Motor Duty

02/04/2018 7:56 AM

Whether a 10 HP S1 duty motor can be replaced with 10 HP S4 duty motor.

Whether a 10HP S4 duty motor can be replaced with 10 HP S1 duty motor.

kindly mention why for yes or no for both the cases.

Register to Reply
Pathfinder Tags: motor duty
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15602
Good Answers: 982
#1

Re: Motor Duty

02/04/2018 9:02 AM

The S# duty ratings for a motor refer to how a motor will be used. Properly following these ratings should optimize the lifetime of a motor for the lowest machine lifetime expense. (I don't like how that is phrased.) Bearing clearances are a common difference in these motor ratings but it is not the only difference. For instance, a continuous duty motor can have more "play" in its bearings before reaching thermal equilibrium than a short time duty cycle motor.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
2
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: Motor Duty

02/04/2018 10:14 AM
S1Continuous dutyThe motor works at a constant load for enough time to reach temperature equilibrium.
S2Short-time dutyThe motor works at a constant load, but not long enough to reach temperature equilibrium. The rest periods are long enough for the motor to reach ambient temperature.
S3Intermittent periodic dutySequential, identical run and rest cycles with constant load. Temperature equilibrium is never reached. Starting current has little effect on temperature rise.
S4Intermittent periodic duty with startingSequential, identical start, run and rest cycles with constant load. Temperature equilibrium is not reached, but starting current affects temperature rise.
S5Intermittent periodic duty with electric brakingSequential, identical cycles of starting, running at constant load and running with no load. No rest periods.
S6Continuous operation with intermittent loadSequential, identical cycles of running with constant load and running with no load. No rest periods.
S7Continuous operation with electric brakingSequential identical cycles of starting, running at constant load and electric braking. No rest periods.
S8Continuous operation with periodic changes in load and speed Sequential, identical duty cycles run at constant load and given speed, then run at other constant loads and speeds. No rest periods.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Motor Duty

02/04/2018 10:23 AM

Yes but there might be consequences to the maintenance requirements and life cycle of the motor...in both cases

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#4

Re: Motor Duty

02/04/2018 12:39 PM

Yes for both questions...because you CAN do it, does not mean you SHOULD do it. Depends on the application.

__________________
Tom - "Hoping my ship will come in before the dock rots!"
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#5

Re: Motor Duty

02/04/2018 1:20 PM

You can use the motor rated for continuous duty in the low duty application. It is made to work at rated output 24/7. The light duty motor will probably have a shorter life, as well as a lower cost for low temperature insulation, cheaper bearings etc, when used in 24/7 service - but it will be cheaper. When it fails you must buy another and you will not have any warranty - not made for 24/7. Continuous duty stuff is made better and costs more. Reminds me of the Chinese cheap socket spanners - the ones that break to avoid over stress on bolts and nuts...

__________________
Per Ardua Ad Astra
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Motor Duty

02/04/2018 4:05 PM

Anything <...can...> be done.

It is a matter of judgement as to whether things should be done and the <...why...> will be the outcome of that judgement.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#7

Re: Motor Duty

02/05/2018 4:51 AM

S4 duty is more stringent involving frequent high currents through the stator windings as well as in the rotor.

Hence, it is possible to use S4 duty motor for S1 and not vice versa.

S1 duty motor if used for S4 duty may suffer rotor thermal damage more specifically.

__________________
Raghunath
Register to Reply
2
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#8

Re: Motor Duty

02/05/2018 7:24 AM

Dear Mr. SRINIVASAN,

S1 duty motor can be replaced by S4 duty. But, S4 duty Motor should be replaced only by S4 duty motor and NOT by S1 duty motor.

For S1 duty the frequent on-off will not be there, load will be more or less constant.

But S4 duty motor S is designed for 300 starts per hour and SHOULD NOT BE REPLACED by S1 Motor, since S1 is NOT designed for 300 start-on and off.

Hence the starting current for 300 starts will be always higher, and many times in transient state continuously and some times the motor has to start against the load. The winding temp. of S4 duty Stator as well as ROTOR will be always higher than the S1 duty motor.

Further the S4 Motor will be subjected to sudden or instant reversal direction starting, and the Torque demand will be high and where as for S1 it is not so

Hence S1 duty motor should not be placed and used where S4 Duty is demanded.

DHAYANANDHAN.S

Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #8

Re: Motor Duty

02/05/2018 10:09 AM

"300 starts per hour" is 5 starts per minute. That's a start every 12 seconds.

Are you sure that number is correct?

I'm asking because I can't find any data to verify the 300 starts per hour and believe that the number of starts depends on number of poles and wiring of the motor, also.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#10
In reply to #9

Re: Motor Duty

02/07/2018 10:31 AM

Yes Mr.lyn.

It is 300 starts per hour as specified in INDIAN STANDARDS INSTITUTION. It is 12 seconds gap between starts. Hence the kick load, and winding temp. effect is considerable when compared to S1 duty, Motor is of constant running, no. of starts per hour is less.

I will try to get the copy of the standards and post here, in 2 days time.

DHAYANANDHAN.S

Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#11

Re: Motor Duty

02/08/2018 12:13 AM

Key:

P= load t= time PV= electrical losses TC= time of one load cycle Θ= temperature

ΔtD= starting/accelerating time Θmax= maximum temperature attained ΔtP= operation time at constant load ΔtR= time de-energized and at rest Cyclic duration factor = (ΔtD + ΔtP)/TC

The appropriate abbreviation is S4, followed by the cyclic duration factor, the moment of inertia of the motor (JM) and the moment of inertia of the load (Jext), both referred to the motor shaft.

Example: S4 25 % JM = 0,15 kg × m2 Jext = 0,7 kg × m2

In my opinion,if P[S4]=<P[S1] you may use S1 duty motor as S4.The problem is the bearing could be quickly worn out.

__________________
Julius
Register to Reply
Guru

Join Date: Oct 2012
Location: 100 miles North from the World Center
Posts: 879
Good Answers: 42
#12
In reply to #11

Re: Motor Duty

02/11/2018 12:33 AM

The overlapping of the two duties - S1 and S4 - was unsuccessful. I think the present diagram is correct.

__________________
Julius
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

7anoter4 (2); aurizon (1); dhayanandhan (2); lyn (2); PWSlack (1); raghun (1); redfred (1); SolarEagle (1); Tom_Consulting (1)

Previous in Forum: VFD Troubles   Next in Forum: EOT Crane

Advertisement