Contactor Humming as Soon as Voltage Increases

01/31/2018 11:47 PM

Hello Everyone, I have a contactor with coil voltage 140-270V, when I check it at 165-175volts, it is perfectly silent. As soon as I increase the voltage around 200 Volts it starts humming.

Register to Reply
Pathfinder Tags: Contactor Humming
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Contactor humming as sson as voltage increases

02/01/2018 12:57 AM

I've never seen nor heard of a contactor coil with that wide of a range for control voltage....are you sure you're reading it right..?. what is the type and model number and brand name of this contactor?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: Jan 2018
Posts: 6
#2
In reply to #1

Re: Contactor humming as sson as voltage increases

02/01/2018 1:16 AM

Its for agri market.. 2 pole contactor coil.. declared is 154 to 264V.. brand is BCH

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #2

Re: Contactor humming as sson as voltage increases

02/01/2018 2:49 AM

I don't see any contactors with a range stated for control voltage....

https://issuu.com/bchindia/docs/bch

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: Jan 2018
Posts: 6
#7
In reply to #5

Re: Contactor humming as sson as voltage increases

02/01/2018 3:23 AM

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#8
In reply to #7

Re: Contactor humming as sson as voltage increases

02/01/2018 4:37 AM

Contactor coil if supplied by bridge rectifier (connected permanently at its terminals) can remain pickedup even up to 45% of rated coil voltage.

This is considered a plus when it comes to motor starters used for Agriculture pump sets.

It doesn't mean the contactor can pickup when the voltage is low (at the bottom end of the indicated coil voltage range).

Thus, it is normal if the contactor is only humming and not picking up when the voltage is low.

As well, when the voltage goes very low, i.e. close to bottom of the range, with contactor in picked up state there is a possibility of contactor humming (and hence drawing higher current).

__________________
Raghunath
Register to Reply
Guru
Safety - ESD - New Member India - Member - New Member Engineering Fields - Energy Engineering - New Member

Join Date: May 2007
Location: Pune , India
Posts: 875
Good Answers: 42
#17
In reply to #2

Re: Contactor humming as sson as voltage increases

02/05/2018 11:12 PM

Is the contactor and coil are reputed make? Is it ISI marked? To my experience there are many small panel manufacturers who use substandard contactors and coils for their panels which results in these types of problems. (Not the reputed company like L&T Snider, Crompton, and similar) The problem with substandard product is the core assembly is not with proper plates and assembly is not tight which results in core heating core humming, coil burning. Even for good quality contactors overheating and prolonged use and repeated operation cause humming due to rust on core face and improper alinement. I have even come across Agro motor control and starter manufacturers who ask you in advance weather we want reputed contactors and coils or ordinary ones for different prices. So better checkup for the quality. BCH is a reputed manufactureer . So you have to check whether it is manufacturing defect .contact the company.

"BCH Electric Limited, an ISO 9001:2008 Company, is one of today™s leading Switchgear manufacturers & LV Panels Manufacturers of low voltage electrical and electronic controls in India. The Company was established in 1965 as a joint venture between Cutler-Hammer, USA, and Indian partners. Since 1977, it is a wholly owned Indian Company with global business connections."

Register to Reply
Member

Join Date: Jan 2018
Posts: 6
#3
In reply to #1

Re: Contactor humming as sson as voltage increases

02/01/2018 1:20 AM

However L & T gives coil of 180-410V. SO range Is not an issue.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Contactor humming as sson as voltage increases

02/01/2018 2:43 AM

Perhaps it doesn't know the words?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jan 2018
Posts: 6
#6
In reply to #4

Re: Contactor humming as sson as voltage increases

02/01/2018 3:20 AM

????

Register to Reply
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#9
In reply to #6

Re: Contactor humming as sson as voltage increases

02/01/2018 11:37 AM

It is a humorous response to the joke: "Why is (fill-in-the-blank-here) humming?"

This is a reference to someone trying to sing along with a song, but since they don't know the words, they hum the tune instead.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10

Re: Contactor Humming as Soon as Voltage Increases

02/01/2018 11:49 AM

These motor starter contactors have coil voltage parameters of operation stated in %'s...Including coil rated voltage, coil operating limits, and electrical consumption among others, but they also have a proper coil voltage stated.........The noise(hummm) is no doubt harmonic resonance...

https://cdn.automationdirect.com/static/catalog/17-motor-controls-contactor-starter-relay-disconnect.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Member

Join Date: Jan 2018
Posts: 6
#12
In reply to #10

Re: Contactor Humming as Soon as Voltage Increases

02/01/2018 12:08 PM

Actualy the problem is the behaviour of contactor.. as soon as we increase the voltage the noise should be reduced.. but here the case is different.. initialy it is silent and become noisy as we increase the voltage..Just need hints what can be the possible reason...

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: Contactor Humming as Soon as Voltage Increases

02/01/2018 11:57 AM

New electronic coils have a small on-board auto-ranging switch mode power supply to a DC wound coil. So you can feed it a wide range of AC input voltages and it just steps it down with a small transformer, rectifies it to DC, then uses a DC PWM chopper to operate the coil at its design voltage.

In that little SMPS, there is a transformer and most likely the hum is the beginnings of that transformer starting to fail. You are hearing magnetostriction acting upon the core laminations, but that core should be solidly riveted to prevent that. So if you can hear it, the core laminations are getting loose. Failure is eminent.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#13
In reply to #11

Re: Contactor Humming as Soon as Voltage Increases

02/01/2018 12:09 PM

Ah yes something new....well, new to me...that explains it, if in fact it is one of these coils...

https://news.thomasnet.com/fullstory/contactors-incorporate-electronic-coil-control-design-19826

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: Contactor Humming as Soon as Voltage Increases

02/02/2018 2:29 AM

One of the possibilities is that there is an unintentional foreign object lodged in the mechanism that requires removal.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#15

Re: Contactor Humming as Soon as Voltage Increases

02/02/2018 11:10 AM

The humming is caused by mechanical movement of the wire windings or associated iron magnetic cores. As the voltage is increased, the current increases. The magnetic force increases and movement/deflection of wires and cores also increases. At some point it deflects enough to make an audible hum or the movement reaches the point that two surfaces in the assembly make contact, causing a noise. This may or may not be a problem, depending on whether the deflection, contact and noise indicate a wear surface or a stress concentration that will eventually lead to wear failure or fatigue failure of some component of the assembly. It's probably normal that a component run at higher power will fail before a component run at lower power, but if it is within the rating and of reasonable quality, it should provide reasonable service.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#16

Re: Contactor Humming as Soon as Voltage Increases

02/02/2018 12:14 PM

The fact that your contactor STATES that the coil voltage has a wide input voltage range can ONLY mean it has one of these electronic coils. There is no other way to make a coil that can accept that wide of a range. So the noise that the coil makes as the coil voltage increases indicates a failing coil.

The other issues of foreign objects etc. do lead to contactor noise, but would NOT be tied to a change in the coil voltage.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 17 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

amar_verma008 (5); Brave Sir Robin (1); Jpfalt (1); JRaef (2); PWSlack (2); raghun (1); SolarEagle (4); V.I.Abraham (1)