/2018 11:14 AM

Here's a disadvantage:

If You Are Wrong

Do your own work and witness the commissioning up close, alone!

Register to Reply
Guru
Safety - Hazmat - New Member United States - US - Statue of Liberty - New Member Engineering Fields - Chemical Engineering - Old Hand

Join Date: Mar 2011
Location: Lubbock, Texas
Posts: 14331
Good Answers: 162
#10
In reply to #9

Re: Transformer Protection

01/26/2018 11:21 AM

ON that 115 kV line, about 5' off to the side on the ground should about take care of it!

__________________
If it ain't broke, don't fix it. Just build a better one.
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 445
#11

Re: Transformer Protection

01/27/2018 12:52 AM

No, the only fault that will be detected is one that causes a sufficiently high level of zero sequence current to flow in the grounded neutral. Your cost saving scheme cannot discriminate between high vs. low impedance faults; and if set too low, will result in nuisance trips due to any phase current imbalances caused by motor starting, varying supply voltages, single phase loads, etc., etc. It also provides NO protection against balanced conditions such as a three phase fault, overcurrent, locked rotor, overload, winding overtemperature, etc., etc.

If the ACB tripping functions were enabled you might get some protection against some of the faults mentioned in the last line of the above paragraph, but that would depend upon your skill in choosing the correct ACB tripping element and settings.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Register to Reply 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

coolyaar (1); Ivanov327950 (1); James Stewart (2); lyn (2); PWSlack (1); raghun (1); RAMConsult (1); Thaddeus Mogire (1); TonyS (1)

Previous in Forum: Clockwise vs Antoclockwise in LV Network of Utility   Next in Forum: Electrical Lift For 20kg Load For 30m Height

Advertisement