VFD Tripping

07/29/2018 5:31 AM

Hi, One of my drive (ACS800) was tripping on over current.After checking motor(110kW,415V) & power cables ,we suspected this to be a problem of drive after discussion with OEM,as it was tripping on no-load run also immediately after motor start command. After replacing the cards & IGBT by the engineer,still the problem remained unresolved as it was now tripping on earth fault immediately upon starting of the motor. We took the trial of this drive with other similar motor and it was running till 200rpm on load.Due to other limitations we didn't run till full load. We again took trial of this drive on original motor in no-load,then it was run upto 100rpm but tripped on earth fault. Kindly share your view points. Thanks.

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: VFD Tripping

07/29/2018 9:10 AM

Sounds like a bad motor....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#2
In reply to #1

Re: VFD Tripping

07/29/2018 5:46 PM

...or bad cabling. You've already proven that the VFD works properly, so it must be associated with something that "touches" the motor.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#3

Re: VFD Tripping

07/29/2018 11:16 PM

Does unbalance inductance plays a role in this ?

Winding resistance: balance 0.08ohm.

Inductance : 0.03mH,0.1mH,0.1mH with power cable

Kindly share your opinion.

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#6
In reply to #3

Re: VFD Tripping

07/30/2018 2:57 PM

For 0.1mH @ 50 Hz....

X = 2πfL = 2 x 3.142 x 50 x 10-4 = 0.03 ohm

R = 0.08 ohm, X < R

You have measured wrong or given wrong units - shaft power/voltage you give would have X ≅ 5 ohm line to star point (L ∼ 15 mH). However, if inductance ratio is correct, something is wrong with motor, maybe shorted turns.

If that "earth fault" is derived from residual of 3 line CTs, you might have insufficient time delay set or too low a current setting to ignore CT saturation imbalance.

Suspecting earth fault, have you done 2.5 kV insulation test on stator??

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#8
In reply to #6

Re: VFD Tripping

07/31/2018 12:42 PM

Hi,

Can you be more detailed about shaft/power ratio.

I will once again check and let you the exact values.

We have done 1000V insulation test on the this motor of 415V.Do I need to check with 2.5kV ?

Thanks.

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#10
In reply to #8

Re: VFD Tripping

07/31/2018 4:02 PM

Apologies for my wrong figures, one has to use locked rotor values!

110 kW shaft power motor @ ξ = 0.9, cosΦ = 0.9, 415V 3 ph

Iph = 110/[0.415√3x 0.9 x 0.9] = 189 amps full load x 6 locked-rotor = 1134 amps.

Z = 240V/1134A = 0.212 ohms, hence X = 0.2 ohms using your resistance measured 0.08 ohm N.B. 0.22 + 0.082 = 0.0464 ≅ 0.2122 = Z2

X = 0.2 = 2πfL L = 0.2/(100π) = 0.64 milliHenry. [a line-line measurement would be higher].

Your measurement of 0.1 & 0.03 mH still seems low.

2.5 kV would be excessive & you have written that motor was rewound so insulation should be OK.

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#11
In reply to #10

Re: VFD Tripping

08/04/2018 1:24 PM

Thanks for the clarification. In my case , i have checked it again.The values has come as below. R-B Y-R B-Y 0.96mH 0.06mH 0.96mH Resistance values are as below R-B Y-R B-Y 0.084ohm 0.108ohm 0.096 Does this indicates inter turn short?

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#12
In reply to #11

Re: VFD Tripping

08/04/2018 5:05 PM

A short may be reason for low value of L, however Y-R seems to have highest resistance.

You should be aware that stator windings are coupled magnetically to rotor. A cage rotor is like a short circuit secondary on a transformer, but rotation of rotor does affect coupling a little since it has copper/aluminium bars in slots in rotor iron circumference. Try different rotor positions.

If possible, I would try applying 12V/30A 50Hz AC supply to each phase & measure current taken with clamp-on meter, to show that this is not just a low level instrument effect.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#13
In reply to #11

Re: VFD Tripping

08/04/2018 5:18 PM

Apologies, I meant to add. You have had a number of parts changed on VFD, but have any filter capacitors to earth between IGBTs & motor been checked or changed? They could connect to earth if faulty & "self-healing" property give intermittent problem.

Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#14
In reply to #13

Re: VFD Tripping

08/15/2018 12:36 PM

Thank you very much for your inputs and for the time you have spent on my questions.

Regarding the issue, we will further check the motor in detail and will revert .

__________________
"Know something about everything and everything about something"
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#4

Re: VFD Tripping

07/30/2018 9:57 AM

Is this an older motor that is not listed as VFD compatible?

I received a replacement motor for a mixer on a tank about 10 years ago, that someone found sitting in a corner of an old warehouse. It must have been 30 years old, was only about 60% efficient, but it had never been run before. That took me and phone calls to technicians from the VFD OEM about 3 days to get the current vs voltage curves just right to allow this antique to run on a VFD. Initially it was as you describe what your VFD/motor combination is doing.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#5
In reply to #4

Re: VFD Tripping

07/30/2018 11:59 AM

It is 8year old motor but was rewounded on last year !

What effects the unbalance inductance causes the vfd to trip overcurrent/earth fault.

__________________
"Know something about everything and everything about something"
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#7
In reply to #4

Re: VFD Tripping

07/31/2018 12:36 PM

It is 8year old motor but was rewounded on last year !

What effects the unbalance inductance causes the vfd to trip overcurrent/earth fault.

__________________
"Know something about everything and everything about something"
Register to Reply
Guru
Engineering Fields - Instrumentation Engineering - EE from the the Wilds of Pa.

Join Date: Feb 2006
Location: middle of nowhere, Pennsylvania
Posts: 2603
Good Answers: 63
#9
In reply to #7

Re: VFD Tripping

07/31/2018 1:04 PM

The motor is most likely VFD compatible. This is not the source of your problem. I am not a motor expert.

__________________
Remember when reading my post: (-1)^½ m (2)^½
Register to Reply