VFD Troubles

02/04/2018 12:10 AM

We are using a pump system that incorporates a 100HP gear pump charged with a 15 HP impeller pump. The 15 HP pump is started with a Schneider Electric soft start and the 100 HP is driven with an Eaton VFD. The 15 HP starts first and after 30 seconds the VFD starts and ramps up to speed.

We have nearly 30 of these units currently running and they have been so over an 6 month period. This last one installed gave us an overvoltage trip on the soft start as soon as the VFD was started. We had set the percentage parmeters and the time delay settings on the Soft Start to the maximum allowed. Either pump would operate correctly and stay running by themselves, but is soon as the VFD came on the soft start would trip.

Voltages phase to phase were 478 and phase to ground 276. STarting voltage flucuations were 2 volts or less. The 15hp was drawing 8 amps. The soft start was replaced with the same results.

We replaced the VFD and it started working correctly, for a few hours. We returned in the morning to find it was down again. When it was restarted the soft start again tripped. We replaced the Soft Start with a size #2 direct starter. It worked fine for about 15 minutes then a lot of smoke came out, they think it was the VFD. Not certain what happened next, but I had them check for faults or alarms on the VFD. They turned it back on and all was clear and normal (bus voltages, frequencies, etc). They restarted the pumps and the VFD popped and cracked and came up with an Over Voltage alarm.

All these VFD's have a line reactor filter and after 10 sec another reactor with capacitors kicks in on the incoming line. The second reactor never came in. The other puzzling thing is it appears to be a utility line problem but a mile down the line we have an identical setup that has been running problem free for 4 months.

They want to install another VFD but I think it will do the same thing after a day or two. What can be going on here and how can we check this?

__________________
deanpavil
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: VFD Troubles

02/04/2018 10:47 AM

What's the amperage draw on the VFD and motor? Sounds like a partial short...a temperature gun might locate the problem...might meg the motor...recheck the wiring, disconnect and check individually...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 3)
2
Power-User

Join Date: Apr 2011
Posts: 104
Good Answers: 5
#3
In reply to #1

Re: VFD Troubles

02/04/2018 4:26 PM

Yup. Found it. B and A phase leads were shorting out in the motor term box. Don't know how we got it to run for the couple hours that it did. Motor current was normal about 60 A. It cooked the TVSS or MOV devices on the incoming lines.

__________________
deanpavil
Register to Reply Good Answer (Score 2)
Power-User
United States - Member - Western Wisconsin

Join Date: Mar 2007
Location: Wisconsin USA
Posts: 305
Good Answers: 25
#4
In reply to #3

Re: VFD Troubles

02/04/2018 8:47 PM

Thanks for reporting back what the problem was.

We often do not hear back from the OP when the issue is solved.

__________________
Troy
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#5
In reply to #4

Re: VFD Troubles

02/05/2018 8:43 AM

Double that response. Nice to know what happened.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Guru

Join Date: Aug 2007
Location: London England.
Posts: 583
Good Answers: 10
#6
In reply to #1

Re: VFD Troubles

02/06/2018 6:23 AM

I was going to say that!

Bazzer

__________________
When I die I'd like to go peacefully in my sleep like my dad,not shouting and screaming like his passengers.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: VFD Troubles

02/04/2018 4:07 PM

<...phase to ground...voltages...> are not relevant.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 6 comments