Generator, Power Factor Correction and Fuel Usage
03/19/2019 8:33 AM
Hi All.
Wesley here from South Africa.
I wanted to ask a question on the above as I have done a fair amount of research and I have not come up with a definite answer, or one that makes sense to me.
I came across this thread:
https://cr4.globalspec.com/thread/112099/Effect-of-Power-Factor-Correction-in-Fuel-Consumption
After reading some of the comments, there are still some holes in the discussion for me.
Let me give you some history:
We are a power quality consultant based in South Africa that specializes in Power factor correction and Harmonic Filtration.
But with the power supply issues we are currently experiencing in our country, we are trying to help our industrial customers in any way we can.
With our current power crises, we are trying to promote the use of an Static VAR Generator (SVG) to our industrial customers to reduce the fuel consumption of their generators, which in certain instances promotes the ROI of the SVG equipment in a very short space of time, due to the very large bills and poor PF of their loads. ( they have traditional PF for when on grid supply, but this is disconnected when on running on genset)
All of the discussions I have read all focus on fixed capacitor banks, and we know these are not good for generators, as if the load drops, and in the delay time that the PF controller has to disconnect banks, the generator will be forced to absorb all that leading energy, and this will damage the alternator unit.
Now, I ask, on a larger generator, eg 500kva at 0.8 PF and a load sitting at 0.85, why can I not reduce my fuel consumption by increasing the PF with a static VAR generator to 0.99?
I understand that I will get a reduction in current, and that will allow for the reduction in I2R losses in the alternator, but how can I not get a reduction in fuel, as the alternator now has to put out lesser useless current as it does not have to supply KVAR.
KVA = KW+KVAR, where KVAR will have reactive current drawn by the load, and this has to be generated by the alternator.
For the Prime mover, power output is a function of RPM and Torque, with RPM being fixed, power output then becomes a factor of torque only, Ie to increase current output of the Alternator, more torque needs to be applied by the prime mover, along with the appropriate excitation from the AVR in order to increase supply.
More torque means more fuel being burnt......
So if I reduce my total current by fixing up the load PF, I would then reduce the load on the Prime mover, and hence save fuel, or am I missing something here?
I am looking forward to your replies.
Thanks in advance.
Re: Generator, Power factor correction and Fuel Usage
03/19/2019 9:57 AM
The answer pivots on the efficiency of the device you use for power factor correction. Capacitor banks are relatively efficient but they do suffer from the switching problem you mentioned along with the inability to "tune" to any desired reactance. The synchronous condenser approach will be tuneable but includes its own set of IR power losses in order to excite the DC field.
However one improves the power factor it can usually reduce the mechanical power needed to make electric power, but every added device has its power cost.
03/19/2019 11:53 AM
Thank you for your reply
Thermal loss of a good quality SVG is around 3%, so will still be less than the power required to generate the required KVAR for the load, so the net gain will still be positive.
03/19/2019 10:08 AM
I think you hit it on the head: with PF correction, you reduce the amount of current necessary to deliver a given amount of power to the load. The power to heat the copper in the generator (and transmission lines) has to come from the generator, i.e. fuel for the engine.
03/19/2019 11:54 AM
Thats what I have been trying to find out, but no one else seems to agree, it seems to defy logic.....so I am not insane by making these assumptions
I really appreciate all the replies gentlemen.
03/19/2019 12:37 PM
Well, the logic most people apply is the Law of Conservation of Energy.
So, yes, any excess current due to the reactive loads will result in additional IR losses in the whole system. So if you can show the delta between PF=1 and whatever PF, then you could calculate the energy losses that the generator is going to take from the engine or turbine or whatever power source is being used.
Then it becomes a question of ROI. Complexity has it's costs too. And you can almost always count on the Laws of Unintended Consequences.
Good Answers: 804
03/19/2019 5:52 PM
There are only two real situations in which PF correction saves you money;
1) when the Power Company assesses a PENALTY for having poor PF, and
2) When you use a fuel based generator. That's because fuel is consumed for providing kVA, not kW. So if you have a low PF, that means your load kW is going to be low, but your kVA is still going to be high and therefore your fuel consumption will be commensurate with that kVA. But if you use PFC, the kVA per kW as seen by the generator is lower, ergo the fuel consumption is lower. So the operative issue then, as was mentioned earlier, is just the efficiency of how you correct the PF. Mechanically Switched Capacitors (MSC) are the most efficient, but are going to have to act in steps that may or may not be accurate to the dynamics of the load. Synchronous Condensors (SC) are an analog response solution, but are slow to change and consume more energy because there are always mechanical losses (friction, wind) as well as electrical losses (I2R in the windings, eddy current losses in the steel). Static VAR Compensators (SVC) are a good compromise because they react faster than SCs, but have internal losses closer to those of MSC.
BUT, you should check with your generator supplier because of possible resonance and AVR issues.
03/20/2019 3:01 AM
Thank you, The compensation will be only via SVG, so 20ms response time, no real capacitance as it is a current amplifier, so that negates the risk of resonance and AVR issues completely.
03/19/2019 11:20 PM
The fuel for the prime mover produces power, kilowatts, NOT kVA. The amount of energy you save by reducing excitation current is minuscule, the I2R associated with the winding resistance is also very small for even some of the worst typical power factors encountered.
You will be hard pressed to measure the fuel savings achievable by adding capacitors to correct the load power factor.
The reason you might want to improve the load power factor is to allow the prime mover to produce more kilowatts, when you are generator limited. At a unity power factor load, the generator kVA = the kW capacity. In this case you take advantage of the efficient use of the prime mover, producing the most useful power for the unit.
Also, the generator running close to unity power factor is inherently unstable, easier to pull out of step, and can lead to power system instability. Operation at 0.95 PF leading from the generator viewpoint, lagging from the load standpoint, meets most generator design specifications for pull-out.
The I2R losses of the load transmission equipment will be reduced, but only if the power factor correction is placed at the load. Capacitors placed close to the generator terminals will do NOTHING to reduce distribution system I2R losses. Distribution system losses, transformers, reactors, conductors, will increase your fuel consumption, producing heat. On anything but the most poorly designed distribution system, you will not be able to measure the difference in fuel consumption, to justify the expense & complexity, reduction in reliability that comes with adding more components to your distribution.
03/20/2019 3:11 AM
But the KW of the Prime mover is a unit of mechanical power, not electrical power, it is converted into electrical power (KVA) by the Alternator, and KVA is the sum of your reactive and active power.
As mentioned as well, we will not be using capacitors but static var generators, that do not have any of the same electrical properties of capacitors, they work by using current amplifiers to be a source of lagging or when required, leading reactive power as well.
Stability is not a problem and you can run the PF at 0.99 all day due to the response time, the AVR wont see any fluctuations besides the need to provide more or less active power as the load change.
Remember, we are not aiming to reduce I2R losses, that happens as a consequence of this, we are aiming to reduce the amount of current the alternator has to put out by reducing KVAR demand as close to zero as possible.
03/20/2019 4:01 AM
CR4 is not really set up to sustain argument.
03/20/2019 12:37 PM
<insert Argument Clinic here> Yes, sometimes it feels like Abuse but the Argument Clinic is down the hall.
03/20/2019 9:12 AM
You are quite wrong, on all counts, and your clients will be very upset if you try this and fail, or if you decide to finance this with the savings, you will fail miserably.
Please research the difference between kVA and kW, only one is power, the other has a minute effect on power consumed, kVA is vector sums of reactive and real power, not related arithmetically. This is the point of your analysis failure.
Good Answers: 137
03/22/2019 10:29 AM
That's right, kW2 + KVAr2 = KVA2
03/23/2019 3:24 AM
So where does the current come from to supply the reactive power that the load requires?
03/23/2019 8:51 PM
The excitation is the 'source' of the current, in so far that if you have no internal excitation, then the magnetizing current for the generator comes from the power system, other generators, capacitors.
There is no fuel penalty for the reactive power, except for the power (not amperes but kW) required to excite the field. The concept of your idea is valid, it is just an order of magnitude lower in opportunity than you imagine. Plus, regardless of your opinion to the contrary, mechanical power system stability is significantly improved by having a good strong coupling between the rotor and the stator.
The I2R losses of the field and stator windings are what you can save by reducing stator current. Unless the machine is a hopelessly inefficient design, if you calculate the power dissipation difference between the two conditions, using the only real and ignoring the reactive component of the amperes, you should find that your fuel measurement instrument will not be sensitive enough to measure the difference between generator leading 65% power factor and leading 95% power factor.
03/20/2019 12:45 PM
You have to ask yourself where the energy goes. Energy In = Energy Out.
Ultimately, it all ends up as heat at the end of the line. I2R losses are heat. The work that the loads do eventually ends up as heat. So where is the wasted energy when you have leading or lagging PF?
03/25/2019 3:18 AM
Your load will required Reactive energy whether you like it or not, the SVG will provide the reactive energy, and it will not have to come from the Generator.
03/25/2019 11:20 AM
Again, you are totally missing the link between the real kw losses associated with transmission of reactive power, and your assumption that reactive power is equivalent to real power, because it is all amperes.
Re: Generator, Power Factor Correction and Fuel Usage
09/25/2024 7:37 AM
Got to dig those unrestrained TLAs.
Register to Reply 19 comments