So i have read from several places that the old rule of them and from other members on this board is
in regards to adding line reactors
If the transformer feeding it is greater then 10 times the KVA of the drive then you should add line reactors.
My question is, If you have one transformer feeder say 2 VFD's should you simply use the same rule but add the KVA of the two drives together?
Thanks for any thoughts
Good Answers: 804
Re: Rule of Thumb for When to Include Line Reactors and When to Not
03/16/2018 6:59 PM
No. You base it on each drive individually. The danger is to the drive rectifier itself, so how many other drives are on the same circuit is irrelevant.
03/19/2018 3:59 AM
Is <...the drive...> CE-marked?
03/19/2018 9:07 AM
I believe so
Why do you ask?
04/09/2018 11:09 AM
You need to size the reactors for each individual drive and install in front of each drive independently.
Dave Oliver