We are having 4 compressors which are tripping more frequently.
The name plate details of the motor are as follows.
1.Simo
Type:YLF3151.1-4F,160 KW380V,50Hz,289A,CONN:Delt
Input Voltage;RY Phase=398.3 Volts,RB Phase=395.6 Volts,YB Phase=391.3 volts
R Phase current=269.7A,Y Phase current=256.7A,B Phase=237.5A
Resistance RY=88.5 Ohm,RB=86.2Ohm YB=85.8Ohm
Inductance RY=1.122 , RB=1.106, YB=1.127 Thermal overload relay is set at 300A
2nd Motor:
Type:YLF3151 ,160 KW380V,50Hz,289A,CONN:Delt
Input Voltage;RY Phase=363.9 Volts,RB Phase=359.8 Volts,YB Phase=350 volts
R Phase current=288.8A,Y Phase current=300.9A,B Phase=280.7A
Resistance RY=100.7 Ohm,RB=110.2 Ohm YB=96.9 Ohm
Inductance RY=1.002 , RB=1.005, YB=1.00 Thermal overload relay is set at 300A
3rd Motor:
Type:YLF3151 ,160 KW380V,50Hz,289A,CONN:Delt
Input Voltage;RY Phase=347.8 Volts,RB Phase=345.8 Volts,YB Phase=344.5 volts
R Phase current=316.8 A,Y Phase current=325.2 A,B Phase=294.5 A
Resistance RY=92.8 Ohm,RB=85.2 Ohm YB=85.1 Ohm
Inductance RY=1.040 , RB=1.011, YB=1.029 Thermal overload relay is set at 300A
4th Motor:
Type:YLF3151 ,160 KW380V,50Hz,289A,CONN:Delt
Input Voltage;RY Phase=358.3 Volts,RB Phase=352.5 Volts,YB Phase=356.5 volts
R Phase current=315.9 A,Y Phase current=305.5 A,B Phase=295.9 A
Resistance RY=97.7 Ohm,RB=97.8 Ohm YB=94.8 Ohm
Inductance RY=1.130 , RB=1.122, YB=1.139
Each compressor breaker is Schneider make,CVS 400--630.The tripping is set that Ir=320A and Isd=4xir. Thermal overload relay is set at 300A
the schneider breakers are tripping frequently .Rarely thermal overload relay is tripping.
We want to know how to eliminate the tripping.The readings are taken at different timings.We are not knowing whether the difference of resistance and inductance in each phase winding plays what type of role in this tripping. I request to guide me for me the further action.And some times all the 3 compressors are tripping at a time.Some times 2 compressors are tripping at a time.Kindly guide us.