We are trying to test insulation of compressor using Digital high voltage Insulation Tester. However, during test the insulation resistance increases as you contuses holding the test button.

Question: For how long should the test button be held to get correct insulation resistance reading?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#1

Re: iNSULATION RESISTANCE TEST

01/20/2019 12:38 PM

It sounds like you have capacitive charging leakage current, this occurs when you have two conductors side by side, the wire that's charging simulates a capacitor charging and should become fully charged depending on length over time....so I would hold the button until it stops moving....

start at 8:00...

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#2
In reply to #1

Re: iNSULATION RESISTANCE TEST

01/20/2019 2:22 PM

Yes, this is typical of testing insulation resistance of long transmission lines. You have to let them charge.

Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#10
In reply to #2

Re: iNSULATION RESISTANCE TEST

01/27/2019 3:56 AM

You must also discharge the lines in substations even after the power is off.

This sometimes requires leaving jumper cables attached for hours.

The capacitance discharge of high voltage wiring and transformers can be deadly.

Theoretically, a capacitor is never fully charged or discharged,but it will get close enough for practical purposes.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Anonymous Poster #1
#12
In reply to #1

Re: iNSULATION RESISTANCE TEST

06/24/2019 10:43 PM
Register to Reply Score 1 for Good Answer
Associate

Join Date: Jun 2019
Posts: 50
Good Answers: 1
#13
In reply to #1

Re: iNSULATION RESISTANCE TEST

06/24/2019 10:45 PM
Register to Reply
2
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#3

Re: iNSULATION RESISTANCE TEST

01/20/2019 4:33 PM

Megger.com have a document called "Stitch in Time", which explains why insulation resistance reading changes during a test & over months of repeat tests & how to interpret it to judge condition of machine.

You will find it if you do a search of their website - you will have to register & log-in before you can download, which is no problem if you are a genuine machine user.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2010
Posts: 1686
Good Answers: 116
#4
In reply to #3

Re: iNSULATION RESISTANCE TEST

01/20/2019 4:47 PM

This is one graph from "Stitch in Time", showing initial currents.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#5

Re: Insulation Resistance Test

01/20/2019 11:03 PM

http://eecoonline.com/motor-repair-best-practices-polarization-index-test/_

It looks like you are applying enough potential during your test to use a polarization index test method to evaluate the insulation condition.

This could be an expedient method to evaluate the insulation, though the fact that it charges up shows the insulation is good. If you use a lower voltage for the test, the charging effect will not be as noticeable. This appears to be a large machine or a high application test voltage. My experience in observing similar circumstances is 4000 volts on a 3000 hp machine, open frame engine type synchronous salient pole machine.

Register to Reply Score 1 for Good Answer
Guru
Popular Science - Cosmology - Let's keep knowledge expanding Engineering Fields - Retired Engineers / Mentors - Hobbies - HAM Radio - New Member

Join Date: Dec 2006
Location: North America, Earth
Posts: 4528
Good Answers: 106
#6

Re: Insulation Resistance Test

01/20/2019 11:35 PM

Read the manual.

__________________
“I would rather have questions that can't be answered than answers that can't be questioned.” - Richard Feynman
Register to Reply
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#7

Re: Insulation Resistance Test

01/21/2019 1:46 AM

You have not given the details of electrical equipment under test (I suppose it is a motor driving the compressor). Please give details of equipment, its rated voltage, type and class of insulation and test voltage. Then it would me easier to analyse the conditions.

Register to Reply
Commentator

Join Date: May 2017
Posts: 70
Good Answers: 1
#8

Re: Insulation Resistance Test

01/21/2019 1:07 PM

PI is a Polarization Index run for 10 min at a particular voltage (function of rate voltage of unit) in order to qualify the electrical insulation per IEEE 143.

Register to Reply
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#9

Re: Insulation Resistance Test

01/22/2019 11:53 AM

The test button is to be held till the IR value stabilises.

It is a good sign that the I value is increasing. If you can read 1-min and 10-min IR values, the ratio of 10-min value to 1-min value is an index of Insulation healthiness. This is called Polarisation index (PI).

The ABB motor manual says PI of 2 and above means insulation is good.

__________________
Raghunath
Register to Reply Score 1 for Good Answer
Associate

Join Date: Jun 2019
Posts: 50
Good Answers: 1
#11

Re: Insulation Resistance Test

06/24/2019 7:55 AM

If the insulation value improves after holding the test button of the high voltage insulation tester, it shows that the insulation system is OK.The insulation resistance improves as the charging current decays down if the insulation system is OK. The insulation resistance taken after one minute fairly gives the reading of the insulation.

To ensure the healthiness of the system Polarization Index Test can be conducted.The polarization index is the ratio of 10 Minutes IR Value to one minute IR Value. If PI is greater than 2 the insulation system is OK.

Read More:Polarization Index Test

Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

67model (2); Anonymous Poster (1); HiTekRedNek (1); Jose1 (1); pcchatur (1); raghun (1); Rajesh52 (2); Rixter (1); rwilliams (1); SolarEagle (1); StandardsGuy (1)

Previous in Forum: Choosing an 8A Drill   Next in Forum: Dual Voltage and Single Voltage MCB

Advertisement