STAR/DELTA QUESTIONS

09/23/2007 2:59 PM

If on a Star/delta motor the U1,V1,W1 wires are removed from the motor and the lables are lost,what is the metod used to find the correct position for the three cables

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: STAR/DELTA QUESTIONS

09/23/2007 3:15 PM

What about other 3 wire ends, U2, V2 and W2 also lost the lables???????

what you mean by three cables?

Starter Panel to Motor terminals or Motor Stator winding to Terminal Box?

Ediri

Register to Reply
Anonymous Poster
#20
In reply to #1

Re: STAR/DELTA QUESTIONS

02/09/2008 4:27 AM

send me wiring diagram for star deltm & deltm star

Register to Reply
Power-User
Hobbies - Fishing - New Member

Join Date: Feb 2007
Location: Suva Fiji Islands
Posts: 229
Good Answers: 3
#2

Re: STAR/DELTA QUESTIONS

09/23/2007 11:08 PM

I am not sure what you are after here please explain a bit better. If you want to know which ends of the windings are which and you know which are U2 V2 W2 just use an ohm meter or preferably a megger to test the windings and find the correct ends. If you dont understand how to do this then I suggest you get an electrician.

__________________
"Multa ferunt anni venientes commoda secum, Multa recedente adimiunt". (The years as they come bring many agreeable things with them; As they go they take many away).
Register to Reply
Participant

Join Date: Sep 2007
Posts: 4
#11
In reply to #2

Re: STAR/DELTA QUESTIONS

09/25/2007 1:49 PM

Thank you for your reply

im still not 100% with it.

Perhaps if i decribe it in another way

if on a star/delta motor all the leads are connected to the motor and are in the right place. Leads u1,v1and w1 are connected to the main contacter but the other ends of the three leads w2,v2 and u2 which would come out of the overload have been disconnected then say there are no lables by the overload to say which position they should be in. what is the method used to find out which one goes where.

Many thanks

Tim

Register to Reply
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#3

Re: STAR/DELTA QUESTIONS

09/24/2007 4:41 AM

You should have 6 cables, three pairs. You can find the pairs with an Ohmmeter. Then, you can connect them as usual.

__________________
Aged man is not old man...
Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#4
In reply to #3

Re: STAR/DELTA QUESTIONS

09/24/2007 6:02 AM

------- if in doubt:

At low voltage:

It must rotate. Then slowly you will gain confidence.

Then you try Star/Delta -- again at lower volts -3 ph.

Register to Reply Score 1 for Off Topic
Anonymous Poster
#5
In reply to #4

Re: STAR/DELTA QUESTIONS

09/24/2007 11:25 AM

What?

Register to Reply
Member

Join Date: Sep 2006
Location: Pennsylvania, USA
Posts: 5
#6

Re: STAR/DELTA QUESTIONS

09/24/2007 11:25 AM

In another life, I was a motor-winder. In the situation your describing, we would connect the motor to a 480V test bench that had the terminals label Phase A, B & C. While facing the drive end of the motor, if it spins counter-clockwise, we would label the lead connected to terminal marked phase A, U1. Phases B & C were marked V1 & W1 respectively. If the motor spins clockwise switch two of the labels. If you have incoming in the plant marked brown, yellow and orange you can use that to. I have assumed you have a direction sensitive application.

I hope I haven't missed the mark for the situation you presented. I hope no one fillets me if I have.

Cheers,

Dan

__________________
99% perspiration, 1% imagination - Edison
Register to Reply
Participant

Join Date: Sep 2007
Posts: 4
#9
In reply to #6

Re: STAR/DELTA QUESTIONS

09/24/2007 2:57 PM

Thank you for your reply

im still not 100% with it.

Perhaps if i decribe it in another way

if on a star/delta motor all the leads are connected to the motor and are in the right place. Leads u1,v1and w1 are connected to the main contacter but the other ends of the three leads w2,v2 and u2 which would come out of the overload have been disconnected then say there are no lables by the overload to say which position they should be in. what is the method used to find out which one goes where.

Many thanks

Tim

Register to Reply
Power-User

Join Date: Jul 2007
Location: The cigarette-stained drunkard living in the cardboard box outside Marks & Sparks delivery entrance, Eastgate Shopping Centre, Basildon.
Posts: 487
#15
In reply to #9

Re: STAR/DELTA QUESTIONS

09/26/2007 10:03 AM

Look.

  • The U1 is connected via a motor winding to the U2 wire.
  • The V1 is connected via a motor winding to the V2 wire
  • The W1 is connected via a motor winding to the W2 wire.

So you can buzz them out with a meter to determine which 1 is connected to which 2, and prove the motor. OK? Before you go any further, put a label on the wires so you konw which one is which. Don't worry about the direction of rotation at this time.

OK. Now for the starter. There should be a wiring diagram for it and if there isn't there damn well should be because you need to be able to determine the following:

  • In star, U1, V1 and W1 are each connected to a phase via the main contactor, and there should be another contactor, the star contactor, energised at the same time to short out U2, V2 and W2.
  • In delta, the shorting contactor de-energises before a third, delta, contactor energises and connects U2, V2 and W2 to the incoming phases, but 120deg out-of-phase forwards relative to their respective 1s. But it needs to be right, otherwise the motor will go from star forwards to delta backwards and the fuses will go if there's a significant load on the motor, and probably if there isn't.
  • That arrangement should be driven by a couple of timers in the control circuit, so that star happens while the motor spins up, then there's a short break, then delta happens. The break is there to give the shorting contactor time to drop away.
  • Contactor 2 and contactor 3 should be mechanically interlocked so that it is impossible for them both to be closed at once. If the interlock is missing and they do then will happen, and you'll lose the supply fuses and probably your eyebrows, every time.
  • Once The Us, the Vs and the Ws are connected properly and the motor spins up in both star and delta, check the direction of rotation. If it's wrong, swap over any two of the phases coming into the starter cubicle.
  • Then connect the motor to the mechanical contraption it is driving and walk away in your Clever Clogs.

There. Dunnit. There's life in the old git yet.

__________________
Essex jobs for Essex yobs! <Burp>.
Register to Reply
Participant

Join Date: Sep 2007
Posts: 4
#17
In reply to #15

Re: STAR/DELTA QUESTIONS

09/26/2007 12:53 PM

Thank you very much for that information

Tim

Register to Reply
Member

Join Date: Sep 2006
Location: Pennsylvania, USA
Posts: 5
#7

Re: STAR/DELTA QUESTIONS

09/24/2007 11:46 AM

Sorry, my previous post should have read:

While facing the Opposite drive end of the motor, if it spins

instead of what I actually posted which was "While facing the drive end of the motor, if it spins"

Check sections 5.1.4 "NEMA Standards Publication Application Guide For AC Adjustable Speed Drive Systems" it is a free download from

http://www.nema.org/

Good Luck

__________________
99% perspiration, 1% imagination - Edison
Register to Reply
Commentator

Join Date: Aug 2007
Posts: 86
Good Answers: 2
#8
In reply to #7

Re: STAR/DELTA QUESTIONS

09/24/2007 2:54 PM

At last ,a confession,after all these years of rewound motors which never have the windings marked correctly,and ALWAYS go the wrong way.(unless star/delta when they hum ominously in delta before the overload melts)

Your retraction was too late,now we know it was deliberate,not a 50/50 chance.

Register to Reply
Member

Join Date: Sep 2006
Location: Pennsylvania, USA
Posts: 5
#10
In reply to #8

Re: STAR/DELTA QUESTIONS

09/25/2007 12:08 PM

"Your retraction was too late,now we know it was deliberate,not a 50/50 chance." Thanks for the fillet, you are so cute. It was my first post and I didn't know there was a time limit. I was actually preparing my lunch.

I was also assuming it was a 6 lead motor and the other sides would "ring out" and be labeled accordingly, then terminated based on the contactor. If it had 9 leads it would have led to a different suggestion.

If you were getting motors rewound and had this problem "wrong way... [Or] ...hum ominously" then either your incoming wasn't phased properly or you picked bad motor shops to do business with. Any motor shop, worth its salt, will have the leads labeled to the NEMA standard connection diagram before it ships.

__________________
99% perspiration, 1% imagination - Edison
Register to Reply
Commentator

Join Date: Aug 2007
Posts: 86
Good Answers: 2
#13
In reply to #10

Re: STAR/DELTA QUESTIONS

09/25/2007 6:47 PM

'Too late' referred to the sequence of events,not the timing.Please feel free to lunch or otherwise refresh yourself at any time. Unfortunately our old fashioned British rewind shops didnt seem to bother with the niceties of labeling and felt justified in presenting the re-installer with an intellectual challenge,'if you can't sort out the connections you shouldnt be messing around with electricity.' was the gist of the reply to the one complaint I ever made.

Register to Reply Off Topic (Score 5)
Member

Join Date: Sep 2006
Location: Pennsylvania, USA
Posts: 5
#16
In reply to #13

Re: STAR/DELTA QUESTIONS

09/26/2007 11:48 AM

Some american rewind shops are no better. Especially if you just send the motor in for cleaning and varnishing. They think, if the motor didn't come in with labels, why should they put them on. It can happen in our larger shops but that is generally when the teenager in the steam cleaning shack blows the labels off. And I am extremely sorry that anyone would respond to your complaint with ..." 'if you can't sort out the connections you shouldnt be messing around with electricity.' when they should have said, "If you don't feel comfortable having me talk you through it, I will send someone to your facility to label the motor leads and check polarity with your assistance." I think this kind of leadership is what made the owner of my company very successful.

In advance please forgive my american grammar;

Cheers,

Dan

__________________
99% perspiration, 1% imagination - Edison
Register to Reply Off Topic (Score 5)
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#12

Re: STAR/DELTA QUESTIONS

09/25/2007 4:36 PM

Also see:

http://globalspec.ip09.com/rd/9z1zitld5a93s7qelrn1f9s2aftnica3ghhtlma8t00

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#14

Re: STAR/DELTA QUESTIONS

09/26/2007 6:46 AM

Hi all, we are unnecessary complicating the matter. Looking at the terminal box of motor from left to right U1, V1 & W1 as convention. Verify

__________________
BNDas
Register to Reply
Anonymous Poster
#18

Re: STAR/DELTA QUESTIONS

01/02/2008 1:21 AM

please send star delta connection & drawing and how to check winding fault?

Register to Reply
Power-User

Join Date: Oct 2006
Location: Kolkata, India
Posts: 447
#19
In reply to #18

Re: STAR/DELTA QUESTIONS

01/02/2008 1:42 AM

I think you have to go for professional consultation.

__________________
BNDas
Register to Reply
Anonymous Poster
#21

Re: STAR/DELTA QUESTIONS

08/07/2010 4:39 AM

hi am looking for some

drawings for connecting eletric motors as i need them for study as i dont no were to get them mainly 3 phase like star delta