SEW Motor Protection

05/30/2018 11:29 AM

Hey guys

So im dealing with a local US customer that insists the SEW movi drive motor cables be protected in sometime of conduit. Something like EMT or sealtite.

I have contacted SEW about this and they have no solution for me.

The cable comes from a tray a few feet from the motor. When the cable leaves the tray it is unprotected for the few feet to the motor.

Given SEW has no solution and the servo motor has a big canon style connector on the end i wanted to see if any of you guys had any ideas.

Thanks in advance

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: SEW Motor protection

05/30/2018 12:00 PM

They make split conduit, just check the material specifications for the application....

https://www.ionnic.com/electrical/wiring-accessories/conduit/polypropylene-pp-split.html

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: SEW Motor Protection

05/30/2018 2:24 PM

Does it have to move? If so, you can offer them cable track, like this:

https://www.igus.com/wpck/17556/overview_TriflexR#section_5

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Associate

Join Date: Aug 2013
Posts: 31
Good Answers: 3
#3

Re: SEW Motor Protection

05/30/2018 3:14 PM

An important question is " does the customer expect the cables to be enclosed or open ended. If open the go with the Seal Tite. Diameter large enough to pass the smaller ends through, then mount the seal tite to the frame. If tywraps are acceptable with the customer then go with that.

Register to Reply
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#4
In reply to #3

Re: SEW Motor Protection

05/31/2018 9:20 AM

Thanks for all the info guys

I think the customer simply expects that the NEC is followed.

I cant find any article pertaining to this style of motor cable protection.

Anyone know of an article number?

Thanks

Register to Reply
Associate

Join Date: Aug 2013
Posts: 31
Good Answers: 3
#5
In reply to #4

Re: SEW Motor Protection

05/31/2018 9:43 AM

The design of the cable does not permit full enclosure. Therefore reasonable protection should be utilized. You need to take this back to the customer with your thoughts and find out what they truly expect. You may find that reasonable protection may be all they require.

If they push for full protection, then it is the manufacturers responsibility to make this happen and return a working design.

Accept nothing less from the Manufacturer.

Register to Reply
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#6
In reply to #5

Re: SEW Motor Protection

05/31/2018 11:12 AM

Well, the customer says they wont accept anything other then what the NEC says....

However, since i cant find an article directly related and SEW told me to take a hike on this im not sure what on the NEC i can quote

If they argue for full protection i need to be able to say......

yes or no and here is the supporting article for it....

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #6

Re: SEW Motor Protection

05/31/2018 11:20 AM

Er, what has it got to do with the motor manufacturer? The electrical installation is not the motor manufacturer's responsibility. It is the installer's responsibility to ensure that the installation is in line with the applicable national electrical installation code, in this case the <...NEC...>.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#10
In reply to #7

Re: SEW Motor Protection

05/31/2018 11:31 AM

It has a lot to do with the manufacture.

The motor is deisgned in such a way that you can not practice the standard NEC methods of EMT, rigid, Sealtite ..... etc

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#24
In reply to #6

Re: SEW Motor Protection

06/01/2018 9:57 AM

I suspect your customer is misreading an NEC code. There are two connectors on that motor, not a threaded coupler for mounting rigid or flexible conduit. The NEC code I can find about conduit is code 430.73 :

430.73 Protection of Conductor from Physical Damage.

Where damage to a motor control circuit would constitute a hazard, all conductors of such a remote motor control circuit that are outside the control device itself shall be installed in a raceway or be otherwise suitably protected from physical damage.

If the voltage and current levels to this motor when exposed cannot present a hazard then physical damage protection is not required by NEC code. If this is not acceptable then you cannot run these cables in a cable tray for a raceway is an enclosed channel.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#8

Re: SEW Motor Protection

05/31/2018 11:24 AM

What is in the cable as far as voltage and current levels? This will dictate which NEC elements apply.

If the existing design meets NEC, than ask SEW for a letter of compliance with NEC and present that to the customer. If the customer wants more, then ask for a specification for the improvement and charge accordingly.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#9
In reply to #8

Re: SEW Motor Protection

05/31/2018 11:30 AM

480 about 20A

Register to Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#11
In reply to #9

Re: SEW Motor Protection

05/31/2018 11:34 AM

Then does the flexible cable comply with NEC requirements for a 480V wire run?

Register to Reply
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#12
In reply to #11

Re: SEW Motor Protection

05/31/2018 12:21 PM

What article # specs 480V

Register to Reply
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#15
In reply to #12

Re: SEW Motor Protection

05/31/2018 2:05 PM

Article 400, flexible cords and cables

Register to Reply
Associate

Join Date: Aug 2013
Posts: 31
Good Answers: 3
#20
In reply to #9

Re: SEW Motor Protection

05/31/2018 5:54 PM

Are you saying that is a 480 V motor? or the machine runs on 480 V/ 20A?

I use very similar motors and they are low voltage motors, same cabling etc... these motors have a driver card module? and if yes what Voltage feeds these driver cards?

Just curious Thanks!

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#26
In reply to #9

Re: SEW Motor Protection

06/01/2018 11:05 AM

That doesn't look like a motor capable of handling 10 kilo watts (aka 13 hp) of power.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#13

Re: SEW Motor Protection

05/31/2018 12:25 PM

The NEC section on cord-and-plug connected equipment may be helpful.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#14
In reply to #13

Re: SEW Motor Protection

05/31/2018 12:31 PM

Good call

Any chance you know what article that is?

ill do a search also

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#16
In reply to #14

Re: SEW Motor Protection

05/31/2018 2:07 PM

https://www.sew-eurodrive.it/meta-pages/videoseite_sps_movi_c.html

..."The NEC only applies to premises wiring, not to the supply cords of listed appliances and luminaires."...

http://www.ecmweb.com/qa/code-qa-protection-flexible-cords-and-fixture-wires-0

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#17
In reply to #16

Re: SEW Motor Protection

05/31/2018 4:57 PM

Define list appliance

This is a motor and to me falls under the motor code

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#18
In reply to #17

Re: SEW Motor Protection

05/31/2018 5:27 PM

Are the connectors listed? Are engineered cable connectors the same as field wiring?

https://download.sew-eurodrive.com/download/pdf/16838017_G07.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#19
In reply to #18

Re: SEW Motor Protection

05/31/2018 5:46 PM

It seems to me these connectors are pre-certified by UL, but all specifications must be followed...

https://download.sew-eurodrive.com/download/pdf/23061715.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2014
Location: Hemet, Land of milk and honey.
Posts: 2365
Good Answers: 36
#21
In reply to #17

Re: SEW Motor Protection

05/31/2018 8:07 PM

If it was an unattached motor, then it would be just a motor. If it was without a motor it would be a non motorized assembly. Kind of like a washing machine, because a motor is mated to a motive assembly. If a washer didn't have a motor it would just be a tub.Once the motor is combined with the assembly, it becomes an appliance.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#23
In reply to #14

Re: SEW Motor Protection

05/31/2018 8:44 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#22

Re: SEW Motor Protection

05/31/2018 8:30 PM

I would have SEW supply these units with a cable tray rated cable. Problem solved...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#25
In reply to #22

Re: SEW Motor Protection

06/01/2018 10:06 AM

i think the cable is rated for tray. But that does solve my problem when the cable leaves the tray.

e.g the few feet from the tray to the motor

Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#27
In reply to #25

Re: SEW Motor Protection

06/01/2018 2:32 PM

As long as the cable is properly supported, it should be ok. At least under the CEC (Canadian code) it would be and our code in Canada is pretty much harmonized in those respects. Call a local inspector and ask.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#28

Re: SEW Motor Protection

06/02/2018 6:26 PM

Scott165,

NEC 400.10(A)(8) says that a flexible cord or cable can be used for..."Appliances where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance and repair, and the appliance is intended or identified for flexible cord connection." These servo motor connectors certainly meet this article's intent.

If you look on the jacket of the cable, I suspect you will find the code letters identifying it as a flexible cord or cable, such as type SO or others. You will also find a U/L certification. In the SEW literature you will find information that identifies this cable as the one intended for this motor.

Look at NEC 400.12(6) where the cable shall not be installed in a raceway, "except as otherwise permitted in this Code".

Look next at NEC 392.3089(B), which discusses conductors going from cable tray to equipment, and allows up to 6' of length provided it is "protected, by guarding or by location, from physical damage." Note the word guarding, which does not require enclosure in a conduit of any form.

That last suggests that the AHJ (authority having jurisdiction) should be consulted. In a large plant, the AHJ may be the plant engineer. If you have done the work in accordance with the manufacturer's installation instructions, you should be covered.

I have wired equipment with many servo motors in different locations, many of which were on portions that moved. We used flexible track for the cables when run from fixed to moving sections (or between moving sections) of the machine. Where they ran from track to cable tray, or even to conduits, they were protected by location and by being closely tied to the equipment. There were NO problems with this installation.

--JMM

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Sep 2017
Posts: 76
Good Answers: 1
#29
In reply to #28

Re: SEW Motor Protection

06/05/2018 9:27 AM

Thanks for the input, that is great

Register to Reply
Register to Reply 29 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

catman58 (3); jmueller (1); Jpfalt (3); JRaef (1); North of 60 (2); PWSlack (1); redfred (2); scott165 (9); SolarEagle (5); tonyhemet (1); Tornado (1)

Previous in Forum: Nichrome 6 Properties   Next in Forum: How Will AC Motor Run Under This Condition?

Advertisement