Tan Delta Correction Factor

11/29/2018 6:56 AM

Dear all,

Good Afternoon!

Based on my tittle for tan delta test results temperature correction factor is mandatory, because of already if i have get with in the limit as per recommended value.further, clarify the formula for same.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Tan Delta Correction Factor

11/29/2018 11:21 AM

Because the degree of deterioration of shielded MV/HV cable insulation must surely vary with temperature, it is only commonsense to include the temperature in the calculation to obtain <... the limit as per recommended value...>.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: Tan Delta Correction Factor

11/29/2018 5:54 PM
__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#3
In reply to #2

Re: Tan Delta Correction Factor

11/30/2018 12:15 AM

You could regress the temperature correction series that Solar Eagle provided from Scribd and that would be your formula, if we are understanding the question properly...

Excel provides a good little utility for that purpose that gives you typical curve fits, other software like EZ-FIT (Perrella) offers more sophisticated analysis tools that often provide closer matches (Rsquared) that you can get in Excel

Register to Reply
Commentator

Join Date: May 2017
Posts: 70
Good Answers: 1
#4

Re: Tan Delta Correction Factor

11/30/2018 9:17 AM

Testing system?

So,

Perform an experiment to collect your own data: Test your system at 20C (keeping same V), then continue testing by steps at different temperatures. This will allow validate your system as function of temperature and make your customer trust on you.

Register to Reply Score 1 for Good Answer
Register to Reply 4 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Jose1 (1); PWSlack (1); rwilliams (1); SolarEagle (1)

Previous in Forum: Cooper Power System Recloser   Next in Forum: Magnetic Shielding of PCB at 50Hz

Advertisement