Hi everyone
I would like to ask about power transformer arrangment
I work at 500/220 KV substation
We have to get new tie transformer but we dont have sufficient area for this extension
Really we need to change the ordinary three single phase power transformer arrangement
We have to put two single phase transformer at same alighment and the third phase will be behind the two another single phases
Now i would ask there is problem if i don't put the three single phase transformer at the same alighment
Specification
Mva for each phase 167 mva
The total power 500 mva
Voltage 500/220 KV
Good Answers: 181
Re: Three Phase Separate Autotransformer 500 MVA Arrangement
07/12/2018 8:20 AM
As long as they’re all clearly identified I can’t see a problem.
07/12/2018 9:49 AM
Thanks for your replay
07/12/2018 9:28 AM
There is not.
However, keep in mind that 3 single phase transformers will be bigger, and hence, more expensive.
Building the future!
07/12/2018 2:28 PM
07/12/2018 12:31 PM
This is the sort of thing that needs to be discussed with the Sales Engineer from the transformer manufacturer. Arrange a site visit for this individual!
07/13/2018 6:32 PM
thanks for you
Good Answers: 445
07/12/2018 1:16 PM
Electrically you will have to ensure that the sequence impedances are not affected by the asymmetrical arrangement of the transformers and interconnecting buswork.
Mechanically you will need to check that the buswork can withstand the asymmetric magnetic forces that will occur when fault currents are flowing during different types of faults/short circuits.
The protective relaying should operate correctly assuming that the burdens are balanced.
07/13/2018 6:35 PM
thanks for you very match
but can i ask you more question if this transformer work in parallel operation with another transformer this arrangement will effect on the parallel operation
also i need sources for point you give me at your comment to collect data more because this points illustration
with my best regards
Good Answers: 445
07/15/2018 6:49 PM
You may be able to parallel them assuming that you provide equal impedance paths between between units and banks, but you have not provided enough information regarding the physical and electrical properties of the arrangement to comment.
Suggest that you get a copy of the "J&P Transformer Book" to learn about how differences in configuration affect the sequqence impedances, especially the zero sequence. There are many fine technical papers regarding the mechanical forces on asymmetrical buswork arrangements. You will find that your favorite search engine(s) will provide many references to both of your inquiries.
07/16/2018 4:15 AM
Thanks very much
In another topic i wrote my thesis (master tgesis and publish paper at ieee conference ) i really hope if i can send it to you to take your opinion about my work at transformer aging and life time assesment