Concealed PVC Conduits Running on Wall

09/09/2018 9:30 AM

Hi,

I want to know whether we can run pvc conduits concealed on wall "Horizontally" ?

As per IEEE/ IEC do we have any regulation stating that we should not run conduits horizontally on wall?

I am referring to electrical works for commercial, factories an mall buildings.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: concealed PVC Conduits running on wall

09/09/2018 11:24 AM

Generally speaking it may be allowed where the PVC is embedded in concrete or buried, or supported continuously, mostly in corrosive environments...but generally speaking, mostly no....Conduit is used mostly to protect the wire or cable from damage, and PVC is known to become brittle over time, and in high heat environments it sags...it just doesn't hold up well over time when exposed to the elements....

https://www.ecmweb.com/design/fast-cheap-and-out-control

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4
In reply to #1

Re: concealed PVC Conduits running on wall

09/09/2018 1:34 PM

Or, you could just hang it on the wall, like this:

Code? Code? I don't need no stinking codes!

Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #4

Re: concealed PVC Conduits running on wall

09/09/2018 2:01 PM

Yeah looks OK new....but in a few years

...not so much...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#6
In reply to #5

Re: concealed PVC Conduits running on wall

09/09/2018 2:45 PM

Nope! It'll still look new 10 years from now.

I've got plenty of conduit clips and concrete screws, if it does sag a little.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#7
In reply to #6

Re: concealed PVC Conduits running on wall

09/09/2018 4:17 PM

..."One of the major concerns when installing long runs of PVC is the amount of length change that can happen due to thermal expansion and contraction. For example, according to Table 352.44 a 100-ft-long run of PVC exposed to a temperature change of approximately 100°F will experience a change in length of about 4 in. Sec. 352.44 requires expansion fittings to be used where the length change in a straight run of PVC installed between securely mounted items is expected to be ¼ in. or greater. If an expansion fitting is not used, as was the case for the installation in this photo, then the PVC will start to bend, buckle, twist, and turn until it eventually self destructs.

Another contributing factor to this self destruction is the lack of supports. Table 352.30 requires PVC sized 1 in. and smaller to be supported every 3 ft."...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#8
In reply to #7

Re: concealed PVC Conduits running on wall

09/09/2018 4:42 PM

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#9
In reply to #7

Re: concealed PVC Conduits running on wall

09/09/2018 5:06 PM

You're wasting a lot of time chasing your tail to prove something, not sure what.

The pipe is, by design, not constrained, just securely supported about every 24-30 inches, not 36. There is an expansion joint in the middle of the 22 foot run.

I'm pleased with the installation and the kids like it just fine when they are playing basketball at night.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#10
In reply to #9

Re: concealed PVC Conduits running on wall

09/09/2018 5:32 PM

Then there shouldn't be any problem....this was more for the OP/thread than you....I'm sure you can install a few lights properly....even though I would have installed fewer larger higher lights than those pictured, you probably had your reasons...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#11
In reply to #10

Re: concealed PVC Conduits running on wall

09/09/2018 6:06 PM

Two reasons.

These lights were free, removed to make way for light rail system, and no one wanted them.

The installed height meant the neighbors across the wall couldn't see them, and eliminated any potential light pollution problems of the other neighbors in the direct path because our lot is pie shaped, on a cul-de-sac so the wall lights face away, more of less away, from them.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#12
In reply to #11

Re: concealed PVC Conduits running on wall

09/09/2018 8:47 PM

So what yer sayin is you stole the lights and you don't want the neighbors to see 'em.....haha

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#2

Re: concealed PVC Conduits running on wall

09/09/2018 11:37 AM

In industrial area you usually have cable trays.

__________________
Common Sense Dictates
Register to Reply Score 2 for Off Topic
Guru

Join Date: Mar 2012
Location: Out of your mind! Not in sight!
Posts: 4424
Good Answers: 108
#20
In reply to #2

Re: concealed PVC Conduits running on wall

09/11/2018 9:24 AM

Whoever voted that OT should kindly explain what is wrong with cable trays!

Thanks!

__________________
Common Sense Dictates
Register to Reply Off Topic (Score 3)
Guru
Engineering Fields - Instrumentation Engineering - New Member Hobbies - Automotive Performance - New Member Technical Fields - Education - New Member Fans of Old Computers - TRS-80 - New Member Hobbies - Musician - New Member

Join Date: Jan 2008
Location: Tucson, AZ
Posts: 1331
Good Answers: 30
#3

Re: concealed PVC Conduits running on wall

09/09/2018 12:15 PM

PVC is not conductive and thus cannot act as "earth ground" for safety.

__________________
...and the Devil said: "...yes, but it's a DRY heat..!"
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13

Re: Concealed PVC Conduits Running on Wall

09/10/2018 4:20 AM

The electrical regulations pertaining to the country of installation (for example BS7671 in the UK) will state whether it is permitted by way of standard. Deviating from standards is the same as sticking one's head above the proverbial parapet and, in the event of an incident, makes one rather unpopular with the facility's fire insurers and liable to prosecution in the event of injury or death. Another risk is unintended, catastrophic and irreversible discharge from employment, which may not be very desirable.

<...can...> The forum is in no position to comment on contributors' abilities. If in doubt, use a qualified local Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#14

Re: Concealed PVC Conduits Running on Wall

09/10/2018 9:15 AM

If on a wall, how is it concealed?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member United Kingdom - Member - New Member

Join Date: May 2007
Location: Harlow England
Posts: 16512
Good Answers: 670
#15
In reply to #14

Re: Concealed PVC Conduits Running on Wall

09/10/2018 9:36 AM

Camo' paint?
Del

__________________
health warning: These posts may contain traces of nut.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#16
In reply to #15

Re: Concealed PVC Conduits Running on Wall

09/10/2018 2:30 PM

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1368
Good Answers: 105
#18
In reply to #14

Re: Concealed PVC Conduits Running on Wall

09/11/2018 12:00 AM

no one including OP has mentioned how & why you might bury the conduit inside a wall, and no mention of how & where it emerges from the concealed location. It could be similar to buried conduit, except in a wall? That has some horizontal components...

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#19
In reply to #14

Re: Concealed PVC Conduits Running on Wall

09/11/2018 3:33 AM

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Engineering Fields - Civil Engineering - Member

Join Date: Mar 2011
Location: ''but, don't we get PAID to ask questions?...''
Posts: 1661
Good Answers: 17
#17

Re: Concealed PVC Conduits Running on Wall

09/10/2018 4:53 PM

Outdoors, no, but indoors, maybe...

__________________
''illigitimi non carborundum...''(i.e.: don't let the fatherless (self-deluding,sabotaging, long-term-memory-impaired, knee-jerking, cheap-shotting, mono-syllabic, self-annointed, shadow-lurking, back-biting, off-topic-inquisitors) grind you down...)
Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Oct 2011
Posts: 20
#21

Re: Concealed PVC Conduits Running on Wall

09/17/2018 12:29 AM

Guys...

Thank you for your responses,

still i dint get my answer, let me put in simple way,

conduits are used in internal hotel building, inside the guest room.

we tried to do concealed conduit inside guest room running horizontally but i am worried if we any any regulation saying that we cant run horizontally on wall as per BS/IEE/IEC ????

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#22
In reply to #21

Re: Concealed PVC Conduits Running on Wall

09/17/2018 12:35 AM

Register to Reply
Register to Reply 22 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

70AARCuda (1); IdeaSmith (2); lyn (5); mannsyed (1); MR. Guest (1); PWSlack (2); rwilliams (1); SolarEagle (7); Tornado (1); user-deleted-1105 (1)

Previous in Forum: Micom P545   Next in Forum: Power MOSFET Blew Up When Increased Duty Cycle From 5% to 10%

Advertisement