Lifetime/Duration of Circuit Breaker After Short Circuit

06/14/2018 8:47 AM

Dear Sirs :

A circuit breaker has been installed in an electrical panel (presumed short circuit current at the installation site = 40 kA, rated voltage of the panel: 460 Vac / 60 Hz), and has the following characteristics:

Rated current = 100 A

Rated voltage = 460 Vac

Current Icu [rated maximum (ultimate) short-circuit capacity] = 40 kA

Standard of manufacturing : IEC 60.497-2

My question is :

How many short circuit events at the 40 kA (same level of the current Icu of this circuit-breaker) level will this circuit breaker support until it needs to be completely replaced?

Thank you for your opinion/comments

Cláudio Morais

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: Lifetime/duration of circuit breaker after short circuit

06/14/2018 10:33 AM

I think this is variable for each breaker as all the faults are not equal...I generally go by nuisance tripping as the time to replace...

https://www.mikeholt.com/mojonewsarchive/EES-HTML/HTML/ElectricalCircuitBreakers~20030621.htm

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#2

Re: Lifetime/duration of circuit breaker after short circuit

06/14/2018 11:09 AM

This is from the BEAMA guidance notes for EN60947...

<< Icu is tested by a cycle...

Open on fault Icu.

Wait 3 minutes.

Close onto fault at Icu & open.

Carry out overcurrent and dielectric tests to find condition.

......Where 2 or more faults occur between Ics and Icu in service, condition of breaker must be verified suitable for further service.>>

I know that on oil rigs, where fault levels are high everywhere, a breaker is replaced immediately if it has cleared a short circuit.

En60947 defines ratios of Ics - service breaking S/C capacity - to Icu; of 25% to 100%; which should be stated in maker's spec.

In short, Icu really can be an Ultimate maximum and should not be relied upon more than two times. Closing breaker onto fault more than once after initial trip could be dangerous, especially with < 3 min between events.

If the installation has Icu fault level at origin, you should consult the breaker manufacturer about how many shorts are tolerable and set operating rules on site.

If you really must use the Icu of the breaker, you should consider if you should have monitoring equipment which tells you if a breaker opened on S/C or overcurrent and written safety rules based on a safety risk review. If that breaker, only 100 amp, is hand operated; a fail to break could injure or kill .

Remote operation, deliberately at a safe difference, will reduce the risks - always supposing the back-up (HV?) protection will clear fault without major damage to switchboard or starting a fire which destroys the installation.

Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#3

Re: Lifetime/Duration of Circuit Breaker After Short Circuit

06/14/2018 2:24 PM

If you're really concerned about continuity of service and/or protecting the equipment fed by the equipment, then treat the breaker as if it were a fuse and replace it after it opens under a 40kA fault. Of course you'll need to verify that it actually saw that Icu, and then choose what is an acceptable level that avoids replacement; i.e., 38, 35, 30kA??

That's why some circuits use a "belt and suspenders" approach and place High Interrupting Capacity fuses in series with the breaker. The other alternative is to choose a breaker that has an Icu higher than than can be reached by the circuitry.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Lifetime/Duration of Circuit Breaker After Short Circuit

06/15/2018 6:03 AM

How about discussing it with the manufacturer, the name of which has been withheld from the forum, over the telephone?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jun 2018
Posts: 1
#5

Re: Lifetime/Duration of Circuit Breaker After Short Circuit

06/26/2018 7:32 PM

CR4 ADMIN: Deleted Post

Spam: This post was deleted because it contained advertising outside the Commercial Space forum. Please review Section 14 of the CR4 Site FAQ about advertising.

Register to Reply Off Topic (Score 5)
Commentator

Join Date: Feb 2010
Location: West Yorkshire, UK
Posts: 96
Good Answers: 11
#6

Re: Lifetime/Duration of Circuit Breaker After Short Circuit

07/04/2018 11:17 AM

I agree with most of the above - the standard does not define it beyond O-C-O.

Many years ago one of our partners was asked the same question and used our board as a test bed. They equipped it with a range of MCCBs (mostly small up to about 50A) and carried out conditional tests at 50kA (Icu) - repeatedly on the same device. After 10 shots they took them away for investigation and at that point they were all still working. So they could them claim (and prove) they were good for several short circuit events without replacement. Good to know.

On another test (different manufacturer), we did an 80kA short circuit test on an MCCB (100A) which was it's Icu value and it blew up first time - test failed.

So the bottom line is ask the manufacturer and choose with care.

__________________
rogerggbr
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); PWSlack (1); RAMConsult (1); ramd2530 (1); rogerggbr (1); SolarEagle (1)