we are operating our 25MW coal power plant in parallel with national grid system to meet our industial complex load of 20MW. while our plant was operating at 20MW (i.e no import/export to national grid), the utility breakers tripped on earth fault in the utility system transmission line. as the utility breaker tripped , our plant power suddenly inreased from 20MW to 22MW and frequency went up from 50 to 51.5Hz. however the GCB did not trip on overfrequency. the steam turbine power then suddenly started dropping from 22MW to 0MW within 3 seconds and GCB tripped on underfrequency.anyone having any idea why the DEH of turbine was not able to bring back the turbine speed/power back to normal 20MW/50Hz ? why sudden rolling back of power to 0MW? we expected our plant to operate in isolated mode to supply our industrial load of 20MW because the earth fault was temperoray and not in our plant system.