Acetylene Appeared After Maintenance and Transformer Testing

02/10/2019 2:53 PM

A 2.5MVA, 34.5KV/ 480V, 5Tap, manual tap, nitrogen blanket ...

issue is: acetylene appeared with 25 ppm, acetylene appeared just after transformer was out of service for testing, test result was all OK, after energizing an oil sample was collected as a normal procedure the acetylene appeared with about 25ppm

the sample repeated three times within one month and the acetylene was almost fixed not propagating, with the same amount of hydrogen

My plan is to filter the oil and continue monitor the oil sample for another one week to see if acetylene disappear or steel inside after filtration

if acetylene will be existing, then I am planning to take the transformer for a work shop for internal check.... can anyone comment please?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Acetylen appered after maintenace and tr testing

02/10/2019 3:01 PM

All transformers generate gases to some extent at normal operating temperatures. Insulating mineral oils for transformers are mixtures of many different hydrocarbon molecules, and the decomposition processes for these hydrocarbons in thermal or electrical faults are complex. The fundamental chemical reactions involve the breaking of carbonhydrogen and carbon-carbon bonds. During this process, active hydrogen atoms and hydrocarbon fragments are formed. These fragments can combine with each other to form gases: hydrogen (H2 ), methane (CH4 ), acetylene (C2 H2 ), ethylene (C2 H4 ), and ethane (C2 H6 ). Further, when cellulose insulation is involved, thermal decomposition or electric faults produce methane (CH4 ), hydrogen (H2 ), carbon monoxide (CO), and carbon dioxide (CO2 ). The gases listed above are generally referred to as key gases.

Caused by arcing.

Register to Reply Good Answer (Score 3)
5
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2
In reply to #1

Re: Acetylene appeared during transformer testing

02/10/2019 4:25 PM

<15 ppm is normal... >70 ppm is clear evidence of arcing and action must be taken....at 25 ppm this calls for more frequent testing to monitor the situation....

https://www.netaworld.org/sites/default/files/public/neta-journals/NWwtr09_Hamrick.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply Good Answer (Score 5)
Member

Join Date: Dec 2015
Posts: 6
#4
In reply to #2

Re: Acetylene appeared during transformer testing

02/11/2019 9:21 AM

Thanks, i will go filtration, retest and continues monitoring

Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#7
In reply to #2

Re: Acetylene appeared during transformer testing

02/11/2019 10:14 PM

Arcing is not the only way to manufacture acetylene in a paper insulated transformer. Overload of the transformer can generate acetylene. The following quote from

https://www.morganschaffer.com/page-article-dga-power.html

Acetylene stands out from the rest as being important at any detectable concentration. In the progression of a thermal fault, this critical gas is formed only at the more extreme temperatures, starting with localized overheating above 700°C. In such cases, the acetylene concentration is typically less than 10% of the ethylene concentration. When the acetylene makes up a higher proportion of the hydrocarbon gases, a critical arcing fault is likely present. The statistics suggest a normal concentration is <5 ppm, which includes the contribution of non-critical thermal faults in aged transformers. However, even 1 ppm of acetylene would be considered a possible serious indicator if found in a new transformer, or when first observed during the service life.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Acetylene Appeared After Maintenace and Transformer Testing

02/11/2019 2:22 AM

The transformer manufacturer can certainly comment. What was the outcome of the telephone calls on the topic, please?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Dec 2015
Posts: 6
#5
In reply to #3

Re: Acetylene Appeared After Maintenace and Transformer Testing

02/11/2019 9:22 AM

Thanks, i will go filtration, retest and continues monitoring

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6
In reply to #5

Re: Acetylene Appeared After Maintenace and Transformer Testing

02/11/2019 11:29 AM

Do NOT yet filter the oil until you find out what caused the acetylene. It is an indicator of arcing taking place under the oil. Acetylene takes a lot of energy to form from the hydrocarbons of the insulating oil. The fact that it has not increased in the past month only means that the arcing has not continued, but it doesn't mean that it won't happen again.

Do you have past (recent) test results to verify that the acetylene was not there already? That is the first thing you must confirm.

During testing, was the DETC operated? If the contacts of the DETC were not well settled at the chosen tap, arcing can occur. Make sure the tap setting is firmly locked.

Was any other internal work done during the testing outage? Were any connections in the tank disturbed? Did the testing apply any voltage to the transformer windings that might have been above their insulation ratings, so that there could have been a flash-over? Was there any other unusual event when the transformer was reenergized?

Filtering the oil will eliminate any evidence of what may have happened. You should also look at the ratios of the other combustible gases to the acetylene (Rogers Ratios), which could give you clues to any other conditions that may have caused it. Check out the site below for a ratio tool. Only filter the oil after you are satisfied that the cause has been corrected. And THEN take a new sample to give yourself a baseline for future comparison.

Rogers Ratios calculator

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jan 2010
Location: Hyderabad
Posts: 343
Good Answers: 22
#8
In reply to #6

Re: Acetylene Appeared After Maintenace and Transformer Testing

02/12/2019 12:59 AM

I too think so. The priority should be given to find out what caused 'arcing'.

Since the OP mentioned only testing was done, whether Tap changer was operated during testing (when the current is flowing) should certainly be looked in to. This is relevant if the tap changer is off-circuit type.

__________________
Raghunath
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#9
In reply to #8

Re: Acetylene Appeared After Maintenace and Transformer Testing

02/12/2019 7:59 AM

It's not just whether there was current flowing during testing. Rather, if the tap changer setting was changed (such as to test winding resistance or ratio on each of the taps), and the contacts didn't make cleanly after resetting to the desired tap, then operation of the transformer afterward could cause arcing at the DETC contacts. I have seen that myself. The springs that put tension on the DETC contacts are not that stiff, and a sloppy detent can cause the contacts not to "make" well. But we'll see if the OP comes back with any additional info...

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Member

Join Date: Dec 2015
Posts: 6
#11
In reply to #9

Re: Acetylene Appeared After Maintenace and Transformer Testing

02/14/2019 6:27 AM

Thanks to all for informative comments, FYI, the history records of oil sampling did not record any appearance of Acetylene before. “We are conducting oil sample test on a yearly basis"

The Acetylene appeared only after last transformer testing conducted on last November 2018-"Off line test every three year basis"

During last test, the DETC -5 taps- was changed for testing of resistance and ratio in all taps.

The oil sampled again after back in service, and since back in service, oil sample was collected for testing, the test repeated three times over one month and the PPM of Acetylene was almost fixed and tends to decrease....

I doubt this happened because of DETC.

Based on those facts, I opt to filter and test and monitoring for weekly sampling for according actions.

I preferred to postpone taking the Tr. to outside workshop until confirm acetylene is not because of DETC.

Register to Reply Score 1 for Good Answer
Guru

Join Date: Sep 2016
Posts: 973
Good Answers: 9
#10

Re: Acetylene Appeared After Maintenance and Transformer Testing

02/12/2019 8:18 AM

Some sort of transformer fart huh? Or something

Register to Reply Off Topic (Score 3)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Acetylene Appeared After Maintenance and Transformer Testing

07/17/2024 8:14 AM

The <...acetylene...> is a gas, and cannot be removed by using a <...filter...>; filtration will only remove solids from fluids.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 12 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: