Hi,
I am in the process of commissioning a micom P443 device. The opto inputs are now confingured but when I activate any of them by applying a DC Voltage, the status in display does not change. I expect the status to change from 0 to 1 according to the configuration but this is not happening.
what could be wrong here?
Re: Micom P443
09/26/2018 12:49 PM
Re: Micom P443
09/26/2018 2:43 PM
How much current flows? A nominal current flow for an optocoupler LED is 10 mA.
Good Answers: 19
Re: Micom P443
09/26/2018 10:25 PM
Generally for the inputs source of DC voltage is taken from the relay.
If input is given from external source , both positive and negative to be connected to the relay.Therefore check connection.
Ramesh,Freelance Electrical/automation Consultant