Question on How to Connect Relay for Restricted Earth Fault Protection For 4 Wire System Wye Transformer

10/08/2018 8:53 AM

Dear All

I have an application whereby the client is requesting for Restricted Earth Fault protection and standby earth fault protection for transformer.

Client has requested us to wire based on the wiring diagram below.

But i have some doubts on their wiring diagram.

If there is a phase to neutral fault before the phasor CT and neutral CT, then the phasor CT and neutral CT will not be able to detect the fault ? and relay won't trip with REF ? Is this correct?

What will be the correct wiring diagram for 4 wire system REF protection and standby earth fault protection?

__________________
There is no limit towards how much one can learn.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Question on How to Connect Relay for Restricted Earth Fault Protection For 4 Wire System Wye Transformer

10/08/2018 9:03 AM

None of the equipment indicated is there to protect against a <...phase to neutral fault...>; that is given by overload protection apparatus that has not been detailed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#2

Re: Question on How to Connect Relay for Restricted Earth Fault Protection For 4 Wire System Wye Transformer

10/08/2018 11:48 AM

The REF protection is for phase to earth faults and what ever happens between phase and neutral, whether it is a single phase load or a short is not the business of REF protection.

__________________
Raghunath
Register to Reply
Associate

Join Date: Jun 2009
Location: Singapore
Posts: 36
#3
In reply to #2

Re: Question on How to Connect Relay for Restricted Earth Fault Protection For 4 Wire System Wye Transformer

10/08/2018 12:16 PM

I am thinking of connecting the neutral wire after the REF CT, then we do not need to install additional CT at Our switchboard neutral end

If we will to do this,then we need to set our standby earth fault relay to trip on directional Earth fault only when there is current flow from neutral to ground ?

Since standby earth is for protection at the downstream side only ?

__________________
There is no limit towards how much one can learn.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Question on How to Connect Relay for Restricted Earth Fault Protection For 4 Wire System Wye Transformer

10/08/2018 2:22 PM

<...thinking of connecting the neutral wire after the REF CT...>

Then think again: the 51G apparatus will operate all the time, as current is never balanced across phases!

Do the right thing, and install the equipment the right way.

If in doubt, consult a qualified local Electrical Engineer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Jun 2009
Location: Singapore
Posts: 36
#5
In reply to #4

Re: Question on How to Connect Relay for Restricted Earth Fault Protection For 4 Wire System Wye Transformer

10/08/2018 8:35 PM

Yes I know current will flow through neutral of load back to the source.

Which is why I am enquiring if we will to connect neutral after the REF CT, I will want to set my standby earth fault as directional earth fault, so that the 51G will only trigger when there is current flow from the tranaformer neutral point to ground.

Any problems with this solution ?

__________________
There is no limit towards how much one can learn.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #5

Re: Question on How to Connect Relay for Restricted Earth Fault Protection For 4 Wire System Wye Transformer

10/09/2018 7:28 AM

An inability to understand is the biggest one.

<...we...>

Consult a local Mentor.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#6
In reply to #3

Re: Question on How to Connect Relay for Restricted Earth Fault Protection For 4 Wire System Wye Transformer

10/09/2018 12:45 AM

Probably you have in mind REF protection scheme that uses only 4-CTs.

Such a scheme exists and is also popular. In that scheme, the 51G CT and REF neutral CT will be two distinct CTs (not two cores of the same CT). The REF neutral CT is located between neutral wire and transformer winding star point whereas, the 51G CT is located between neutral wire and the earth point.

The 5-CT scheme (as shown in original post) is preferred by many vendors, as it is easier to accommodate one single CT (with two cores) in the transformer.

__________________
Raghunath
Register to Reply Score 1 for Good Answer