Anonymous Poster #1

UPS Input Power

10/17/2018 5:02 AM

I have a 2 kVA UPS - I assume this is rated output. Say, I have a load of only 1kVA. What is the Input power to the UPS?

Input Power = Rated output Power / Efficiency of UPS

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: UPS Input Power

10/17/2018 5:17 AM

<...Input Power = Rated output Power / Efficiency of UPS...> gives the answer. The numbers can be determined by simple measurement. The heat that is rejected by the UPS added to the dissipation of the <...load of only 1kVA...> to give the input power. Or, the input power minus the <...load of only 1kVA...> gives the heat rejected by the <...UPS...> and other arithmetic gives the efficiency.

It's rather like asking the following question:

  • One has a 100W tungsten light bulb that is dimmed by a commercial lighting dimmer so that the bulb gives an output power of 25W. What is the input power to the dimmer?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2

Re: UPS Input Power

10/17/2018 9:37 AM

Your load will always change. People will in the future plug more things into this UPS, too. RTFM on the UPS to find out what input power the designers planned for.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: UPS Input Power

10/17/2018 10:49 AM

If the UPS is sustaining the <...load of only 1kVA...> during a power outage, then the <...input power to the UPS...> will be zero. After all, that is its only real purpose.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#4

Re: UPS Input Power

10/17/2018 11:38 AM
__________________
All living things seek to control their own destiny....this is the purpose of life
Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#5

Re: UPS Input Power

10/17/2018 10:06 PM

As long as you know the efficiency at the 1 kVA operating point. The marketeers always tout the 'peak' of the efficiency curve. If you operate a typical UPS at 2% of its rated capacity, its efficiency will be VERY low.

Reply Score 1 for Good Answer
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #5

Re: UPS Input Power

10/18/2018 9:37 AM

True, the efficiency will be low but the actual power draw will be less than when it is most efficient.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#6

Re: UPS Input Power

10/17/2018 10:38 PM

Is that a single phase UPS or 3 phase UPS and what is your UPS input voltage

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#7

Re: UPS Input Power

10/18/2018 9:15 AM

Is it on-line or off-line? If off-line, the input power will be equal to the output power (when the mains power is on (obviously), and when the battery is fully charged).

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#8
In reply to #7

Re: UPS Input Power

10/18/2018 9:31 AM

But what will the power draw be just after going online as the battery charges and the fans cool and vent whatever outgas is produced by a charging battery? This is why the OP should RTFM.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Member

Join Date: Dec 2012
Location: Chennai, Tamil Nadu, India
Posts: 8
#10

Re: UPS Input Power

10/19/2018 11:44 AM

you cannot use the formulae directly.UPS is having a battery charged at the constant flow rate. you can use maximum power of 2 KVA for a programmed hour of usage depending on the capacity of the storage battery.

You can think of an analogy of water tank in your house. Suppose you have a water tank of 2000 Liters. You have a pump which delivers water at the rate 500 litres per hour.

You are drawing water in the outlet pipe at the rate of 1000 litres per hour.

The water inlet is not changed with reference to your outlet.

The delivery depends on the storage on the tank and not directly linked to your inlet flow

UPS functioning is also similar to this analogy

Reply
Reply to Forum Thread 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Brave Sir Robin (1); JohnDG (1); panneerselvam (1); PWSlack (2); redfred (3); Simon Wan (1); SolarEagle (1)

Previous in Forum: How to Choose A Suitable Sampling Frequency for this Current Sensor?   Next in Forum: Slip Frequency Measurement

Advertisement