09/25/2018 9:51 AM
Dear Sirs,
It appears to me that substation construction power are basically lighting loads (2 kW), welding loads(2*7 kVA for two welding machines) and oil filtration plant for (maybe 5 kW ?). This makes 25.12 kVA load. For this 50 kVA distribution transformer would be sufficient.
I am not so sure about load for oil filtration plant.
Any other ideas?
Best Regards,
Re: Construction Power for Substation.
09/25/2018 10:24 AM
Well, it all depends on the design of the substation. You might need low-voltage for transformer cooling fans. Any telemetry equipment will probably require low-voltage to feed their power supplies. Some substations require perimeter surveillance equipment to deter theft and foolish suicides. Motors for remote switching will probably need low-voltage. You might even need outdoor lighting. You probably won't need to heat a hot tub but if the customer wants one...
Good Answers: 131
09/25/2018 3:45 PM
Redfred, I think the OP is talking about (temporary) construction power, not accessory power for misc loads in the substation.
To the OP: You need to find out what equipment your installers / constructors of the substation expect to use. Besides tools and installation equipment, they may have a construction trailer or other shelter that needs lights, heat, power for computer, etc. You can't just guess. However, based on projects I have dealt with, I'd say 50kVA is plenty for what is likely to come up unless it is a very large substation with multiple constructors and their facilities. But your best bet is to talk to the various constructors and get their power needs from them.
09/25/2018 6:02 PM
If this is electric power for construction then I would expect the construction contractors will be using their own generators instead of tapping into the high voltage grid to make a substation. I also wonder what kind of oil filtration needs to be performed to construct a substation. A simple funnel, filter paper, two buckets and gravity can filter oil, albeit very slowly.
09/25/2018 11:16 PM
Hi Redfred,
When you commission a big transformer (s) you are talking about twenty foot containers full of oil that you have to heat filter and recirculate under a vaccuum for up to several days to get it to meet the vendors requirement, for temperaure and dryness, then you top it wth pressurized dry nitrogen. The last one I did was in 95 , so I dont remember the exact power requirement of the filtration skid ( Also a twenty foot container full) but it was in the range of 40 or 50 amps / 3ph /380 vac.
Best,
Expat
09/26/2018 11:33 AM
That's interesting to know, thanks.
Still, this is a temporary task. I would expect whoever is contracted to perform this commisioning work will have their own equipment requirements covered in one of two ways. They will bring all that they need or specify in their contract that which must be provided.
09/25/2018 11:50 AM
If you're building a POWER substation, wouldn't you already have POWER for the construction phase?
Electrical Substation Design, Modification & Construction
Your Guide to Electrical Substation Construction - NU Transmission
09/25/2018 3:56 PM
<...This makes 25.12 kVA load....> Actually, it makes 21kVA.
As to <...ideas...>, contact the vendors of the oil filtration plant and get a <...so sure...> figure!
Good Answers: 137
09/26/2018 10:36 AM
No, it's 7kW for the lighting + oil filtration plant, 14kVA for the welders. It would be 21kVA if the lighting + oil filtration plant had PF 1. Incandescent lighting has PF 1, but fluorescent and LEDs are lower. We don't know what lighting the OP has. The oil filtration plant is likely to be less than 1.
09/27/2018 4:47 AM
Whatever. The OP still needs to the oil filtration plant vendor, and discuss.
<unsubscribes>
Good Answers: 117
09/25/2018 11:49 PM
I have an idea.. go back to school and learn how to calculate loads!
If you can't work out a simple load, and have your considered 'diversity', then you are in the wrong job!
Harsh? Yes!
Reply Score 1 for Off Topic