MCCB and its Ics and Icu

05/18/2018 7:30 AM

hi, if short circuit current is Ik, then which MCCB is selected?

Ics<Ik<Icu

OR

ONLY: Ik<Ics

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: MCCB and its Ics and Icu

05/18/2018 11:33 AM
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: May 2018
Posts: 13
#2
In reply to #1

Re: MCCB and its Ics and Icu

05/18/2018 1:33 PM

no this is not.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: MCCB and its Ics and Icu

05/18/2018 4:02 PM

It depends on what you want.

Icu is the "ultimate" breaking capacity of the breaker, but the breaker does not need to survive the attempt, meaning it can be sacrificed in the task, so long as the fault is interrupted.

Ics is the "service" interrupting capacity, meaning it will interrupt the fault, but will be able to be re-used (after inspection).

Here in North America, the concept of Icu is irrelevant (actually non-existent), our rules require that the breaker be able to re-close and trip again, at least once. So take that for what it's worth.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Active Contributor

Join Date: May 2018
Posts: 13
#4
In reply to #3

Re: MCCB and its Ics and Icu

05/18/2018 4:25 PM

so many thanks for your complete answer.

then for your aria Ics>=Ik is ok. am i right?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: MCCB and its Ics and Icu

05/18/2018 6:42 PM

Yes.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #3

Re: MCCB and its Ics and Icu

05/20/2018 5:48 PM

The definition I have (UK)for Icu is O -t- CO, that is open on short, wait 3 minutes and close onto the fault and open successfully. I think that is much what JRaef wrote. One should always look at the particular standard or ask the manufacturer.

Ics requires that the breaker be suitable for further service after the fault. Ics is basically "refer to manufacturer" but for domestic service type MCB the rated value must be Ics, since a domestic user will reclose several times before resorting to an electrician.

BS EN60947-2, which is commercial & industrial european standard, defines both Icu & Ics. Ics may be 25/50/75/100% of Icu according to that standard.

In domestic & similar service here, there is always an HBC, current limiting, fuse upstream of MCBs which chops off current before it actually reaches the peak value of Ik, that is break before first half-cycle peak. The distribution board & MCBs are actually designed around a stated maximum ""fuse size & type standard in the supply company's incoming cable head.

Register to Reply Score 1 for Good Answer
Register to Reply 6 comments