Re: TRANSFORMER GROUNDING
05/27/2018 4:26 PM
05/28/2018 10:50 AM
is it worthy to prove again and again that you know nothing?
05/28/2018 10:56 AM
You mean, "We" know nothing.
05/28/2018 11:15 AM
Coolyaar, at least Lyn can google, you can learn from him.
Good Answers: 445
Re: Transformer Grounding
05/28/2018 5:56 PM
Because it was designed by someone who used the advice that he got for free from some equally clueless anonymous poster in a forum on the web...
Good Answers: 181
05/28/2018 6:03 PM
So lyn is a “no nothing”? I don’t always agree with lyn but I respect him as one of the backbones of this forum.
Now we should look at some of your previous questions. They show someone that is dangerously incompetent. They also show someone that is idle when it comes to doing basic research.
I think it’s time you took stock of your future career.
05/28/2018 10:09 PM
much of the logic for such an array of equipment depends on the remainder of the distribution system you don't show.
Typically the serving utility would have a solidly grounded source, to be sure you can detect system faults, and stabilize transient voltages generated by distributed line capacitance. In the case of a single grounded leg that couldn't be fixed quickly, I suppose you could shut down the system and open the ground switch connection.
The balance of the equipment could be used to protect the transformer primary winding insulation, while allowing operation with one grounded leg. An intermittent arcing fault can generate transient overvoltages that stress transformer insulation.
05/29/2018 3:43 AM
Yes. The individual who designed it can explain, and this individual's name will be on the documentation for the transformer, which documentation cannot be seen from here.
Good Answers: 42
05/30/2018 3:45 AM
I think that, like most of our colleges, this neutral ground connection is not linked to NEC even directly in IEEE. So I will try to explain this in simple words.
A step-up transformer it is a very expensive part of a power station. Insulation of the high voltage winding is a very expensive part of the transformer so the turns insulation is reduced gradually from terminals to neutral. In this case the system has to be solid grounded. Sometime the high voltage system short-circuit ground fault current is higher than permissible so neutral of transformer has to be disconnected from the grounding and the surge arrester has to protect the transformer neutral for the transients as a lightning phenomenon.
Since the arrestor could be damaged by a very high lightning strike a discharge gap is provided as back-up protection.
Julius
Good Answers: 445
05/30/2018 6:16 PM
Because this drawing is not describing a grounding scheme, but an improperly drawn call-out box for an impulse counter installation. The line drawn to the neutral should have been drawn with an arrowhead pointing to the transformer, which would indicate that the "stuff" in the box was part of a surge counter installation, and is not to be taken literally.
Surge counters are typically installed at the bottom of LAs on transformers when there is a history of equipment failure traceable to high/repeated TOVs (Transient Over Voltage). The spark gap (aka Arcing Horn/Ring) is there to protect the equipment from TOVs that would cause insulator flashovers and carry any subsequent powerline frequency follow-through currents. The two counters give a relative indication of the "normal" LA operations vs. the number of "severe" TOV flashovers across the spark gap.
Notice that there are two dual-core CTs in the grounding conductor of the spark gap, one often goes to the protective-relaying system, the other to a TDR (Transient Data Recorder) and/or SCADA/DAQ system.
The disconnect switch is mislabeled, it is a safety grounding switch that ensures that the lines are de-energized and provides a drain for any random charge buildup on the transmission lines, all for personnel safety.
There is one circumstance where such a setup IS connected to the neutral, that would be if it were installed as part of a high voltage test lab for type-testing of different winding insulation systems. The 30MVA generator makes this an unlikely scenario as presented, especially since no impulse generating equipment and additional testing circuitry is shown.
Good Answers: 42
05/31/2018 12:27 AM
Thank you, RAMConsult. It is very interesting.
Julius
05/31/2018 7:23 AM
thank you for reply. but the setup is actually for a power plant in china.
05/31/2018 10:04 AM
Coolyaar, yes a power plant in China with a overvoltage counter facility and that is the part of the schematic shown.
Good Answers: 445
05/31/2018 10:29 PM
The country is irrelevant, such installations are common in areas of high isokeraunic (lightning) activity, especially for stations that are at the end of very long transmission/distribution lines.
06/05/2018 11:31 AM
This information is hardly trivial so I'm glad some people on the forum take the time to answer for those of us that are not simply incompetent but perhaps not versed in that specific area of engineering. Very interesting information
This forum is a wonderful resource but the bickering and rudeness is rivaled only by a kindergarten playground. It truly is a shame