SWITCH GEAR--HOUSEING SOCITY

09/23/2007 8:20 AM

THE BUILDING HAS THREE PHASE POWER sUPLLY 220 V 50 CYCLE,invariably one or two phases are lost,plunging some floors in darkness.is it possible to have jumpers which will restore supply from live phase and automatically disconnect to original supply plan once the supply is restored...site mumbai india

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#1

Re: SWITCH GEAR--HOUSEING SOCITY

09/23/2007 9:41 AM

They are called NEMA switches in the USA. I live in Florida and the switches are used to automatically switch to a backup generator.

They are expensive for single phase, so I imagine 3-phase is going to be costly since they are designed to handle a lot of current.

Register to Reply
Anonymous Poster
#2

Re: SWITCH GEAR--HOUSEING SOCITY

09/23/2007 11:55 PM

there might be a problem in your transformers, you might as well activate your genset to restore your lightings, jumpers is too risky for you and to the building circuitry. better contact a qualified electrical engineer for the troubleshooting required. trace the current from your main supply, down to your main distribution panel for a thorough system check.

Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#3

Re: SWITCH GEAR--HOUSEING SOCITY

09/23/2007 11:57 PM

No

each phase is ideally supplying 1/3 of the power, the remaining phase will probably not be able to deliver the amount of current [power].

there is also the matter of equipment that require 2 phases, the 440volts won't be available.

better to solve the problem causing loss of phase(s)

a back up generator would work, but is probably cost prohibitive.

Register to Reply
Associate
India - Member - New Member

Join Date: Sep 2007
Posts: 26
Good Answers: 1
#4

Re: SWITCH GEAR--HOUSEING SOCITY

09/24/2007 2:28 AM

U can use Auto Matic Transfer Switch which automatically switches to backup generator when the supply is gone and to normal supply hwen it is restored ..

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#5

Re: SWITCH GEAR--HOUSEING SOCITY

09/24/2007 3:41 AM

I would summarize the answers (and agree myself) to the following:-

1) Do not install Nema(?) switches, the most usual effect would be that the last phase would be overloaded and also pop off ! Net effect would be that the whole building is then in darkness....

2) Install DG, suitably sized for the whole building and with automatic start up and switch over. Expensive but effective. A 3 Phase DG would make installing easier than a single phase I would imagine.....but it depends on the cost of the DG and/or the switching equipment....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Oct 2006
Location: New Jersey U.S.A.
Posts: 1114
Good Answers: 38
#6

Re: SWITCH GEAR--HOUSEING SOCITY

09/24/2007 8:15 AM

If this is a industrial building and at times may call for three phase wiring, your motors will not run. We normally have two different supply lines entering our facilities. If one line surges or drops a phase it automatically switches to the other service.

Jumping a phase is a definite NO NO. If you only have voltage on one line of a two or three phase component, current surges occuring on the live line may overload and cause wiring or component burn out unless each is protected by a overcurrent device.

__________________
The last fight was my fault. My wife asked "What's on the TV?" I said "Dust!"
Register to Reply
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#7

Re: SWITCH GEAR--HOUSEING SOCITY

09/24/2007 8:42 AM

Be careful to not backfeed the lines aswell!

__________________
“It's kind of fun to do the impossible.” Walt Disney
Register to Reply