10/09/2018 12:34 AM

Which is the correct equation for calculating the cumulative voltage drop?

For example, the power supply sequence is Transformer --> MDB --> SMDB ---> DP ---> LP ---> 1PHASE FINAL CIRCUIT

VD1 = 3 Phase voltage drop from transformer to MDB

VD2 = 3 Phase voltage drop from MDB to SMDB

VD3 = 3 Phase voltage drop from SMDB to DP

VD4 = 3 Phase voltage drop from DP to LP

VD5 = 1 Phase voltage drop from LP to FINAL CIRCUIT

Cumulative VD = VD1+VD2+VD3+VD4+VD5

(OR)

Cumulative VD = (VD1+VD2+VD3+VD4)/1.732 +VD5

If the second equation is correct, why do we have to divide the three phase voltage drops by 1.732?

Thanks!

Register to Reply
Pathfinder Tags: BS 7671 Cumulative voltage drop
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#1

Re: Cumulative voltage drop

10/09/2018 3:18 AM

It depends upon the installation's configuration, which has been withheld from the forum.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9939
Good Answers: 1148
#2

Re: Cumulative Voltage Drop

10/09/2018 10:06 AM

It depends on your circuit.

If your final single phase circuit is phase-to-neutral and you measure your voltages at the 3 phase points as phase-to-phase, then you divide the 3 phase voltage measurements by the square root of 3 (1.732...) to calculate the voltage drop you would have measured if you had been measuring phase-to-neutral at the 3 phase points.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#4
In reply to #2

Re: Cumulative Voltage Drop

10/09/2018 3:14 PM

...though this assumes that there is no other load on the circuit. Without the original poster's circuit description, it is impossible to tell.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: Dec 2016
Posts: 51
#6
In reply to #4

Re: Cumulative Voltage Drop

10/09/2018 11:55 PM

There are other single phase lighting circuits.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#8
In reply to #6

Re: Cumulative Voltage Drop

10/11/2018 7:10 PM

<...single phase lighting circuits...>

3-phase lighting circuits are somewhat uncommon...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3

Re: Cumulative Voltage Drop

10/09/2018 11:07 AM

Your question has been answered on the IET forum.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32209
Good Answers: 839
#5
In reply to #3

Re: Cumulative Voltage Drop

10/09/2018 5:52 PM

Thank goodness for that.

NEXT!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Off Topic (Score 5)
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9939
Good Answers: 1148
#7

Re: Cumulative Voltage Drop

10/10/2018 3:58 PM

What's the point of adding all the drops? The sum of the drops is just the initial voltage minus the final one, correcting for whether it is phase-to-phase or phase-to-neutral of course.

You can, however, look at each individual IR drop to show where a possible trouble spot is.