Anonymous Poster

motor to be run at higher frequency than it is designed for.

09/14/2007 4:00 AM

i have a 7.5 kw motor , 3 phase, 50 hz , 1500 rpm. that is being used in a dehumidifier.

To vary the speed a VFD is Installed. now to get the required CFM (cubic feet per minute) I hav to run it at 58 hz at all the time.

now please tell me is it advisable to run this motor at 58 hz.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: motor to be run at higher frequency than it is designed for.

09/14/2007 4:15 AM

Provided the motor rating parameters are entered into the VFD correctly then there shouldn't be an immediate problem, as the VFD's on-board control algorithms will look after the motor.

What may be found is that with a fan or blower, because the load varies with the rotation speed raised to a higher-than-unity power, the load current at 58Hz may rise beyond the rated full-load-current of the motor. The VFD should take care of it if correctly programmed either by reducing the motor speed to bring the motor within rated operating limits or by tripping out, in which case a larger motor might be the only solution avaliable to achieve the CFM required; check the cabling size and VFD rating to make sure they are compatible. Of course, if the motor is conservatively rated with respect to the fan size, then this issue might not occur. It can't be seen from here, so it's experimentation time with the installed equipment. It is worth a phone call to the fan supplier's technical help-desk to check the fan/motor combination and its capability at the higher frequency.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: motor to be run at higher frequency than it is designed for.

09/14/2007 9:18 AM

I agree, should be fine as long as the motor is capable of the expected overload. But you also have to realize, once you take a motor over its design frequency, you have run out of voltage to maintain the proper Volts/Hz ratio necessary to continue to create torque. So above 50Hz, you are in what is called "constant power mode" meaning your motor power remains the same and torque is dropping off with increased speed. As PWSlack said, the load in a fan will increase with speed so you get more load with less torque and that results in a rapid increase in overload risk. That overload condition increases at a logarihmic rate as speed over unity is increased, right up to the point where eventually, the motor no longer produces enough torque to spin its own mass. So just be careful and watch everything.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#3

Re: motor to be run at higher frequency than it is designed for.

09/14/2007 11:36 PM

<advisable to run this motor at 58 hz>

You know your job is best done at 58Hz.

You know it works.

You are worried?

Watch the Amps aand feel the Temp when the Work is going on.

Theoretically 58 HZ will be OK for the Motor's Electro-magnetics.

Bearings/winding mechanics always have large margins.

Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#7
In reply to #3

Re: motor to be run at higher frequency than it is designed for.

09/15/2007 6:34 PM

Wow, hold your horses ,

Assuming that this is not a home made unit, but rather a well designed factory made one, where the manufacture specifies a certain CFM at 1500RPM/50Hz. and if the rated RPM is not obtained under these conditions, but at a higher speed (58Hz), that means that the culprit is the blower, more specifically the blade pitch and not the motor or other circuit component... Moreover, If the rated CFM are met at the 58HZ, there is NO additional load on the motor, and the only extra loss will be motor internal heating due to asynchronous conditions. This should definitely be taken into account. If there are no power reserves at the power supply or the motor, than de rating of the CFM should be considered.

That doesn't mean that I disagree with you that nothing Will go wrong for the moment, It may, or may not. But just to focus on what I believe the real problem is.

BTW, what does MUKULMAHANT means? (curiosity killed the cat...)

Wangito.

__________________
Never trade luck for skill.
Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#12
In reply to #7

Re: motor to be run at higher frequency than it is designed for.

09/16/2007 10:13 AM

Thanks Wangito.

  • First things first:Mukul C Mahant is my complete name.
  • Mukul is Old Sanskrit for a flower Bud just going to bloom !
  • Mahant is a Hindu familyTitle meaning Pious Teacher to society's lower strata-and who looks after their spiritual wellbeing-carries on in the family whether you are that or not.
  • Don't blame me-this SURNAMEwas given by somebody 500 years back.

And now the Second part:

WANGITO?

Reply
Guru
Hobbies - HAM Radio - CE3AM....4X4SW....CE3NSW

Join Date: Aug 2006
Location: Santiago Chile.
Posts: 845
Good Answers: 7
#13
In reply to #12

Re: motor to be run at higher frequency than it is designed for.

09/16/2007 2:47 PM

Impressive. And I always thought the old testimony is the leader in saying a lot with just few words. I guess I was wrong...

Wangito is the name of the guy in my avatar. (also Sanskrit if I am not wrong?) who, to my greatest sorrow passed away on August 31st this year, (that is 2 weeks ago) at 12 years of age. The MOST beautiful Chow-Chow ever lived.

Wangito. (Ira G. Curtis...)

__________________
Never trade luck for skill.
Reply
Anonymous Poster
#4

Re: motor to be run at higher frequency than it is designed for.

09/15/2007 7:10 AM

thanks for ur replies

Reply
Anonymous Poster
#5

Re: motor to be run at higher frequency than it is designed for.

09/15/2007 11:20 AM

The motor with V/F can be run at speed In the ratio of 1:10 below synchronous speed.When u run it above syn speed Ie more than 1500RPM to keep V/fcosntant U may have ti raise the voltage. The other problem if Voltage is not raised is lower Torque.More than electrical Mechanical problems may arise like Earlier Failure of bearings,noise etc.If possible try using a 3000rpm (2P) motor and operating it at lower speed .This will also give you a wide speed range ,choice of Higher speed if required comfortably without problems.

Reply
Associate

Join Date: Aug 2007
Location: Boston area
Posts: 38
#6

Re: motor to be run at higher frequency than it is designed for.

09/15/2007 3:21 PM

The motor manufacturer needs to say that running at the increased speed will not damage the motor.

Reply
Power-User

Join Date: Aug 2007
Location: N.E. Alberta 55.6329 N Lat. 111.0729 W Long. Canada
Posts: 216
Good Answers: 7
#8

Re: motor to be run at higher frequency than it is designed for.

09/15/2007 8:40 PM

Hi, check and see if your fan is turning the proper rotation. I have seen many squirrel type fans installed with the rotation indicator pointing the wrong way. The fan will push some air but not as good as the proper rotation almost 45 to 50% less. A 50 Hz motor should rotate at rated rpm if on a vfd and provide you with the proper cfm, if it was engineered prior, something else might be amiss.

__________________
Could be worse, it could be me. :)
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9
In reply to #8

Re: motor to be run at higher frequency than it is designed for.

09/15/2007 9:24 PM

That should NEVER be a design issue on a 3 phase motor! They are all inherently reversing regardless of being driven by drives, so the fans need to work in either direction. If you came across something with that as a problem, it was either one of the worst motor designs I have ever heard of, or it was some sort of customized OEM high temperature motor designed for a specific one-way rotation.

This isn't something anyone should worry about with a standard off-the-shelf 3 phase AC induction motor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Power-User

Join Date: Aug 2007
Location: N.E. Alberta 55.6329 N Lat. 111.0729 W Long. Canada
Posts: 216
Good Answers: 7
#10
In reply to #9

Re: motor to be run at higher frequency than it is designed for.

09/15/2007 11:42 PM

Hi, JRaef, I think you missed the point, the fan could be running in the reverse direction. I have seen fans, centrifugal type, being coupled to a motor and being spun backwards. The motor is not the problem, but the sense of rotation of the fan. I know motors are ambidextrous so are centrifugal fans, they are more efficient when spun the proper way.

__________________
Could be worse, it could be me. :)
Reply
Associate

Join Date: Feb 2007
Posts: 50
#11

Re: motor to be run at higher frequency than it is designed for.

09/16/2007 9:17 AM

The motor won't know or be able to tell what hz is is feed with.

We run some at 15 hz to 40 hz. That same motor we ran up to 180 hz.

At high hz the motor don't have enough torque to start a heavy load.

I say run them.

Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2006
Location: Rochester, NY
Posts: 867
Good Answers: 11
#14

Re: motor to be run at higher frequency than it is designed for.

09/17/2007 8:05 AM

As long as you've got a thermal protection circuit in the motor you should be fine.

__________________
Eric
Reply
Power-User

Join Date: Jul 2007
Posts: 182
Good Answers: 1
#15

Re: motor to be run at higher frequency than it is designed for.

09/28/2007 2:23 AM

Did you ever see the old commercials where they use the blender device to quickly make peanut butter and wip milk shakes? They ran at night and the video was very sloppy with poor editing, if any of you recall.

They were busted for fraud when the service ratings on the motors were being used at double speed for the informercials; exagerating the speed of the process in order to sell the device. I happened to be in the storage lot, by complete accident, when they got raided with the car wax scam, as well.

If you knowingly try to increase planned obsolescence by over driving the prescribed voltages; you will probably be liable for any fire and losses directly; as your device will be out of regulated power prescribed by the manufacturer.

...who cares if your just selling to people far away from a company you are driving into the ground; right?

It doesn't matter if it works temporarily, it's improper to use the motor unless it's within manufacturers spec.; no matter how much it costs to use the correct motor.

"The device most likely cannot be produced at reasonable cost with the proper components", is where I see this going.

Design it right. Use the correct motor.

Filling dumps with raw materials, for a brighter future, is so cool.

Reply Off Topic (Score 5)
Reply to Forum Thread 15 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); Blitz (1); ca1ic0cat (1); fliptop427 (1); JRaef (2); mayt2u (2); Moto (1); MUKULMAHANT (2); PWSlack (1); wangito (2)

Previous in Forum: how to measure the distance using SRM400(Sonar Ranging Module)?   Next in Forum: conductive grease at electrical contact
You might be interested in: DC Motor Drives, Motor Controllers, AC Motor Drives

Advertisement