Hi everyone

I would like to ask about power transformer arrangment

I work at 500/220 KV substation

We have to get new tie transformer but we dont have sufficient area for this extension

Really we need to change the ordinary three single phase power transformer arrangement

We have to put two single phase transformer at same alighment and the third phase will be behind the two another single phases

Now i would ask there is problem if i don't put the three single phase transformer at the same alighment

Specification

Mva for each phase 167 mva

The total power 500 mva

Voltage 500/220 KV

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Three Phase Separate Autotransformer 500 MVA Arrangement

07/12/2018 8:20 AM

As long as they’re all clearly identified I can’t see a problem.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Oct 2013
Location: Saudi arabia
Posts: 40
#3
In reply to #1

Re: Three Phase Separate Autotransformer 500 MVA Arrangement

07/12/2018 9:49 AM

Thanks for your replay

Register to Reply
Power-User

Join Date: Sep 2016
Location: SPAIN
Posts: 233
Good Answers: 13
#2

Re: Three Phase Separate Autotransformer 500 MVA Arrangement

07/12/2018 9:28 AM

There is not.

However, keep in mind that 3 single phase transformers will be bigger, and hence, more expensive.

__________________
Building the future!
Register to Reply
Associate

Join Date: Oct 2013
Location: Saudi arabia
Posts: 40
#6
In reply to #2

Re: Three Phase Separate Autotransformer 500 MVA Arrangement

07/12/2018 2:28 PM

Thanks for your replay

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Three Phase Separate Autotransformer 500 MVA Arrangement

07/12/2018 12:31 PM

This is the sort of thing that needs to be discussed with the Sales Engineer from the transformer manufacturer. Arrange a site visit for this individual!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Oct 2013
Location: Saudi arabia
Posts: 40
#7
In reply to #4

Re: Three Phase Separate Autotransformer 500 MVA Arrangement

07/13/2018 6:32 PM

thanks for you

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#5

Re: Three Phase Separate Autotransformer 500 MVA Arrangement

07/12/2018 1:16 PM

Electrically you will have to ensure that the sequence impedances are not affected by the asymmetrical arrangement of the transformers and interconnecting buswork.

Mechanically you will need to check that the buswork can withstand the asymmetric magnetic forces that will occur when fault currents are flowing during different types of faults/short circuits.

The protective relaying should operate correctly assuming that the burdens are balanced.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply Score 1 for Good Answer
Associate

Join Date: Oct 2013
Location: Saudi arabia
Posts: 40
#8
In reply to #5

Re: Three Phase Separate Autotransformer 500 MVA Arrangement

07/13/2018 6:35 PM

thanks for you very match

but can i ask you more question if this transformer work in parallel operation with another transformer this arrangement will effect on the parallel operation

also i need sources for point you give me at your comment to collect data more because this points illustration

with my best regards

Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#9
In reply to #8

Re: Three Phase Separate Autotransformer 500 MVA Arrangement

07/15/2018 6:49 PM

You may be able to parallel them assuming that you provide equal impedance paths between between units and banks, but you have not provided enough information regarding the physical and electrical properties of the arrangement to comment.

Suggest that you get a copy of the "J&P Transformer Book" to learn about how differences in configuration affect the sequqence impedances, especially the zero sequence. There are many fine technical papers regarding the mechanical forces on asymmetrical buswork arrangements. You will find that your favorite search engine(s) will provide many references to both of your inquiries.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Associate

Join Date: Oct 2013
Location: Saudi arabia
Posts: 40
#10
In reply to #9

Re: Three Phase Separate Autotransformer 500 MVA Arrangement

07/16/2018 4:15 AM

Thanks very much

In another topic i wrote my thesis (master tgesis and publish paper at ieee conference ) i really hope if i can send it to you to take your opinion about my work at transformer aging and life time assesment

Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

haysam (5); Ivanov327950 (1); PWSlack (1); RAMConsult (2); TonyS (1)

Previous in Forum: What are Different Fields Where Electrical Engineers Can Work?   Next in Forum: Broken Wire Analysis

Advertisement