cable sizing calculation

10/07/2007 9:56 AM

i want to know wat exactly calculation we follow for cable sizing for any parameters.Pl send it on urgent basis.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#1

Re: cable sizing calculation

10/07/2007 10:27 AM

try this

__________________
“It's kind of fun to do the impossible.” Walt Disney
Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#2

Re: cable sizing calculation

10/08/2007 12:22 AM

dear nitin

try this

1) calculate ampacity load to be connected

2) select conductor size as par NEC 110.14 (c), 310.16 (wherever applicable)

3) derate cable size (temp derating and group derating)

4) after derating check the rating with your load, if less go for next higher size and repet from step 2 (reverse calculation)

5) check the VD within permissible limit (3%)

6) select the overcurrent protection device NEC 240.3(b)

any problem pls comback to me (email removed)

CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

__________________
manirul
Register to Reply
Participant

Join Date: Jul 2007
Posts: 3
#3
In reply to #2

Re: cable sizing calculation

10/09/2007 6:40 AM

Somebody please indiacte method based on IEC.

Register to Reply
Anonymous Poster
#4
In reply to #3

Re: cable sizing calculation

11/21/2007 12:55 AM

For IEC sizing you can use the following free online tool:

http://www.myelectrical.com/pages/cables/cableSizing.aspx

Their site also has information on the process for sizing cables to IEC.

Steven

Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#5
In reply to #4

Re: cable sizing calculation

11/21/2007 1:21 AM

Thanks Steven, the tool is really nice and helpful but it is restricted up to 1000 kv, could you please suggest similar tool for higher level of voltage, i have a 1837 kw motor feed from 6.6 kv bus, breaker size selected 1250 A, length of feeder is 70 m, ambient temp 45 deg C, how would i size feeder for this? please suggest some method.

thanks

__________________
manirul
Register to Reply
Member

Join Date: Oct 2007
Location: mumbai
Posts: 8
#6
In reply to #5

Re: cable sizing calculation

11/23/2007 2:22 AM

To size the current you should refer the relevant bs,is or IEC standards.

Alternatively from cable manufacturer tables(ducab or polycab or oman) one can calculate the current but several factors have to be taken into consideration

1. cables being laid in air,duct or buried ground.

2. cables are touching or spaced - derating factor will be applicable

3. If in trays the no of vertical tiers of tray laid

4.the deration factor due to ambient temperature.

5 . the cable should be able to take the fault current till the time breaker disconnects

(for a 11KV VCB breaker the disconnect time is 80milli second as per abb.)

For this sq of k x sq of S=>sq of I x t has to be calculated where

k = factor depending on cable insulation and conducting material

s = cross sectional area of cable

Sq of I x t = called let through energy of the device(product of fault current and the time of flow through the device)

formula is Power = 1.732 x voltage x current x p.f

I assume that in your case the fault current at the breaker terminal will be 35KA for 1 sec as for 11 KV it is 25 KA max for 1 sec

In this case

I = 1837 x 1000

--------------- = 206 A

6.6 x 1000 x 1.732 x0.8

refer to ducab catalogue or polycab catalogue for quick calculation as it freely available from web and take into account all the derating factors,and the fault current capacity for 1 sec.

As for considering sq of ixt value size the cable according to fault current(35ka) & rated current as any manufacturer breaker will disonnect in 1 sec.

But i dont know why you have gone for 1250A breaker as a 400A or 630A breaker will suffice.

Errata

This 1837 KW of motor is it input or output power.if it is output then it has to be divided by efficiency.actually you will have to look at manufacturer chart( if available) and know the current for 1837 KW.that is the correct method for calculating current.

Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#7
In reply to #6

Re: cable sizing calculation

11/23/2007 3:54 AM

current is not a problem with ducab or polycab or oman mfr table or tool available at there web but it is voltage 6.6 kv which is not supported by their web based tool.

__________________
manirul
Register to Reply
Member

Join Date: Oct 2007
Location: mumbai
Posts: 8
#8
In reply to #7

Re: cable sizing calculation

11/23/2007 4:01 AM

In ducab catalogue on the web the current capacity of ducab 3.3kv/6.6 kv/11KV cables is available with short ckt withstand current,various derating factors are available in pdf form.If you want i can send the pdf file.

Register to Reply
Anonymous Poster
#9
In reply to #8

Re: cable sizing calculation

06/11/2008 5:43 AM

U are right sir,I really need one sir, if possible please send it to my mail id :

<email removed>

well...about me, I am P. K. Singh,BE(Electrical Engineer,kolkata) but a fresher n totally new in design world of electrical engineering, i have worked as a site engineer..earliar in a construction firm.

I am also registering today on this site.

hope for the best.

CR4 Admin - email address removed

From the CR4 Rules: Do not post phone numbers or email addresses. The CR4 Admin will delete all phone numbers and email addresses posted in threads or comments. You can share this information via the CR4 internal messaging system.

Register to Reply Off Topic (Score 5)
Anonymous Poster
#11
In reply to #6

Re: cable sizing calculation

08/27/2010 1:54 AM

can u please suggest cable size for 2.75 MW, 6.6 KV, 283 A motor for a length of 150 m?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: cable sizing calculation

03/08/2010 7:46 AM

British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856