09/23/2018 7:58 AM

Hi People, I got a number of 3 phase outlets with Earth pin and NO NEUTRAL, that are currently protected by 3pole Type D, Circuit Breakers but no earth leakage protection.

What brands/manufacturers offers RCDs that will protect 3 phase outlets without neutral. (Clipsal 4pin 500Vac 50Amp)

These outlets are used for different loads of different sizes but not exceeding 50Amp.

Thanks for any assistance/ ideas.

__________________
Observe-Plan-Execute-Monitor-Control
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: 3 Phase 3 Wire & Earth Supply, Earth Leakage Test

09/23/2018 1:31 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2014
Location: Port Macquarie N.S.W. Australia
Posts: 1071
Good Answers: 225
#2
In reply to #1

Re: 3 Phase 3 Wire & Earth Supply, Earth Leakage Test

09/23/2018 5:09 PM

Be a bit cautious there.

These 3 phase RCDs generally pass all 3 phases through a toroid to accurately determine that equal currents are present in each phase - ie none flowing to earth etc., which is fine until you use only 2 of those phases for control purposes.

Manufacturers often recommend fitting a resistor when a neutral is not continued to the device, but this only permits the test function to work. Control equipment across 2 of the phases (which is the common method of control for 3 phase equipment where no neutral is present) creates an out of balance situation which can cause much nuisance tripping.

Register to Reply
2
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#4
In reply to #2

Re: 3 Phase 3 Wire & Earth Supply, Earth Leakage Test

09/24/2018 1:22 PM

The unbalanced current for controls or single phase L-L loading normally returns on the conductors that pass through the current transformer, so unbalanced phase loading will not upset a zero sequence current transformer.

However, the caution is appropriate insofar as the sensitivity of this method is much less than other ground fault detection methods, due to internal CT saturation and the inductive characteristics of the sensing device connected to the current transformer. Many of these combinations required actual component testing to predict the pickup point where the relay could sense a ground fault.

Register to Reply Good Answer (Score 2)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: 3 Phase 3 Wire & Earth Supply, Earth Leakage Test

09/24/2018 7:39 AM

A 3 pole RCD will work perfectly well with 2 phases so long as they are balaced.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5

Re: Three-Phase Three-Wire and Earth Supply, Earth Leakage Test

09/25/2018 3:36 AM

All the equipment does is identify whether the sum of the currents passing through it at any moment exceeds the trip setting, and, assuming this sum current is passing along an earth conductor (which might be a human) trips to disconnect the supply for safety. So, anything that works with a <...NEUTRAL...> conductor will also work without it.

If in doubt, consult a qualified local Electrician.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 5 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

PWSlack (1); rwilliams (1); SolarEagle (1); spades (1); TonyS (1)

Previous in Forum: Ice Loading on Transmission Lines   Next in Forum: Construction Power for Substation

Advertisement