Motor Current Discrepancy

02/24/2019 10:32 PM

We have replaced a 3 phase induction motor (30kw) 415V on a fan; now the current has changed from 20A to 30A with both well below FLA which is 53A.

Mechanically (fan) everything else is the same. No extra noise or heat is being produced.

Old motor: 30Kw, 6 pole, but can't see the RPM or P.F. Brand is Hyundai

New Motor 30Kw, 6 pole, 990RPM. Brand is WEG

May someone please explain the difference in Amps?

Actually shaft Diameter has changed from 65mm to 70mm.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: motor current discrepancy

02/24/2019 11:05 PM

I cannot explain this from the information you've provided us. I suspect a difference in the wind inductance has lead to different power factor. Then again you might have made a reassembly misalignment that is leading to excessive bearing wear, too.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#2

Re: motor current discrepancy

02/24/2019 11:06 PM

I would say you increased the RPM ...you might have a 50hz motor running on 60hz power supply...?

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: motor current discrepancy

02/24/2019 11:59 PM

Did you try to discover the missing data by Goggling the mfg. motor number from the name plate.

Motor RPM? Frequency?

Provide adequate information for an informed answer.

Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#4

Re: motor current discrepancy

02/25/2019 12:35 AM

These are all 50Hz motors with 50Hz supply, alignment is perfect. The only factors that are different are shaft diameter, maybe RPM may have changed from 950 to 990RPM.The new motor is a high efficiency motor.

Can these factors alone can cause the change in amps.

Register to Reply
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#6
In reply to #4

Re: motor current discrepancy

02/25/2019 3:11 AM

~ 12% increase in airflow could account for the additional power demand...it's possible there was some restriction in the airflow previously? ...or the rpm on the old motor was something around 870...or the fan blades were really dirty and have since been cleaned....

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: motor current discrepancy

02/25/2019 1:20 AM

At the time of motor replacement, were any air passages also cleaned? If so, the increased air flow could explain (at least some of) the increased amperage.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#7

Re: motor current discrepancy

02/25/2019 4:13 AM

This is a significant increase in power demand; (50%)

The only things I can think of that result in higher amps from one motor to the other are:

Increased load (air flow,bearings,alignment,etc.)

Improper direction of rotation?

Pulley size change or excessive belt tension, if belt driven.

Wrong frequency or voltage connection (wye,delta); double check connections on motor.

Is there a perceptible increase\decrease in air flow?

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply Score 1 for Good Answer
Guru
Australia - Member - New Member

Join Date: Feb 2008
Location: Australia
Posts: 2181
Good Answers: 255
#8
In reply to #7

Re: motor current discrepancy

02/25/2019 5:25 AM

My first thought after reading the request was also that of wye/delta connection, followed closely by the outcome of the inevitable maintenance done on the air flow path and any screens aka cleaning.

Others already there with the descriptions.

__________________
Just an Engineer from the land down under.
Register to Reply
Guru

Join Date: Sep 2016
Posts: 973
Good Answers: 9
#9

Re: Motor Current Discrepancy

02/25/2019 8:09 AM

Recalling P=VI= I2R, so R=P/I2, the old has more resistance/impedance than the new by roughly 50%, so you better check do insulation test for both not operating and compare.

You may also look at P=Tω.

Casing or bearing housing to shaft alignment and preload condition might be different also. Types of bearing used between the old and new could also be an attribute.

Fluid dynamics of the work piece might also be an issue.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Motor Current Discrepancy

02/25/2019 9:38 AM

If the new motor is operating inside the full load current of the existing installation, can someone please explain why the <...We...> has a perceived problem to solve?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
4
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11

Re: Motor Current Discrepancy

02/25/2019 10:36 AM

You are falsely equivocating current with power, you are leaving out Power Factor. Current may be higher simply because the power factor is lower: P = A x V x PF x eff (x 1.732 for 3 phase). Watts may actually be lower on the motor with the higher current with a significant difference in partial load power factor. This is not unusual for high efficiency motors; they are designed to optimize the real power consumption at full load, you are not using it at full load. Measure this again with a watt meter and see for yourself.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 4)
Guru

Join Date: Mar 2007
Location: by the beach in Florida
Posts: 33392
Good Answers: 1817
#12
In reply to #11

Re: Motor Current Discrepancy

02/25/2019 1:19 PM

I was looking at this as a possibility as well, it seems this motor is only about 40% loaded....so the motor is over sized for the application... Ideally the motor should be loaded 60-80%....The power factor is probably <60 ....

https://www.energy.gov/sites/prod/files/2014/04/f15/10097517.pdf

__________________
All living things seek to control their own destiny....this is the purpose of life
Register to Reply
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#13
In reply to #11

Re: Motor Current Discrepancy

02/25/2019 3:48 PM

Thank you, clearly aligns with our set up. Just to note, Everytime we replace these Hyundai motors with a new motor we notice a change in amps, it is more noticeable in this application, maybe due to the motor being oversized.

Amps is something Process people look at ,it is a challenge to change that.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#14
In reply to #13

Re: Motor Current Discrepancy

02/25/2019 6:55 PM

"Amps is something Process people look at ,it is a challenge to change that."

Amps change not only with power factor, but also with voltage swings. I personally don't like using amps on a motor as a process value. Spend a few dollars more and get a kW meter. kW ALWAYS correlated to actual shaft power, which is meaningful no matter what other changes are going on. the nice thing now is that there are many "smart overload" relays that will give you an analog output proportional to kW, so rather than have multiple devices on the same circuit, you just swap out the OL relay for a smart one and get the info from that.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Oct 2006
Location: 44.56024"N 15.307971E
Posts: 8277
Good Answers: 270
#16
In reply to #14

Re: Motor Current Discrepancy

02/25/2019 11:26 PM

Industrial users of electricity have 3 charges:1 for KWH, 1 for KVAR(power factor),and one for Demand.

The billing is based on all three factors,with a steep multiplier for high demand and low power factor.

These used to be separate meters,but they are now recorded digitally and an instantaneous real time usage is available to the user.

Some older plants still insist on having the old analog meters in addition for verification.

Whatever the cause of the high amp draw,it is costing the company at least 50% more to run the new motor.

__________________
"A man never stands so tall as when he stoops to help a child." "Never argue with a stupid person.They will drag you down to their level and beat you with experience" "To create an apple pie from scratch, first you must create a universe"
Register to Reply
Guru

Join Date: Jul 2016
Posts: 1367
Good Answers: 105
#15
In reply to #13

Re: Motor Current Discrepancy

02/25/2019 10:24 PM

A small change in speed (because your newer motors have lower slip) will increase power consumption significantly for a centrifugal fan, the higher amperes is likely due to the higher air flow, due to the higher speed. Power factor may have some small impact on the observed amperes.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#17
In reply to #15

Re: Motor Current Discrepancy

02/26/2019 3:39 AM

Quite. Power consumption varies with something like the cube of the impeller tip speed.

Why the <...process people...> are interested in <...amps...> is somewhat abstruse.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#19
In reply to #15

Re: Motor Current Discrepancy

02/27/2019 12:25 PM

"A small change in speed (because your newer motors have lower slip) will increase power consumption significantly for a centrifugal fan, ..."

Excellent point. Yes, power required by a centrifugal fan increases at the cube of the speed change. So even a small change in slip speed will have an amplified effect on power consumption.

A 50% increase in current however would require a 14% increase in speed alone; more than just what you might expect in a slight difference in slip speed on a motor of the same pole count. It's likely a combination of a higher slip speed AND a lower power factor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
2
Guru

Join Date: May 2016
Posts: 1746
Good Answers: 87
#18

Re: Motor Current Discrepancy

02/26/2019 1:51 PM

You have indicated that the shaft size is different, so the motor frame designation is probably also different. Current draw can be affected by any other internal geometry changes, including actual amount of iron present in the rotor and stator, clearances and shunt pieces installed. That amount of current draw change at that low a loading wouldn't be unusual and I would guess that the individual(s) inquiring about the current change are simply trying to look forward to see that an unforeseen unfortunate occurrence is avoided. If the motor always runs at this condition, it might be worthwhile to add some fixed capacitance to correct the power factor for lifetime energy cost if the economics pencil out. I knew of one company that kept an overenergized synchronous motor idling on line to keep the plant power factor as close to 1 as possible with a fairly generous return on investment in power savings.

Register to Reply Good Answer (Score 2)
Register to Reply 19 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

eltech (2); gutmonarch (1); HiTekRedNek (2); Jpfalt (1); JRaef (3); Just an Engineer (1); lyn (1); PWSlack (2); redfred (1); rwilliams (1); SolarEagle (3); Tornado (1)