Harmonic Analysis

03/27/2019 5:18 AM

Hi All,

I have carried out a harmonics test on a site the system is with the generator and the distribution loads the distribution load is having some communication systems.

i got values ranging between 4% to 20% current harmonics and also my neutral to ground phase harmonics measurements are all above 50% . My voltage harmonics are less than 2%.

Clearly am not having an idea of harmonics measurements can any one suggest the values are good as per standards.what are the standards for voltage harmonics and current harmonics.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster #1
#1

Re: Harmonic Analysis

03/27/2019 6:57 AM
Register to Reply
Guru

Join Date: Apr 2010
Location: About 4000 miles from the center of the earth (+/-100 mi)
Posts: 9910
Good Answers: 1141
#2

Re: Harmonic Analysis

03/27/2019 12:06 PM

To start with, voltage is supplied by the generator. Current is the load's response to the voltage.

Many loads are non-linear in that they draw current when the voltage is at its peak value. Examples are power supplies which charge internal capacitors and fluorescent lighting which conducts when the gas is ionized. These will cause current harmonics.

Harmonics in the neutral current in three-phase loads will be higher than the phase current harmonics because all three phase currents return through the neutral.

The amount of harmonics present depends on the characteristics of the load and how well it is balanced.

Register to Reply
Participant

Join Date: Mar 2019
Posts: 4
#3

Re: Harmonic Analysis

03/27/2019 12:56 PM

Thanks for the replies,

if the voltage harmonic values are in limits( THD>5 and individual >3),any relevance for current harmonics?

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Harmonic Analysis

03/27/2019 9:01 PM

Condensed version of a complex subject.

Current harmonics are what cause voltage harmonics. So the current harmonics in your facility are the source of voltage harmonics, along with the stiffness of the system as measured by the ratio of Available Short Circuit current vs actual Load current. Current harmonics are also affected by EXISTING voltage harmonics in a system in that if there is high V-THD coming in FROM the utility connection, it will make your I-THD worse and the situation can spiral out of control, causing transformers to melt down etc. So V-THD is of concern when you are connected to a utility supply because voltage harmonics travel from you to your neighbors on that common connection. IEEE 519 specifications call out the limitations for the end users AND the utilities with regard to how they affect each other in order to prevent this down hill spiral.

If you are on your own generator, the IEEE 519 rules are irrelevant. They can still be used as a guideline however, because what the I-THD will affect is the capacity or fuel consumption of your generator. The generator has to supply ALL of the power going to the equipment, whether at the fundamental frequency or at the higher harmonic frequencies. If you follow the IEEE-519 guidelines, you can mitigate the impact that harmonics will have on your generator capacity and/or fuel consumption. Or you can chose to ignore it, because it will not affect anyone but you.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#5

Re: Harmonic Analysis

03/28/2019 12:59 AM

what equipment are you running on the gen set power supply?

Motors with VSD's etc?

__________________
The square root of nothing is what you make it!
Register to Reply
Participant

Join Date: Mar 2019
Posts: 4
#6
In reply to #5

Re: Harmonic Analysis

03/28/2019 1:02 AM

Thanks for the replies,
want to add one more query:
If i am using a generator supply for the system and my load is sensitive communication system, all i understand is some current harmonics will be there for sure may be higher or lower.
My sensitive communication system is fed by the generator and its having some issues during operation and is it be the only possibility is to provide a UPS supply before the communication system for rectification?.
I also have some utility load in the same bus which is also fed from my generator.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#7
In reply to #6

Re: Harmonic Analysis

03/28/2019 1:54 AM

what issues are you having with your generator?

__________________
The square root of nothing is what you make it!
Register to Reply
Participant

Join Date: Mar 2019
Posts: 4
#8
In reply to #7

Re: Harmonic Analysis

03/28/2019 1:59 AM

No issues with the generator , but the communication system(Load) having some noise issues.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#9
In reply to #8

Re: Harmonic Analysis

03/28/2019 2:18 AM

Noise issues or spikes could be due to your generator not being earthed properly.

Hopefully you have rated the generator to suit your Kva demand, or that will be an issue, also with noise on your comms that could be due to bad connections and equipment earthing.

As I don't know what type of comms you are using, it will be difficult to assess the problems. However i suggest you get the manufacturer to help

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#10

Re: Harmonic Analysis

03/28/2019 3:46 AM

Noise is not harmonics...

Common Mode noise is often the result of PWM switching, which often comes from the SAME EQUIPMENT that creates harmonics, so they are often guilty by association. But these are different issues. CM noise is usually made worse by poor grounding practices as mentioned. Start there.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Register to Reply 10 comments