ELR Tripping Sometimes While Starting the Motor Through VFD

04/08/2018 7:31 AM

Hello,

I have recently changed a VFD in my company and after installing the new one (15KW), while switching ON the motor , the earth leakage relay trips ( sometimes). Is it due to leakage current from vfd? I changed the default carrier frequency of vfd from 8Khz to 6 Khz, and then afterwards ,the same ELR started tripping while turning on other motors with other VFDs.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: ELR Tripping Sometimes While Starting the Motor Through VFD

04/08/2018 12:07 PM

Why was the new VFD installed? If the problems occurred after the new VFD was installed, then contact the VFD manufacturer. If there were problems that led to the replacement of the VFD, then make sure that the problems were resolved properly.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
3
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: ELR Tripping Sometimes While Starting the Motor Through VFD

04/08/2018 4:52 PM

Newer VFDs use transistors that turn on faster than old ones, upward of 10x as fast. So that then increases the common mode noise that is created by the drive and that often shows up as causing nuisance trips of ground / earth fault protective devices. Add a shielded isolation transformer ahead of the drive, add common mode chokes (ferrite cores) to the output conductors, make sure everything is properly grounded, turn your carrier frequency down to 2kHZ.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 3)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3
In reply to #2

Re: ELR Tripping Sometimes While Starting the Motor Through VFD

04/08/2018 5:05 PM

This hardly sounds like a step forward if you have to do all that just to make it work properly.....even if it is cheaper...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #3

Re: ELR Tripping Sometimes While Starting the Motor Through VFD

04/09/2018 3:15 PM

Very few drives need to be installed behind Earth Leakage / Ground Fault protective devices that would be sensitive enough to trip on the CM noise involved here. it's a rare enough situation that it's dealt with on a case by case basis. I only brought it up by way of an explanation because the OP had CHANGED from an older drive to a newer one and had not previously experienced it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#4

Re: ELR Tripping Sometimes While Starting the Motor Through VFD

04/08/2018 6:02 PM

Another thing to check is if all the motors are rated for "Inverter Duty". Many older motors are not, and the fast rise times from VFDs have a nasty habit of slowly puncturing the end-turn insulation in them. Many times this incipient failure mode exhibits itself as higher and higher earth leakage current.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Active Contributor

Join Date: Feb 2015
Location: Greater Memphis, Tn. Metro
Posts: 20
#5

Re: ELR Tripping Sometimes While Starting the Motor Through VFD

04/09/2018 11:02 AM

I would highly recommend installing a Line Reactor ahead of the VFD.

__________________
Dave Oliver
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: ELR Tripping Sometimes While Starting the Motor Through VFD

04/09/2018 5:06 PM
  • Question the need for the earth leakage relay.
  • Question its setting.
  • Question the quality of the VFD. If it is new and CE-marked, for example, then this sort of thing shouldn't happen.
  • Question what happens when the VFD is removed from circuit and the motor is started by other means.
  • Evaluate what to do after the above has been completed.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: May 2011
Posts: 76
#8

Re: ELR Tripping Sometimes While Starting the Motor Through VFD

05/08/2018 2:59 AM

Some VFDs equipped with EMC/RFI filters to protect them from the radio frequency which causes capacitive current discharge to ground during power up where using ELR or ELCB is not sufficient, so check with manifacturer.

Register to Reply
Register to Reply 8 comments