Surge Arrestor Blast

10/05/2018 2:33 AM

I have been working in the electrical construction, operation & maintenance field for about 35 years now. I have worked on all voltages from 240V to 420kV. All along my experience, I have never heard of a surge arrestor blast. For me, surge arrestor is such a device, which would act as an insulator until the voltage across it does not increase beyond its rated voltage. And, when the voltage across the surge arrestor goes beyond its rated voltage, the surge arrestor conducts the surge to earth/ground. But, as soon as the surge dies down, the surge arrestor reclaims its insulating properties and becomes an insulator again, ready for the next surge. Isn’t it true?

But, of late, I have been hearing & experiencing quite a lot of surge arrestor blasts, particularly, indoor polymeric surge arrestors, installed in Medium Voltage VCB Switchgear Panels. There is nothing wrong with the selection (viz.) the MCOV, the rated voltage, the nominal discharge current, the rated line discharge class, the rated pressure relief class, etc. The selection is based on manufacturer’s guidelines and on site conditions.

This blast phenomenon is more prevalent in:

i) 33kV Class Switchgear (though there are isolated incidences of SA failures/blasts at 12kV & 24kV)

ii) More so in Solar Photovoltaic Power Plants (At the same voltage level, there are no such failures reported from any other power plants’ or process industries’ installations)

iii) More when the cable length is more, say, of the order of a few kilometres

iv) Initially, there were recurring PT failures, but, later, when the PTs were strengthened with a higher Overvoltage Factor or when the PTs were removed, the Surge Arrestors started failing/blasting.

v) It is unique in VCB Switchgear Panels (At least, I am not aware of such failures with other types of switchgear).

Now, my questions are:

a) What is the reason for such surge arrestor blasts?

b) Why is it predominant only in 33kV Voltage Level?

c) Why is it unique in Solar Power Projects?

d) What has cable length got to do with it?

e) Could the PT failures also be for the same reason?

f) Is this phenomenon unique to switching with VCBs?

g) How to avoid such failures/blasts?

I request your expert opinion on this.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Mechanical Engineering - New Member Fans of Old Computers - TRS-80 - New Member Popular Science - Weaponology - New Member Safety - Hazmat - New Member Hobbies - Fishing - Fish On! United States - Member - New Member

Join Date: Apr 2012
Location: Detroit MI, USA
Posts: 2496
Good Answers: 271
#1

Re: Surge Arrestor Blast

10/05/2018 6:42 AM
__________________
How we deal with death is at least as important as how we deal with life. --CAPTAIN KIRK, Star Trek II: The Wrath of Khan
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: Surge Arrestor Blast

10/05/2018 6:49 AM

Surge arrestors we have used - recommended by our compliance consultants - are "once-only" in operation. If they operate to arrest a surge, subsequently powering them on sounds a buzzer to indicate that they must be replaced.

https://www.dehn.co.uk/en-gb/1629/31742/Familie-html/31742/DEHNflex.html

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3
In reply to #2

Re: Surge Arrestor Blast

10/05/2018 7:19 AM

But DEHN is manufacturing only Low Voltage Surge Arrestors. My question is on Medium Voltage (3.3kV to 33kV) Surge Arrestors.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: Surge Arrestor Blast

10/05/2018 11:25 AM

These types of failures are usually caused by moisture ingress.... has a forensic analysis been performed? I would guess that the failures are related to lack of maintenance and monitoring of the varistor element health of the surge arresters...

http://www.ijoee.org/uploadfile/2013/1006/20131006033843423.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jun 2007
Location: chennai,India
Posts: 592
Good Answers: 19
#5

Re: Surge Arrestor Blast

10/06/2018 12:36 AM

I may be wrong, but my thinking goes like this.

Failure occurs due to temperature , due to current flow to the earth.Are we calculating the worst current flow condition and selecting the device to withstand such current?

When i was doing a survey in one of the presiegious installation , i noticed this anamoly and device changed.

__________________
Ramesh,Freelance Electrical/automation Consultant
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6

Re: Surge Arrestor Blast

10/06/2018 5:40 AM

Is 33kV system isolated type (The source Transformer windings delta connected, for example)!

If true, I have a feeling the long cable capacitance coupled with transformer reactance resulting in resonance. This could be happening if there is a problem in VCB switching (not all poles closing simultaneously).

Other possibility is undetected 1-phase to ground fault in 33kV system, that results in raise of healthy phase voltages which could be as high as L-L voltage.

These over voltages cause PT failures as well as deterioration of SA and subsequent thermal run-away and blast.

The SA, if made to conduct frequently, cause deterioration of ZnO material in the discs which can reduce its insulation value and increase the leakage current. Higher leakage current means higher heat in the SA leading to damage/blast.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Surge Arrestor Blast

10/06/2018 3:55 PM

It <...blasts...> because the surge voltage exceeds its rating.

After a <...blast...>, it's f$£&%ed as a result of the surge.

Simplesζ.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8

Re: Surge Arrestor Blast

10/07/2018 2:41 PM

Sounds to me like it could be due to induced current due lightning strikes on or near to the site. The solar site by its very structural nature is covering a wide area all connected together with a long cable run, a good potential receiver of lightning (well) potential. You basically have a big antenna.

In regard to your other questions, large scale solar sites are going to be running at a higher voltage to keep the current (and hence cable size and cost) manageable. Yes, PTs are killed by voltage spikes too.

Standard surge arrestors alone may not be enough and you should look into including higher lightning potential grade rated air gap or similar arrestors to help protect against this sort of thing (in addition to the standard surge protectors). Perhaps an air termination system if direct strikes are occurring on or very near the site (like the actual panels or structures in or near the site, eg- security fence, etc).

__________________
jack of all trades
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers: