Power Transformer

03/05/2018 12:51 PM

Greetings

We have 8nos of 80mva power transformers & we r planning to do installations of all accessories of transformer first then we will go for vaccumming,oil filling,leak test,filtration,normalize then precom testing, so as per manufacturer if we installed 1st transformer before moving for 2nd transformer manufacturer recommendations to fill N2 in maintank at 2psi(positive pressure)

Planning to fill from maintank conservator

Conservator as aircell bag which will b kept open (atmospheric pressure will come out from air cell)then N2 will be filled from air bleeding pipe of conservator and will open main tank buchlozz relay valves and oltc valve will b closed (ie., only will n2 in main tank of transformer)

So please share your views,i was planning to do like i this is it ok or not

Register to Reply
Pathfinder Tags: power transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Power transfomer

03/05/2018 1:33 PM

I don't see why not as long as you are careful and don't let any atmospheric air and potential moisture or contaminants leak in to the transformer during the N2 filling.

__________________
jack of all trades
Register to Reply
Participant

Join Date: Mar 2018
Posts: 3
#2

Re: Power transfomer

03/05/2018 1:53 PM

Sure will take care but is it safe way to filling nitrogen becoz i was worried may be it will damage/rapture air cell bag

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Power transfomer

03/05/2018 2:06 PM

Then carry out such precautionary measures as are necessary to avoid this potential problem.

Discussion should be taking place with the manufacturer over the telephone, and not with a bunch of random strangers on a global Engineering forum. However well-intentioned the bunch may be, if the manufacturer's advice is incorrect then some commercial redress is available, which is not the case with the bunch of random strangers.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4
In reply to #2

Re: Power transfomer

03/06/2018 1:21 PM

Good point, I don't know what pressure your transformer is rated for.

Best to contact the transformer manufacturer for guidance.

__________________
jack of all trades
Register to Reply