Tertiary MVA of Autotransformer

10/05/2018 6:13 AM

Dear Sirs,

What could be the tertiary winding rating if the 3*50 MVA single phase autotransformer forms one three phase 150 MVA autotransformer?

Is it normally 1/3rd the size? We have to supply a load with it (cannot say precise load at the moment).

Are there problems associated with auto-transformer tertiary loading?

Best Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Tertiary MVA of autotransformer.

10/05/2018 6:14 AM

What did the transformers' manufacturer say during the telephone calls on this topic?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Tertiary MVA of autotransformer.

10/05/2018 11:03 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply
Power-User

Join Date: Sep 2016
Location: SPAIN
Posts: 233
Good Answers: 13
#3

Re: Tertiary MVA of Autotransformer

10/05/2018 6:53 PM

Absolutely no.

Usually transformers have one winding, not even a second, so your question is very confusing.

Each winding should have a power rating. Provide the nameplate if you do not know how to interpret it. 1/3rd is very likely to be wrong.

__________________
Building the future!
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#4

Re: Tertiary MVA of Autotransformer

10/07/2018 2:47 PM

Are you talking about a custom transformer which includes an additional winding for local utility power purposes? If so 1/3 seems way too high to me. 50-500kVA perhaps.

What's the additional winding actually being used for (or is this all a hypothetical situation)?

__________________
jack of all trades
Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#5

Re: Tertiary MVA of Autotransformer

10/10/2018 9:04 AM

A tertiary winding on a large power autotransformer is often used for auxiliary power requirements such as station service. That is not uncommon. The rating of that tertiary winding should be shown on the transformer's nameplate, with an MVA or KVA rating for each winding. If the nameplate doesn't show it (it should!), the manufacturer will be able to tell you.

__________________
To get the right answers, first you need to ask the right questions.