Anonymous Poster #1

Transformer Foundation and Drainage

02/16/2019 9:28 AM

Dear Sirs,

We have a situation where, we have to pass draianage pipe carrying water below the transformer foundation. Is it a good practice to keep drainage pipe below the foundation of transformer?

The drainage pipe has to carry water obtained from uphill areas.

Best Regards,

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Transformer Foundation and Drainage.

02/16/2019 10:09 AM

That is NOT enough information for any knowledgeable answers.

You should consult a LOCAL civil engineer and do the installation correctly, instead of trying to do it on the cheap.

Transformer Basics-Working principle, Construction, Types, Applications
Controlled Drainage – Transforming Drainage | Project Funding

Reply Score 1 for Good Answer
Power-User

Join Date: Mar 2010
Location: The Canyons of the Ancients
Posts: 356
Good Answers: 2
#2

Re: Transformer Foundation and Drainage.

02/16/2019 12:54 PM

Of course the design of the transformer foundation and surrounding area are key. The foundation should not be in a drainage of low spot. Uphill from the site should be addressed first to make sure any water (runoff or otherwise) is properly diverted around foundation. Gravel and French drains are mandatory to keep site dry. Any water piping should go around the site. Water will not stay in pipes forever.

__________________
" looking for conscience in the brain is like looking for the band in the radio" N. H.
Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: Transformer Foundation and Drainage.

02/16/2019 10:24 PM

I wouldn't put the opening of a drainage pipe above a transformer.

Good practice requires knowing the local codes where this transformer resides. We don't know your location to tell you what your local codes say.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Anonymous Poster #2
#16
In reply to #3

Re: Transformer Foundation and Drainage.

02/18/2019 9:52 AM

Above the actual transformer, or above the transformer bund wall? Much assumption and misreading being accounted in this forum.

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#18
In reply to #16

Re: Transformer Foundation and Drainage.

02/18/2019 11:06 AM

You said 'Much assumption and misreading being accounted in this forum.'

Well what do you expect when you only give a bit of the story? If you are a regular visitor to our little band of misfit engineers, who like to exercise the grey matter muscle, that grey matter does tend to run amuck, at a tangent, without proper data, facts and figures!

We will assume the unseen, unread and unannounced, then concoct a wonderful story to suit our imagination!

So tell us the truth, the whole truth, and nothing but the truth and we will attempt to give you the benefit of our collective years of experience!

If you can't....... expect the worst!

__________________
The square root of nothing is what you make it!
Reply
Anonymous Poster #2
#21
In reply to #18

Re: Transformer Foundation and Drainage.

02/18/2019 12:51 PM

"Is it a good practice to keep drainage pipe below the foundation of transformer?" No interpretation required. Clearly the answer is Yes or No.

I agree, the English language is most confusing and assuming. Even more so for the English.

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#22
In reply to #16

Re: Transformer Foundation and Drainage.

02/18/2019 1:29 PM

Above the actual transformer, itself is not a good place for the drainage opening. I was dissuading the OP from this ridiculous option that would funnel the runoff to the worst place possible.

As for others concerns about putting the drainage pipe below the foundation, I can think of situations where this would be preferred. This is particularly true if the drainage pipe is part of the initial transformer and bund installation. If instead this is a drainage upgrade on an existing system then this still might be the best option but can easily induce unforeseen complications. In either case, the licensed engineer site plan based on the geological/hydrological survey should be followed!

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#4

Re: Transformer Foundation and Drainage.

02/16/2019 10:37 PM

Ye Gods... re-route it so you don't have to dig beneath the foundations!

surely you cannot be that blind to the obvious!

__________________
The square root of nothing is what you make it!
Reply Score 1 for Good Answer
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#5

Re: Transformer Foundation and Drainage.

02/16/2019 11:19 PM

Pipes eventually require repair. It would be better to not have to dig up the foundation if possible to repair the pipe.

Also, if the pipe leaks, you run the risk of undermining the foundation, also not the best to assure service continuity.

Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#6

Re: Transformer Foundation and Drainage

02/17/2019 10:26 AM

Is the transformer pen fully tanked? If not oil seepage can get in to water courses. I don’t know the laws in your country but here in the UK you would be facing enormous fines imposed by the law courts.

25 years ago our company contaminated water courses with quarry slurry. The courts imposed a fine of £1.25M, added to that was the clean up bill.

Think long and hard about what you plan to do.

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#17
In reply to #6

Re: Transformer Foundation and Drainage

02/18/2019 10:16 AM

If the transformer, (and it should be), is fully tanked with oil, the bund should be of sufficient capacity, that is, at least 10% more capacity of the transformer tank and reservoir tank on top of the tranny. This is the same in all countries, including the UK.

To install drainage below a tranny bund is acceptable and normal in may builds, espcially substation drainage, as long as the clearance is sufficient and the rainwater drainage does not flow into the tranny catchment tanks that may be installed, The tow drainage systems must remain separated and never connected to one another.

If the bund exists, a direction bore could be used to go underneath the transformer bund. It is not a good idea, but Yes, it can be done ad it is not an infraction of any rule/laws. it may be odd, but it is prefectly fine to do so as rerouting could cause a flood in a station or undermine gantries and equipment.

Agreed, information is insufficient and only the poster knows his conditions, risks, and station layout, and enviro. It may be his only option to go below the tranny bund.

Reply Score 1 for Good Answer
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#7

Re: Transformer Foundation and Drainage

02/17/2019 11:14 AM

No there is not enough information.

We have pipes that are well over 100 years old as well as pipes that are well over a hundred feet deep as well as pipes that are layered between multiple utilities.

Rerouting and making turns that are not necessary exasperate issues that otherwise would have not been.

If done correctly. The infrastructure will outlast all of us.

If installed incorrectly it doesn't matter where the pipe or the transformer is located.

How many pipes and utilities cross at a 90 degree angle above and below each other?

If none of it were permissible and all of it was deemed a bad idea... Nothing would ever be accomplished.

__________________
High Tolerance is Beautiful
Reply
Power-User

Join Date: Mar 2010
Location: The Canyons of the Ancients
Posts: 356
Good Answers: 2
#8
In reply to #7

Re: Transformer Foundation and Drainage

02/17/2019 11:54 AM

Hundred year old pipes are made of what?

__________________
" looking for conscience in the brain is like looking for the band in the radio" N. H.
Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#9
In reply to #8

Re: Transformer Foundation and Drainage

02/17/2019 1:05 PM

You name it.

__________________
High Tolerance is Beautiful
Reply
Power-User

Join Date: Mar 2010
Location: The Canyons of the Ancients
Posts: 356
Good Answers: 2
#10
In reply to #9

Re: Transformer Foundation and Drainage

02/17/2019 1:28 PM

How about, rusty steel, concrete, and lead. And 100' down, I imagine gravity.

__________________
" looking for conscience in the brain is like looking for the band in the radio" N. H.
Reply
Guru

Join Date: Apr 2008
Location: Chicago
Posts: 3990
Good Answers: 144
#11
In reply to #10

Re: Transformer Foundation and Drainage

02/17/2019 1:52 PM

Yes indeed. And right outside some 1800 era water main was replaced last year.

I was surprised at the decent condition of sections.

We also have brick pipes.

Most homes in my neighborhood are well over 100 years old.

The deep tunnel drains can be over 300' deep . Not as old, but under everything.

The intakes for the city water are a modern marvel of yesteryear.

New would be nice.. and expensive.

I can count on on one hand with no fingers or thumb the number of times I've witnessed new work undermined by a sinkhole.

__________________
High Tolerance is Beautiful
Reply
Power-User

Join Date: Mar 2010
Location: The Canyons of the Ancients
Posts: 356
Good Answers: 2
#12
In reply to #11

Re: Transformer Foundation and Drainage

02/17/2019 2:19 PM

I would expect that the excavator drivers sphincters are pretty tight, and adrenaline is brown

__________________
" looking for conscience in the brain is like looking for the band in the radio" N. H.
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#14
In reply to #12

Re: Transformer Foundation and Drainage

02/17/2019 2:46 PM

The excavators always seem to have holes in the seat,even new ones.

I asked why,and was told that the sphincter muscles were very powerful under stress and kept pinching holes in the seat covers.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply Score 1 for Off Topic
Anonymous Poster #2
#15
In reply to #8

Re: Transformer Foundation and Drainage

02/18/2019 9:48 AM

100 Year old clay.

Reply
Power-User

Join Date: Apr 2010
Location: Moncks Corner, South Carolina, USA
Posts: 157
Good Answers: 6
#23
In reply to #7

Re: Transformer Foundation and Drainage

02/22/2019 11:12 AM

I have been involved in construction work at power plants where digging any hole resulted in a change order because of buried treasure. These plants were only 30 years old but not much was done to track buried utilities. After the initial construction was complete the original construction office trailers were buried on site because it was cheaper than moving them.

__________________
You can always tell a Nuke because you can't tell him anything!
Reply
Guru

Join Date: Feb 2013
Posts: 2004
Good Answers: 31
#24
In reply to #23

Re: Transformer Foundation and Drainage

02/22/2019 2:24 PM

Something I have notice about American companies and military, they throw equipment away and leave it behind without thinking anything of it. Where, in all other countries I have worked, equipment is removed, including brick buildings and foundations and all is reused or recycled elsewhere. And left over aggregate and sand is donated to the community, they just arrive with a pickup, shovel it up and go build something at home. Even spoil gets collected by the community and used as fill for building sites for anyone who needs it.

You guys certainly throw away a lot of money and the client at days end, pays for all that waste in the initial costs. Like the UK, you seem to be a 'throw away society' or, your material are so cheap and profits so high, you can afford to waste. Bemused by these actions. But I guess you mark up the buried treasure on site plans!!!!!! Of course it is marked up.....

Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#25
In reply to #24

Re: Transformer Foundation and Drainage

02/22/2019 2:35 PM

Usually the markings are just graffiti.

__________________
"Don't disturb my circles." translation of Archimedes last words
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#27
In reply to #24

Re: Transformer Foundation and Drainage

08/22/2024 3:53 PM

When a train derails in the USA,sometimes the entire cars are buried on site beside the tracks to save the money for hauling them away.What a waste.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#13

Re: Transformer Foundation and Drainage

02/17/2019 2:42 PM

Since the 1970's transformers are required to have retainer wall around their bases.

Gates in the wall were allowed to pass rain water but required to be closed at the first sign of an oil leak.

This was to prevent PCB Contamination of the environment.

The PCB oils were heavier than water,and would quickly sink into the ground.

In regard to old underground pipes,there is a method now where they inflate a long plastic liner into the tube without digging it up.

This method is being used in many cities now.

Tunneling under a transformer is not a very good idea. Redirecting the route from the beginning to avoid it is the best way.

Don't be penny wise and pound foolish.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Reply
Power-User

Join Date: Mar 2010
Location: The Canyons of the Ancients
Posts: 356
Good Answers: 2
#19

Re: Transformer Foundation and Drainage

02/18/2019 12:17 PM

Apparently you are not very proud of your question, #1.

__________________
" looking for conscience in the brain is like looking for the band in the radio" N. H.
Reply
Guru
Engineering Fields - Civil Engineering - Member

Join Date: Mar 2011
Location: ''but, don't we get PAID to ask questions?...''
Posts: 1661
Good Answers: 17
#20

Re: Transformer Foundation and Drainage

02/18/2019 12:33 PM

How about providing a Site Plan, with all existing relevant water course(s), and all appropriate cross-section(s), etc., with all relevant dimensions and elevations, with enough relevant details, features, info, etc., included to define the situation well enough for us to make specifically relevant suggestions, instead of just trying to make intelligent guesses?...

__________________
''illigitimi non carborundum...''(i.e.: don't let the fatherless (self-deluding,sabotaging, long-term-memory-impaired, knee-jerking, cheap-shotting, mono-syllabic, self-annointed, shadow-lurking, back-biting, off-topic-inquisitors) grind you down...)
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#26

Re: Transformer Foundation and Drainage

08/22/2024 7:37 AM

If <...We have to...> then <...Is it a good practice...?...> doesn't matter.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 27 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); brich (2); HiTekRedNek (3); IQ (2); JE in Chicago (3); lyn (1); MR. Guest (1); munch (5); PWSlack (1); redfred (3); rwilliams (1); TonyS (1); XNuke (1)

Previous in Forum: Timed Light Switch   Next in Forum: Transmission Line Leg Profile

Advertisement