TWhy the IEC cable catalogs show,
Phase conductor DC resistance @ 20 degree celsius
Phase conductor AC resistance @ 90-degree celcius
Why not at some other temperatures as well?
Re: Cable temperature
02/24/2019 9:37 PM
Why not provide a link?
02/26/2019 6:01 AM
Re: Cable Temperature
02/24/2019 10:50 PM
Knowing what temperature rating the insulation is, defines the conductor carrying capacity, so knowing what the specific current carrying capacity is at a certain temperature you can calculate how that may vary in different circumstances...and AC resistance is different in nature from DC....AC resistance is generally 1.6 times more than DC current due to skin effect...
https://www.quora.com/Which-one-is-more-AC-resistance-or-DC-resistance
https://www.electricalengineeringtoolbox.com/2014/07/dc-resistance-of-conductor.html
https://iaeimagazine.org/magazine/2000/03/16/wire-temperature-ratings-and-terminations/
02/25/2019 11:02 PM
Also, If you are going to measure the DC resistance of a cable you are presumably going to do it at a time when there is no (significant) AC current flowing in it, so it is likely to be close to ambient temperature (commonly taken as 20°C).
On the other hand, the current-carrying capacity of a a cable will be worst-case conditions when it is hot, so it is logical to specify the resistance when hot.
02/25/2019 9:41 AM
What did <...the IEC cable catalogue...> publisher say during the telephone calls made on this topic?
Reply Score 1 for Off Topic
Anonymous Poster #2
02/27/2019 3:17 PM
The publisher spoke in French and the poster never understood a word he said, so he asked here, Merci pour votre appel
Good Answers: 22
02/26/2019 4:53 AM
For XLPE and HR PVC insulated cables, the recommended max operating temperature is 90degC. This explains why AC resistance @ 90 degreesC.
Raghunath
02/26/2019 6:06 AM
Can I understand, when the tabulated current ampacity for the particular cable flows through the cable, temperature will be within 90 degree celcius?
But how to find the time limit for the cable before which the temperature of the cable reaches up to 250 degree celcius during short circuit
02/26/2019 10:11 AM
The maximum current ratings of cables depend upon the ambient temperature and the installation arrangements of each cable and its neighbours where they cross and also, particularly, run parallel. The time limit for the cable in the installation arrangement can be calculated using the applicable national electrical code, and the circuit protective device(s) can then be chosen to suit, giving a cable that is fully protected when installed in accordance with that code.
A full protocol for working all this out is given in British Standard 7671, as an example of one nation's electrical standard; other standards are applicable in other jurisdictions.
If in doubt, consult a qualified Electrical Engineer.
Good Answers: 22
02/26/2019 11:33 AM
The catalog provides a formula for SC withstand. If the required duration is less, the cable can withstand higher magnitude of SC current.
It follows the relation 'Isquaredxt' is constant. That is, for a reduction in current, the increase in SC duration would be substantial (exponential).
Raghunath
Good Answers: 116
02/26/2019 6:17 PM
The time to reach 250'C from 90'C maximum working temperature is found by assuming the cable conductor loses no heat during short circuit but all current2 x resistance heating is absorbed by the mass x specific heat capacity of the cable [this is called adiabatic heating]. This calculation must take into account the initial resistance @ 90'C & increase in resistance of the cable as its temperature rises.
BS7671:2018 clause 434.5.2 gives formula t = k2*S2/I2 where t = seconds for temp to rise from rated continuous current value to maximum short-circuit value: S = cross-section of conductor in square millimetres: I is rms AC fault current in amperes: k is coefficient according to material and initial & final temperatures. For 90'C rated thermosetting insulation & final temperature 250'C with standard copper conductor, k is given as 143 in table 43.1
As an example, this is a graph of short circuit withstand times for various mm2 copper PVC insulated 70'C rated cables compared to fuse maximum operating times......Note that, with this fuse protection, the danger for the cable comes if short-circuit current is too low - maybe if you over-estimate short-circuit current with no margin on cable withstand time.
Your local regulations may give different rules, so this is just an example from UK regulations.