LV Blowers & Compressors Stopped During 33kv Incoming Dips

02/16/2018 4:00 AM

Hi All,

We facing 'unknown' phenomenon after our 33kv ( step don to 33/22kv 10Mva and further to 415V 50Hz) incoming power supply dips for about half second.

Here with the observations :

1. All plant lighting flicks

2. 250KW centrifugal compressors x2 , some continuous running , some stopped ( from same transformer 22/.415Kv 2500Kva , loading at 90%

3. Centrifugal blowers 185kw x3 with ABB VSD all stopped

4. But some compressor & blower still continuous to operation which get the power from same transformer

Need advise and point of view from all electrical experts

Thank you & Regards

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: LV blowers & compressors stopped during 33kv incoming dips

02/16/2018 5:00 AM

One wouldn't expect plant of this size to "ride through" a brown-out without some sort of flywheel effect in the equipment.

If the starters for the equipment are required to maintain functionality through the brown-out then some form of uninterruptible power supply facility needs to be added to sustain the contactors through the brown-out, however the plant will start on its own once the brown-out has cleared and the facility may not want that.

The VSDs are behaving as they ought to: await restart after power loss.

Repairing the 33kV supply to prevent recurrence is extremely attractive. One might be able to put pressure on the utility supplier to improve through the commercial arrangements in place between that body and the user.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: LV Blowers & Compressors Stopped During 33kv Incoming Dips

02/16/2018 9:14 AM

What's the question?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: Mar 2009
Posts: 130
#5
In reply to #2

Re: LV Blowers & Compressors Stopped During 33kv Incoming Dips

02/16/2018 8:13 PM

What is possible reasons some blowers & blowers are continuous working and some did not as they are same power source and same configuration.

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#6
In reply to #5

Re: LV Blowers & Compressors Stopped During 33kv Incoming Dips

02/16/2018 11:29 PM

It could be as simple as the tolerance of the coils for electromechanical contactors, maybe some dirt on the face of the laminations that make up the magnetic circuit, or subtle differences in design of the circuits, tolerance of capacitors is often wide. The location of each piece of equipment within the distribution system, where it is connected in relation to other components, could create small voltage differences enough to allow some equipment to maintain, while other drops out.

Without an extremely detailed analysis of all of the components connected in the system, between the equipment that rides through and the equipment that doesn't, I don't think you will be able to come up with just one or two causes for your observation.

Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#3

Re: LV Blowers & Compressors Stopped During 33kv Incoming Dips

02/16/2018 9:20 AM

In power stations, we used to have timer included in the motor stater circuits for all essential drives. The timer is off-delay type and maintains 'close' contact in the power contactor closing circuit (DOL) for 2s. This used to ensure that the subject pump / compressor restarts automatically in case the power is restored to healthy levels within the set time.

In O&G stations, these motors are provided two stage restart scheme.

One, is set for 0.2s and all the drives (essential as well as normal) are allowed to restart immediately and automatically in case the power is restored to healthy levels within 200ms.

The second is only for identified / essential drives and the restart is through a set time delay (if the power is restored after 200ms). This is staggered starting to prevent sudden overloading of incoming power transformer if large no. of drives are to start simultaneously.

May be, your plant requires one such restart scheme.

__________________
Raghunath
Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: LV Blowers & Compressors Stopped During 33kv Incoming Dips

02/16/2018 12:06 PM

A danger in AC induction motor control system design during a momentary loss of power is in re-closing a contactor too soon, BEFORE the magnetic fields in the stator fully collapse. The larger the motor, the longer it takes for the magnetic fields to collapse, that can take upward of 1-1/2 to 2 seconds in some cases. What can happen is that re-applying power after the motor has slowed slightly and the fields are still present, becomes equivalent to connecting two generators together that are out-of-sync; a huge current and voltage spike can take place that can damage other electrical systems and cause severe torque transients in the motors. I have seen it shear off a motor shaft on a 500HP compressor. So "half a second" is an eternity for sine wave power, that's 25 cycles in your part of the world, more than enough to cause this phenomenon. The way that is prevented is to drop out the contactor and have a delay in allowing it to re-close, or require a direct control command to re-close, which can only be given after sufficient time has passed for the fields to collapse.

In the case of a voltage DIP, with no complete loss, you CAN attempt to "ride through" by not allowing the contactors to open or controllers to shut down, either with capacitor devices on the coils, UPS systems on the controls or even using mechanical latching contactors. But doing so runs the risk of the dip being a precursor to a total power loss and having the above scenario take place, so it should be done with the utmost caution and a system that is accurately observing the power.

In your case, it sounds as though nobody has looked at this strategy and you have ended up with some equipment acting one way, some acting the other. Either that or, someone HAS studied this extensively and made appropriate decisions, but you are unaware of them. It would serve you well to get to the bottom of this.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Active Contributor

Join Date: Feb 2018
Posts: 13
#7

Re: LV Blowers & Compressors Stopped During 33kv Incoming Dips

02/17/2018 12:31 PM

The ABB drives are designed to drop out with a low voltage event. They are doing what they need to do, to protect themselves.

The voltage dip is it an inside the plant event or from the utility.

If it is an inside the plant event, you are looking for loose connections or overloaded equipment. You stated that you have motor loads that are 90% of the rating of the transformer. Something that is not very big can put the transformer beyond it's design limits. The age of the distribution system is also a factor. When was the last time the maintenance group went through and verified all the connections.

Remember, "If you did not document it, you did not do it"

Good luck.

A data logger might provide additional information.

Register to Reply
Register to Reply 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aikhh (1); JRaef (1); PWSlack (1); raghun (1); rick_shoop (1); rwilliams (1); SolarEagle (1)

Previous in Forum: Inertia Power System - How Much is Good Enough?   Next in Forum: Need for Switching Station

Advertisement