Transformer No Load Loss at Different Temperature

02/01/2018 12:13 AM

Hello,

As per IEC standards, there is a reference temperature for measurement/calculation of transformer Load loss (75 degree C). i.e Most of the load loss is I2R component. and resistance varies with temperature. Hence even the loss measurement is done at ambient temperature it is corrected to reference temperature .

But why No load is not corrected in the same way, irrespective of different ?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Sep 2016
Location: SPAIN
Posts: 233
Good Answers: 13
#1

Re: Transformer No load loss at different temperature.

02/01/2018 1:01 AM

Simply because no load temperature is barely higher than the ambient temperature.

Unless, of course, that you are always working at the highest temperature using some sort of controlled refrigeration.

__________________
Building the future!
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Transformer No load loss at different temperature.

02/01/2018 1:13 AM

It might be a negligible amount of variation...if you are operating within the recommended operating parameters....

..."Power transformer losses are a combination of the power dissipated by the core's magnetizing inductance (iron loss) and the winding's impedance (copper loss). Iron losses are a function of the applied voltage and are often referred to as "no-load losses" - they are induced even when there is no load current. Copper losses are a function of the winding current and are often referred to as "load losses". These losses are calculated for any operating condition if a few parameters of the power transformer are known. The transformer manufacturer commonly provides this information on the transformer test sheet:

 rated total kVA of the power transformer (VATXtest).

 rated voltage of the power transformer (VTXtest).

 No-load test watts (LWFeTXtest) - the active power consumed by the transformer's core at the rated voltage with no load current (open circuit test).

 Full-load test watts (LWCuTXtest) - the active power consumed by the transformer windings at full load current for rated kVA (short circuit test).

 %Excitation current - ratio of No-load test current (at rated voltage) to full load current.

 %Impedance - ratio of Full-load test voltage (at rated current) to rated voltage.

The No-Load and Full-Load VAR losses (LVFeTXtest and LVCuTXtest) may not be provided, but are calculated from the above data."...

http://static.schneider-electric.us/docs/Energy%20Solutions/Offers%20by%20Market%20Segment/Utility/70072-0153-08%20Technical%20Note%20Transformer.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#3

Re: Transformer No Load Loss at Different Temperature

02/01/2018 9:52 PM

But why No load is not corrected in the same way, irrespective of different ?

Loaded transformer losses are due to copper resistance which is temperature dependent. No load losses are due to iron core losses which are not temperature dependent.

"Causes of transformer loss Power transformer losses are a combination of the power dissipated by the core's magnetizing inductance (iron loss) and the winding's impedance (copper loss). Iron losses are a function of the applied voltage and are often referred to as "no-load losses" - they are induced even when there is no load current. Copper losses are a function of the winding current and are often referred to as "load losses". "

http://static.schneider-electric.us/docs/Energy%20Solutions/Offers%20by%20Market%20Segment/Utility/70072-0153-08%20Technical%20Note%20Transformer.pdf (Sorry, link no longer available.)

Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#4

Re: Transformer No Load Loss at Different Temperature

02/02/2018 11:29 AM

The iron inductance losses are still temperature dependent both due to temperature dependence of magnetic hysteresis and eddy current production and dissipation. I suspect that the difference is low enough to be considered not significant for rating purposes.

Reply