90 KVA UPS , Parallel redundant system,
Fault (IGBT Failure ) in Inverter -1 section & it's dc fuses blown , but SAT trip (Saturation Trip) has been sensed by inverter -2 also.
Can anybody tell me how to avoid this kind of situation
Re: UPS
02/03/2019 12:15 PM
Get a job at UPS
Re: UPS
02/03/2019 12:48 PM
"how to avoid this kind of situation"
1. Unplug the device.
2. Consult the owner's manual.
3. Call the manufacturer's tech service.
4. Ask a competent electrician to trouble shoot it.
5. Simply replace it.
Re: UPS
02/03/2019 4:07 PM
GA. Nothing to add.
Re: UPS
02/03/2019 5:05 PM
Since you could not contact the fabricator of this UPS, stop buying from low bidders with questionable product.
Re: UPS
02/04/2019 1:06 AM
Re: UPS
02/04/2019 1:48 PM
As good a guess as any on the actual manufacturer. Saturation Trip sounds like an external overload of some sort, but without more detail, at least Manufacturer and Model and Age, type of load, difficult to help & guide...
Re: UPS
02/04/2019 4:54 AM
it's its
Re: UPS
02/04/2019 1:18 PM
For what it's worth, the poster's command of the English language is much better than my command of Hindi or any other language outside of my mother tongue.
Re: UPS
02/04/2019 7:40 PM
This AP spent his, and our, time to pick this nit?
How come AP's are allowed to post anyway? (Don't answer that. I heard all the lame excuses already)
Good Answers: 804
Re: UPS
02/04/2019 6:49 PM
A "saturation fault" in an IGBT based device, like a UPS, is generally indicative of a problem with the voltage between the collector and emitter of an IGBT transistor. In modern devices this is now usually TTL level signals, so +5VDC with a "trip" threshold of around +7VDC. That means one of several possibilities:
  1. You have a serious defect in your firing board, in which case the problem will repeat itself with an new IGBT module and cost you more money in fuses and IGBTs.
  2. Bad grounding resulting in excessive noise in the system that ends up 'fooling" the sensing elements into thinking the IGBT collector/emitter voltage is too high. This too will repeat itself.
  3. A short circuit on the output side, which makes the IGBT the highest impedance device in the circuit for that brief moment until the fuses clear. This will not only repeat itself but likely start cascading and taking out more and more parts of the system.
Give that the fuses cleared, I would take a wild guess at #3...