11 comments
Rate Comments: Nested
Anonymous Poster #1

Number of Motor Starting

10/07/2018 7:16 AM

Hi dear,

I need to configure one Siemens continuous duty (S1, Design H) type motor to gap control. If it is implemented then the fan motor will start & stop number of times per day according to the process temperature. Unfortunately, the IEC 60034-12 standard is not available with me, so I need more confirmation from you guys about this matter. I think the continuous type motor frequently start / stop will damage the motor. Please share your thoughts and inputs.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#1

Re: Number of Motor Starting

10/07/2018 9:35 AM

Unfortunately, the IEC 60034-12 standard is not available with me ...

Here it is.

https://www.sis.se/api/document/preview/569004/

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Number of Motor Starting

10/07/2018 10:29 AM

<...standard is not available...> What nonsense! A telephone call and a credit card can change that on any <...standard...> at any time, anywhere on the planet. Rumour has it that one can even do that over the internet these days...

<...think...damage the motor...> A simple telephone call to the motor manufacturer, or, better, a review of the manufacturer's data sheet for the motor, will yield information about the maximum recommended starting rate.

<...you guys...> There is nothing in this forum preventing varying the inclusion. Posting anonymously doesn't make any headway in that direction though.

Anonymous Poster #1 just isn't trying hard enough.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Off Topic
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#3

Re: Number of Motor Starting

10/07/2018 11:56 AM

The critical factor here, assuming you have proper sized motor for load, is the insulation class....frequent starting and stopping can increase the operating temperature of the motor....the motor must be designed to handle this heat or it's life will be cut short...

https://www.machinedesign.com/blog/5-common-motor-myths

Always best to chose a higher insulation class than you think you need...

http://sites.ieee.org/houston/files/2016/01/3-Fundementals-of-Motors-IEEE-Houston-February-2015.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#4
In reply to #3

Re: Number of Motor Starting

10/07/2018 11:42 PM

In most cases, induction motor designs are rotor limited, so that needs to be checked first. You need to know the Wk2 of the load, and the voltage available at the motor terminals during start, from which you can calculate the starting & acceleration torque. From that you can calculate the time when the stator field is much faster than the rotor field, which causes large amounts of current to flow in the rotor bars, raising the temperature of the rotor.

NEMA has some standards that are incorporated in standard T Frame motors. There are also rules of thumb for motor designs that are likely to be stator limited, usually high voltage and small horsepower.

NEMA motor starts Shows an excerpt of the design compliments of L&B Electric, more detail is available in the NEMA Standard.

in cases I’ve investigated, the Actual Motor Design parameters are the safest ones to use, as our PWSlack always postulates. Usually takes about 5 phone calls, detailed information of the driven load, but the designer does know at what point the heat in the rotor starts softening components.

Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#5
In reply to #4

Re: Number of Motor Starting

10/08/2018 12:39 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6

Re: Number of Motor Starting

10/08/2018 1:05 AM

The most onerous duty for motors from rotor heating point of view is, stopping the motor before it reaches full speed and then starting again before the motor speed comes to standstill. If this has to happen again and again, better be careful in selecting the right duty motor.

__________________
Raghunath
Reply
Guru

Join Date: Apr 2017
Location: Southern Illinois
Posts: 627
Good Answers: 13
#7
In reply to #6

Re: Number of Motor Starting

10/08/2018 9:56 AM

"...then starting again before the motor speed comes to standstill".

Does this only apply to motors with starting centrifugal switches or all motors? I've never really thought about how that would affect motors started with motor-controllers.

But, with across-the-line starting without any special starting sequence, I'd think that the residual kinetic energy would make the subsequent start less stressful. Am I wrong?

__________________
Science is the "cookbook" for making things.
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Number of Motor Starting

10/08/2018 11:25 AM

<...the residual kinetic energy would make the subsequent start less stressful...> Sounds good from here.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9
In reply to #7

Re: Number of Motor Starting

10/08/2018 11:51 AM

True provided, the back emf has died down completely.

__________________
Raghunath
Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#10
In reply to #9

Re: Number of Motor Starting

10/08/2018 5:01 PM

or as VFDs often provide, the re-application of voltage is synchronized with the rotor speed, often called 'flying start' in VFD parameter-speak.

Reply
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#11

Re: Number of Motor Starting

10/20/2018 10:03 AM

What do you mean by "gap control"??
The standard writes that you can have two starts from cold or one from hot with a certain inertia constant & motor torque constant at rated torque during start.
What you need is the starting time & motor voltage for your fan application. An assumption that current is at "locked rotor value" during start is reasonable and will give a margin for life. You really need to work with the actual motor voltage during start, which may be as low as 80% nominal due to supply & cable impedance.
It would be essential to know the heating and cooling time constants of the motor to find the effect of any cycle of run-time & stop time. These constants are not part of a standard.
However, if you determine the expected cycle, the motor maker is best placed to advise on the acceptability of the cycle. You should investigate if the use of a variable speed drive would not have benefits in reduction of motor size/thermal shock to process or motor and high starting currents/low power factor on supply.
So your most important task is to to extract the required duty cycle for your process from its designers.....the questions "what do you usually do?" and "what would you really like to do?" come to mind.

Reply
Reply to Forum Thread 11 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (1); Dennis R. Levesque (1); PWSlack (2); raghun (2); Rixter (1); rwilliams (2); SolarEagle (2)