Transformer Sizing

10/30/2018 6:01 AM

Dear sirs, I have to select a transformer 20KV primary/5.5 kV secondary for my plant. The loads are specified as below.

1.Raw mill motor-1 = 1650KW

2.Raw mill motor-2 = 1650KW

3.Bag House Fan = 1350 KW

4.Compressor - 1 = 250 KW

5.Compressor -2 = 250 KW

Total load = 5150 KW

I request you to kindly give me the selection of power transformer with detailed calculation. I am having one no.6 MVA transformer. Can I use it or shall I go for 10 MVA transformer? Both raw mill motors start at a time i.e., 2x1650=3300KW load. Both motors starting current is to be considered. Thanks

Register to Reply
Pathfinder Tags: Transformer sizing selection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - DIY Welding - Wannabeabettawelda

Join Date: May 2007
Location: Annapolis, Maryland
Posts: 7940
Good Answers: 458
#1

Re: Transformer Sizing

10/30/2018 12:57 PM

Most transformer manufacturers would be thrilled to help you determine the most appropriate size for your application.

Register to Reply
Commentator

Join Date: Oct 2010
Posts: 62
Good Answers: 5
#2

Re: Transformer Sizing

10/30/2018 11:09 PM

You absolutely must double the mva of your transformer. You must consider start up load, and consider thermal overloading of a too small transformer, the problem of having to re set the overloads, re setting the mills that were mid operation when the compressors kicked on. A 6mva transformer is not enough.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Transformer Sizing

10/31/2018 1:17 AM

STOP!

Do not proceed.

Contact 3 manufacturers and give them your requirements.

They, alone, can help you size your transformer!

No one here can help you.

Some may try but they may just kill you and others with their misguided kindness.

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Transformer Sizing

10/31/2018 3:59 AM

You don’t say what starting method is used for each motor.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 1460
Good Answers: 30
#5

Re: Transformer Sizing

10/31/2018 6:38 AM

If you already have one transformer, do you have the space to install a second transformer and split the loads between them?

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#6

Re: Transformer Sizing

10/31/2018 9:54 AM

This sounds like a job for a contractor or consultant.

We should all know our limitations or somebody can get hurt.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#7

Re: Transformer Sizing

10/31/2018 10:44 AM

The 6MVA transformer may well be large enough. The load factor for your equipment is often less than 50%, for design a conservative rule of thumb is to use 75% of nameplate. The value of the heat lost switching to a larger transformer is rarely if ever justified, because most end up underloaded in actual operation, the value of the incremental heat is very small, and not easily predicted.

The transformer manufacturers are not the technical resource you want. Your starting methods and the starting torque requirements of your loads/motors are required to know if you can start the loads, without lowering the transformer voltage so low you cannot develop the accelerating torque for the motor you are trying to start. The transformer manufacturers have no knowledge of this, and by the time you give them this information, you could have done it yourself, with no chance of giving them the wrong information.

Since this has only motor load, light flicker from voltage dips while starting a motor will not be objectionable, and once one of the motors is running, subsequent voltage drops from other motors starting will likely not be enough to make them slip out of synchronism (pull out).

The detailed calculations are now easily done by computer, and that is your job, as you alone have access to the technical information required to perform the modeling.

If I was to size this based on experience, with no calculation, I would choose the 10mVA option, the 6MVA could be marginal or not work at all, depending on your power system source impedance before the transformer, your speed/torque curves of the machinery, the type of motor, synchronous, induction, wound rotor, and your starting method. You run all of the connected loads, and then start the largest motor, to see if the system will survive. You need to know the upstream power system source impedance, and the impedance of your proposed transformer, use a standard value around 5-6%, check with your tentative transformer manufacturer.

My rule of thumb is you can start a 200hp motor across the line with no ill effects with a 1000kVA transformer, 5.75% impedance, and maybe less than 250MVA short circuit availability to the primary of the transformer. Starting a medium voltage motor is less critical, since the other machines on the transformer will tolerate voltage dips during starts.

Register to Reply
Associate

Join Date: Oct 2006
Location: Hyderabad,India
Posts: 49
#8

Re: Transformer Sizing

11/05/2018 2:04 AM

1) Pl provide the Working/ Standby loads.

2) Pl give the sequence of operation for the various motors. Which is the last motor to start ?

3) What is the mode of operation ie starting for these motors ? Any VFD's are present in the circuit ?

4) What are the other loads ( tie feeders or trafo feeders ) on the 5.5 kV board ?

Register to Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#9

Re: Transformer Sizing

11/09/2018 2:33 AM

You have to give the type of motor,Starting method, acceleration time (Voltage should not fall below 80% and trf should be capable)Starting sequence etc

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Brave Sir Robin (1); lyn (1); nesubra (1); phph001 (1); ravipra01 (1); redfred (1); rwilliams (1); TonyS (1); tundrawolf (1)

Previous in Forum: Verizon 5G Home   Next in Forum: Switching DC Earth Fault

Advertisement