Breaker Sizing

10/09/2007 1:22 AM

What is the sizing calculation of main incommer of MCB or MCCB breakers?

__________________
manirul
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: breaker sizing

10/09/2007 3:47 AM

Refer to the local Wiring Regulations applicable to the country of use.

In the absence of a local standard, use the Institution of Electrical Engineers' current edition of the Wiring Regulations applicable in the UK as a guide to good practice.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Aug 2007
Location: HCMC, VietNam
Posts: 16
#2

Re: breaker sizing

10/09/2007 4:37 AM

Incomming circuit breaker. Pls give some more in formation about: phase, rated current, protection type, voltage,etc.

__________________
.....................
Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#3
In reply to #2

Re: breaker sizing

10/09/2007 4:50 AM

i dont think all those info is required to get calculatation procedure, i have not ask for rating of breaker, what i want to know how to calculate not the resulte of calculation, any way the info is as below

phase :3

rated voltage: 440

rated frequency: 50 Hz

Rated current: 800 A

__________________
manirul
Register to Reply
2
Active Contributor
India - Member - New Member

Join Date: May 2007
Location: India - (Home town - Tamil nadu, Working - Jemshedpur)
Posts: 12
Good Answers: 1
#10
In reply to #3

Re: breaker sizing

10/09/2007 10:11 AM

Dear manirul,

MCCB & MCB are basically used for Short circuit protection. MCB for Low rating & MCCB for High rating. For selection, two factors- Short circuit rating (KILO AMPERE) & Over load rating (AMPERE) are to be considered as mentioned below:

Short circuit rating (KILO AMPERE): Measure the resistance of outgoing busbar or cable, i.e., resistance from the point of MCCB outgoing termination to the distribution load switch gear(s) & calculate the max current it (busbar or cable) can withstand. Now refer the standard chart of MCCB manufacturers & select the short circuit rating (KILO AMPERE) matching more or less to your calculated figure. Finalise that as Short circuit rating (KILO AMPERE).

Loading capacity (AMPERE): Sum up distributed load currents (max instantenous current) which can flow through MCCB. Multiply the same with 1.5. The is the over load capacity of MCCB. Note: If you have more no of high rating motors with distributed load & if they start simultanously, considering their starting current, increace this rating to some more %. Now refer the standard chart of MCCB manufacturers & select the loading capacity (KILO AMPERE) matching more or less to your calculated figure. Finalise that as loading capacity (AMPERE).

Regards,

Vinod.P (Asst Mgr-Engg),

SCJPPL, HP,India.

Email Id- vinod29mar@gmail.com

__________________
Regards, Vinod.P, Engineering Deptt, LAFARGE , India
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#12
In reply to #10

Re: breaker sizing

10/10/2007 12:24 AM

Thanx Mr. vinod

I appreciate ur effort to put the light from technical point of view and that's prove ur tecnitiality while other people just have an argument to kill the time. ur shareing of Knowledge will be gr8 help to me.

__________________
manirul
Register to Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#13
In reply to #3

Re: breaker sizing

10/10/2007 2:41 AM

Is it clear you can not have MCB

The batter alternate is Air Circuit Breaker for the rating of 800 Amps.

nascon

Register to Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#4

Re: breaker sizing

10/09/2007 6:18 AM

Dear

As the breaker names indicate , The MCB is miniature Circuit Breaker., i.e breaking capacity limited for short circuit / fault level .

MCCB i.e Moulded case Circuit Breaker., not limited to miniature SC.

The MCB sizing is limited up to lower short circuit / fault level say @ 63 Amp., due to product designed limitation of short circuit level / fault current @ 10 KA recently available on request for 80 / 100 Amp.

The MCCB sizing for the fault level are for higher breaking capacity ., i.e short circuit for more than 10 KA and up to 143 KA amp rating up to 1600 Amp.

nascon

Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#5
In reply to #4

Re: breaker sizing

10/09/2007 6:39 AM

Dear

you are talking about difference B/W MCB and MCCB, but discussion is not intendent to that.

__________________
manirul
Register to Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#6
In reply to #5

Re: breaker sizing

10/09/2007 7:35 AM

Dear

Breaker sizing , if not discreamination of falut ? not amp and SC ? what do youmean over all dimension?

nascon

Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#7
In reply to #6

Re: breaker sizing

10/09/2007 7:43 AM

dear

breaker sizing is not fault calculation but it definitely amps but not SC

__________________
manirul
Register to Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#8
In reply to #7

Re: breaker sizing

10/09/2007 8:03 AM

Dear

You must know the basic, when you are sizing the breaker with Amp ., it is rate Amp. And, the said rated amp must withstand the required SC / Falut current for the system it is connected to.

Hope, you will understand the what the sizing of breaker means ?

nascon

Register to Reply
Power-User

Join Date: Oct 2007
Location: Pune, India
Posts: 132
Good Answers: 2
#9
In reply to #8

Re: breaker sizing

10/09/2007 8:16 AM

exactly, now the question is if you are saying withstanding, then it is not only SC but also time which is relavent, am not sure about it.

__________________
manirul
Register to Reply
Power-User

Join Date: Apr 2006
Location: Texas, by God! Houston for precision
Posts: 167
Good Answers: 2
#11

Re: Breaker Sizing

10/09/2007 11:09 PM

What's the load on the circuit? FTLOG, without that all questions are meaningless!

__________________
If all else fails, read the directions. That's if, and only if.
Register to Reply
Associate

Join Date: Aug 2007
Posts: 29
#14
In reply to #11

Re: Breaker Sizing

10/10/2007 9:59 AM

What is the criteria in selecting ACB, MCCB, OCB, VCB etc. in both LT & HT distribution. In other words, how is the / in what basis the selction of breaker is made? can some one explain??

Register to Reply
Commentator
India - Member - PROFESSIONAL Engineering Fields - Power Engineering - electrical planning - designing

Join Date: Sep 2007
Location: Ahmedbad, Gujarat
Posts: 97
Good Answers: 1
#15
In reply to #14

Re: Breaker Sizing

10/11/2007 4:25 AM

HT , two more type of breakers are available i.e MOCB (Minimum Oil Circuit Breaker ) and SF 6 (Sulphur Hexa Fluoride)

nascon

Register to Reply
Active Contributor
India - Member - New Member

Join Date: May 2007
Location: India - (Home town - Tamil nadu, Working - Jemshedpur)
Posts: 12
Good Answers: 1
#16
In reply to #14

Re: Breaker Sizing

11/16/2007 8:25 AM

MCCB & ACB are used in LT side. MCCB for low rating (It is safe upto 400 Amp) & ACB for more than 400 Amp.

OCB: OCBs comes just above ACB for highier rating. Earlier days it was used both in LT & low level HT side. Later it was used only in low level HT side. But now days OCBs are slowly getting replaced by VCBs. This is because of OCBs need more maintenance, maintenance cost is high & not environment friendly.

VCB & SF6: These are used in HT side. They is more relaible & efficient. For some special applications like very high making & breaking currents, VCBs are also used in LT side.

Note: The above said are the classifications & some what related to selection also. Other than this, selection includes Breaking capacity, Short circuit current, Load current capacity, Earth leakage current level, No of poles required, Protections required, Voltage level etc.

Regards,

Vinod.P (Asst Mgr-Engg),

SCJPPL, HP,India.

Email Id- vinod29mar@gmail.com

__________________
Regards, Vinod.P, Engineering Deptt, LAFARGE , India
Register to Reply
Associate

Join Date: Aug 2007
Posts: 29
#17
In reply to #16

Re: Breaker Sizing

11/16/2007 8:51 AM

thanks vinoth,

though it was posted long back, you have replied with some valuable datas.

Register to Reply
Participant
Technical Fields - Technical Writing - New Member India - Member - New Member

Join Date: Jan 2009
Posts: 2
#18

Re: Breaker Sizing

04/14/2010 2:36 AM

For calculating Breaking capacity of CB downlaod excel base program from

www.jiguparmar.com

__________________
jiguparmar
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#19
In reply to #18

Re: Breaker Sizing

04/14/2010 11:34 AM

Superb website....hats off to you Jiguparmar.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#20

Re: Breaker Sizing

04/14/2010 11:43 AM

Ok...having seen and studied the replies, may i mention that you need to look at circuit breakers in series mode...discrimination and cascading. An excellent paper on this is available from Schneider, please visit ...

http://www.schneider-electric.com/documents/technical-publications/en/shared/electrical-engineering/dependability-availability-safety/low-voltage-minus-1kv/ect167.pdf

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Register to Reply 20 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

haivot (1); jiguparmar (1); ktel60 (1); kvsridhar (2); manirul (5); Minsaramanithan (2); nascon (5); PWSlack (1); winotp (2)

Previous in Forum: Use Of Diversity Factor   Next in Forum: Switch Versus Isolator
You might be interested in: Circuit Breakers, Load Centers

Advertisement