Is it advisable to enable Auto Reclosing Function for Circuit Breakers feeding Underground Cable Networks? If yes, should it be single shot or multi-shot? What should be the typical dead time?
They were originally designed for OH lines as they are more susceptible to intermittent faults. Faults on UG cables are unlikely to be intermittent so reclosing on to the fault will just cause more damage.
So, no I don’t think it would be a good idea.
__________________
The reports of my death are greatly exaggerated.
You mean Transient fault (not intermittent fault).
In overhead line distribution, 80% of faults are transient nature and tripping and reclosing is the best way to restore the service fast. In case of Cable feeders, there are no transient fault. If insulation is damaged it cannot recover on its own, is damaged for good.
45+ years back at engineering college one of our lecturers gave us a project as homework. It was to control a timed and monitoring sequence using opamps.
The circuit he had designed while working for a switchgear manufacturer in the early 60’s became our homework.
Fault.
Switch open.
Wait.
Switch close.
Switch open if fault is still there.
Wait.
Switch close.
Switch open if fault is still there.
Wait.
Switch close for a couple of seconds to try and burn the fault clear.
Switch open if fault is still there followed by Lockout.